International Association of Certified Home Inspectors
|
|||||||
| Electrical Inspections Contains discussions about electrical systems. This includes receptacles, panels, wiring, etc. |
![]() |
|
|
LinkBack | Thread Tools |
|
#1
|
||||
|
||||
|
What would you say about this?
how do I know what amp it is ? by the incoming service, it should say on the panel right? thanks for your input Eragorn Northe Der Hous Inspector LLC Certified Home Inspector Mobile - 306.684.1748 www.derhouseinspections.com |
|
#2
|
||||
|
||||
|
I don't see a mains disconnect. Any more pics?
There are also burnt neutrals on the upper right hand bus. You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell |
|
#3
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Why didn't you take a picture of the mains section of that Federal Pioneer panel?
|
|
#4
|
||||
|
||||
|
Hi to all,
Looks like a double tap 3rd from bottom on right hand bus, I am guessing that there's a main at the top of the panel out of frame, but I, never seen that kind of layout with the Neutral buss crossing the Hot busses. I agree with Mike about the neutral conections Regards Gerry "To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future." (Mark B Adams) Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida. NACHI cell 484-429-5466 NACHI02121106 |
|
#5
|
||||
|
||||
|
the main section looked ok, that is why there is not a pic here.
Eragorn Northe Der Hous Inspector LLC Certified Home Inspector Mobile - 306.684.1748 www.derhouseinspections.com |
|
#6
|
||||
|
||||
|
Quote:
yup got those ( neutrals) Eragorn Northe Der Hous Inspector LLC Certified Home Inspector Mobile - 306.684.1748 www.derhouseinspections.com Last edited by aerb; 4/20/08 at 9:44 AM.. |
|
#7
|
||||
|
||||
|
Seeing picture you can put a 200 amp panel on a 100 amp service .
Yes it usually Say's what size the panel is good for ,but that does not say that is the size of the service . service size is controlled by size incoming feed ,and disconnect/Breaker Smallest link in the chain is the deciding factor. Did one that had Breaker meter on pole and every thing in the house was two hundred amp and the agent got upset with me till I showed it was only a 35amp service. I think it had been on the pole for about 60 years~ ...Cookie Need help on inspection call my cell 613-827-2011 I like email Roycooke@hotmail.com Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun. |
|
#8
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Nevermind. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical Inspections | 19 | 8/23/11 3:56 PM |
| What's this video worth? | jtedesco1 | Inspection Education & Training | 5 | 4/18/08 9:24 AM |
| Electrical Safety Information | jtedesco1 | Electrical Inspections | 0 | 2/19/06 1:48 AM |
| Bad electrical problem | Pest Guy | Electrical Inspections | 4 | 1/20/06 9:26 PM |