Default Re: Electrical Inspections by Home Inspectors

Quote:
Originally Posted by jpope
Without codes (all codes), the HI has no reference for what is right or wrong. It's as simple as that.
Agreed Jeff, those who say that codes have no place in home inspection are just plain wrong, while we should not be trying to quote specific articles of codes we should be applying the principles behind them. Code changes are the result of prior failures and changes in technology and as HI we need to be aware of them.

Does thois mean that we should all be swatting the IRC or NEC, no probably not (unless you are doing new construction inspection) but any inspector who does not at the very least carry the "CodeCheck" series around with them is simply not providing the best service to his clients.

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #17  
Old 7/1/06, 12:51 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,557
Default Re: Electrical Inspections by Home Inspectors

Quote:
Originally Posted by pabernathy
I did not post the links...but their are alot of articles and so on at www.mikeholt.com to browse through.
Sorry for the confusion Paul. Of course I meant MR. Tedesco.

Mike Holt's site is a very good resource that I use regularly and encourage others to as well.



He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father

The democracy will cease to exist when you take away from those who are willing to work and give to those who would not. Thomas Jefferson

Never underestimate the difficulty of changing false beliefs by facts.
- Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
and
Minnesota Home Inspector

Reply With Quote
  #18  
Old 7/1/06, 12:53 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,557
Default Re: Electrical Inspections by Home Inspectors

Quote:
Originally Posted by gbeaumont
while we should not be trying to quote specific articles of codes we should be applying the principles behind them. Code changes are the result of prior failures and changes in technology and as HI we need to be aware of them.
Well said Gerry. I completely agree.



He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father

The democracy will cease to exist when you take away from those who are willing to work and give to those who would not. Thomas Jefferson

Never underestimate the difficulty of changing false beliefs by facts.
- Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
and
Minnesota Home Inspector

Reply With Quote
  #19  
Old 7/1/06, 1:20 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Electrical Inspections by Home Inspectors

I agree...well stated Gerry



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #20  
Old 7/1/06, 2:38 PM
Richard L. Bennett Richard L. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Frostproof, Fl
Posts: 2,307
Default Re: Electrical Inspections by Home Inspectors

Don't forget all the NEC code around cat 3-5, cable TV, FCC required prewire telephone for new construction, HVAC control systems, and other low voltage items like home entertainment and alarm systems.

Smoke alarms that are hardwired have some standards that a just plain fun. In our town they must have battery backup.

If you don't have it you do not meet the min housing standards! -- Now if it was only enforced. Like an HI is going to call city hall but if we put it in our report that this house does not meet min. housing standards it does wake people up.

Yes, I understand that NEC code for low voltage is outside our scope but perhaps we should revise this part. The NEC has for many years -- at one time it was outside of their scope - Anyone remember when this change?

rlb



rlb
Reply With Quote
  #21  
Old 7/1/06, 3:49 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical Inspections by Home Inspectors

Sure glad to hear from some of the new kids who understand the intent of my post.

I have been criticized by someone recently here on this forum for trying to teach the NEC to the Home Inspector, how many NACHI people are qualified to teach the NEC? Not you Bubba! Please let others come forward!

I would like to hear more about new construction inspections .. you check box fill and all of the items that the City Inspector's check?
Reply With Quote
  #22  
Old 7/1/06, 6:51 PM
Patrick Bolliger's Avatar
Patrick Bolliger Patrick Bolliger is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Chicago, IL
Posts: 890
Send a message via Skype™ to pbolliger
Default Re: Electrical Inspections by Home Inspectors

Quote:
Originally Posted by roconnor
I agree with Jeff that an HI has very little to reference as a guide to assist with deciding what gets reported as (installation) defects except for an SOP and model codes (as "current construction standards"). A basic working knowledge of major provisions is sufficient, with a practical application. But reports should never call out defects as "violations" or reference code sections.


Just one ... the International Residential Code (IRC). Also includes a real handy 70 page summary of the NEC requirements applicable to residential construction, with some diagrams ...


Robert,
Check this out: An ICC code adoption by state and local jurisdiction. When you find Chicago , Il. Tell me what you see?

www.iccsafe.org/government/
(right side pane under Jurisdiction and one under state adoptions) Down load the state and the local PDF files. Great reference....for all
Reply With Quote
  #23  
Old 7/2/06, 10:48 AM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Electrical Inspections by Home Inspectors

Many areas have not adopted ICC based model codes like the IRC, or have local requirements that are more restrictive (like in your area with restrictions on sheathed cable wiring for example). It is still an excellent reference for HI's, and many preach the use of the IRC based CodeCheck series by HI's regardless of what model codes have been adopted at the state/local level. You just have to be aware they are not the legal requirements, and there may be local restrictions.

I was using references like the CABO code (predecessor to the IRC) and CodeCheck as a guide for home inspections well before my state adopted ICC codes in 2003. Worked very well as a guide.

JMO & 2-nickels ...



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #24  
Old 7/2/06, 11:13 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 13,952
Default Re: Electrical Inspections by Home Inspectors

Quote:
Originally Posted by jtedesco1
Sure glad to hear from some of the new kids who understand the intent of my post.

I have been criticized by someone recently here on this forum for trying to teach the NEC to the Home Inspector, how many NACHI people are qualified to teach the NEC? Not you Bubba! Please let others come forward!

I would like to hear more about new construction inspections .. you check box fill and all of the items that the City Inspector's check?
Joe how many Home Inspections have you done for pay.
Roy Cooke sr alias BUBBA sr.
Reply With Quote
  #25  
Old 7/2/06, 11:55 AM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Electrical Inspections by Home Inspectors

Quote:
Originally Posted by jtedesco1
I would like to hear more about new construction inspections .. you check box fill and all of the items that the City Inspector's check?
I have done code compliance inspections as a former chief building inspector for a local municipality, and although there are some common elements a home inspection is completely different. Unlike code officials, home inspectors just need a working knowledge of major model code provisions as a guide, and the practical application of those provisions. As far as checklists, CodeCheck is indeed a widely referenced HI guideline.

For example, box fill should be checked on a code compliance inspection based on the number and type of cables for a given box size. However, as part of a phased home construction inspection it may become an issue only if it looks really bad (in which case it probably is well beyond the acceptable limits). It would also be written up differently, possibly as a "safety concern" with a practical explanation and recommendation for further evaluation, and not as a "violation" with just a code reference section that requires correction.

JMO & 2-nickels ...



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #26  
Old 7/2/06, 12:19 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Electrical Inspections by Home Inspectors

Quote:
Originally Posted by jtedesco1
Sure glad to hear from some of the new kids who understand the intent of my post.

I have been criticized by someone recently here on this forum for trying to teach the NEC to the Home Inspector, how many NACHI people are qualified to teach the NEC? Not you Bubba! Please let others come forward!

I would like to hear more about new construction inspections .. you check box fill and all of the items that the City Inspector's check?
lol.......knowing the NEC is a HUGE bonus for HI's.....gives them better understanding and knowledge of the foundation of Electrical Safety.

Lets all join hands....sing and PRAISE the NEC......



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #27  
Old 7/2/06, 1:07 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,482
Default Re: Electrical Inspections by Home Inspectors

Quote:
Originally Posted by pabernathy
Lets all join hands....sing and PRAISE the NEC......
Kumbaya my code, kumbaya...kumbaya my code, kuubayyaa
Reply With Quote
  #28  
Old 7/2/06, 2:48 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical Inspections by Home Inspectors

Quote:
Originally Posted by rcooke
Joe how many Home Inspections have you done for pay.
Roy Cooke sr alias BUBBA sr.
Thousands! During my career since 1958 as an electrician and an Electrical Inspector since 1969.

I am not a Home Inspector, what's your point Bubba Sr.,

Paul knows I meant him "Bubba" anyway.

He He He Lol Lol
Reply With Quote
  #29  
Old 7/2/06, 7:07 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical Inspections by Home Inspectors

Hurry go for it!

Too late!

They are gone!

Last edited by jtedesco1; 7/2/06 at 9:23 PM..
Reply With Quote
  #30  
Old 7/2/06, 8:40 PM
John Bowman's Avatar
John Bowman John Bowman is offline
Active Poster
 
Join Date: Dec 2003
Location: ROME, PA
Posts: 2,204
Please Note: jbowman is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical Inspections by Home Inspectors

I don't see them Joe....
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Home Inspector Listings jbowman Miscellaneous Discussion for Inspectors 225 10/18/11 7:54 PM
Scumbag NAHI hits new low at ASTM meeting yesterd cmccann General Inspection Discussion 25 2/22/07 4:31 PM
Inspector Wendy's Home Inspections-Service Areas wforsyth Miscellaneous Discussion for Inspectors 57 9/6/06 12:10 AM
Buckeye Home Inspections Service Area sboyd2 Miscellaneous Discussion for Inspectors 3 9/4/06 8:21 PM


All times are GMT -4. The time now is 2:48 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts