Default Electrical Panel Installation

I'm sure I read before that the electrical panel must be installed on a non-flamable material such as drywall. But I think there were exceptions.

Can anyone tell me if it is true the panel must be installed on non-flamable material and are there exceptions? I suppose it would be different in ever state, but up here in Ontario Canada I'm sure there is a requirement.
Reply With Quote
  #2  
Old 9/15/06, 11:33 AM
Rob A. Parker Rob A. Parker is offline
InterNACHI Member
 
Join Date: May 2004
Location: London, ON
Posts: 405
Send a message via ICQ to rparker
Default Re: Electrical Panel Installation

Chistopher I believe it was a requirment some years ago for the panel to be installed on a non flamable material ,but I also believe that the requirment was drop just a few years ago



Rob Parker RHI CMI
ITC Level 1 Thermographer
Thamespec Inc.
www.thamespec-inspections.com
Reply With Quote
  #3  
Old 9/17/06, 5:16 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Electrical Panel Installation

Good question....now personally I install every panel on treated plywood because it looks nice and professional having the NM Cables stapled to it as they come down and into the enclosure.

But I do not recall it being a requirement per say.....now many mount panels directly to block walls and the panels are made in such a way they have a 1/4" stand off for air circulation and so on.....but in regards to the mounting on plywood.....not sure it is a big problem.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #4  
Old 9/17/06, 6:56 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical Panel Installation

Must have been a Canada thing. I have never heard of this.
All my masonary mounted panels are on plywood as Paul does, only I use A-C.

Also, how many panels have we all seen mounted to the framing of finished walls? It doesn't get much closer to flamable than that.
Reply With Quote
  #5  
Old 9/17/06, 7:17 PM
Doug Edwards,  CMI's Avatar
Doug Edwards, CMI Doug Edwards,  CMI is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Florida panhandle
Posts: 4,760
Default Re: Electrical Panel Installation

Doesn't do much good if they insist on mounting it above the clothes dryer and it is full of fine lint. Lint is an absolutely excellent emergency fire starter. Find panels in the laundry rooms are often full of it too.



"War is an ugly thing, but not the ugliest of things; the decayed and degraded state of moral and patriotic feeling which thinks nothing is worth a war, is worse. A man who has nothing which he cares more about than he does about his personal safety is a miserable creature who has no chance at being free, unless made and kept so by the exertions of better men than himself."

- John Stuart Mill







Reply With Quote
  #6  
Old 9/17/06, 7:39 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical Panel Installation

Quote:
Originally Posted by dedwards
Lint is an absolutely excellent emergency fire starter.
Especially when used inside a dryer.
Reply With Quote
  #7  
Old 9/17/06, 10:53 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,717
Default Re: Electrical Panel Installation

Quote:
Originally Posted by pabernathy
Good question....now personally I install every panel on treated plywood because it looks nice and professional having the NM Cables stapled to it as they come down and into the enclosure.
Ewwww! You use NM for wiring raceways? How barbaric!

haven't you ever heard or EMT?

PLEASE NOTE; This is just 'chain pulling' of a friends.



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #8  
Old 9/18/06, 9:34 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Electrical Panel Installation

Quote:
Originally Posted by wdecker
Ewwww! You use NM for wiring raceways? How barbaric!

haven't you ever heard or EMT?

PLEASE NOTE; This is just 'chain pulling' of a friends.
lol......WHAT........we are LESS barbaric because we use MODERN cable other than that "HARD METAL PIPE" you guys in that freakish state use...thehehehehehhe

Now see here Monkey Avatar fellow...lol......you know somethings up when 95% of the US allows NM Cable and Illinois does not......can you say...Capone..?

Me pullin back at your chains my fine fellow....



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #9  
Old 9/18/06, 9:37 AM
rwand1 rwand1 is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,861
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical Panel Installation

Chris

The requirement as Rob alluded to was dropped sometime ago by ESA.
Reply With Quote
  #10  
Old 9/18/06, 9:40 AM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,717
Default Re: Electrical Panel Installation

Paul;

I understand.

The fine art of EMT bending is a subtle thing. Well beyond most electricians grasp.



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #11  
Old 9/18/06, 9:45 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Electrical Panel Installation

lol......I bent that stuff up to 4" for nearly 12 years of my career.....I was GLAD to leave that "subtle thing" years ago...lol....

From the good ole Benfield Bender to the Hydralic Bender......my PIPE luggin days are over.....thehehe



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #12  
Old 9/19/06, 10:19 AM
brepanshek brepanshek is offline
Active Poster
 
Join Date: May 2006
Location: York, PA
Posts: 235
Please Note: brepanshek is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical Panel Installation

Hey Paul what are the requirments for fastening wires, the distance from where wires enter/exit the main panel? What I mean is that if the panel is mounted on a masonary wall about 4 feet from the ceiling, the incoming and outgoing wires need to be secured ( what 12" from box?) without plywood like you use behind your installs to fasten wires to what should I see for proper fastners for when mounted to block only?
Reply With Quote
  #13  
Old 9/19/06, 10:30 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Electrical Panel Installation

Brian,

If you are speaking of NM Cable then you should always see the cables going into enclosures via a connector for support and retention and the wires need to be fastened within 12" of the enclosure. Section 334.30

Block or plywood the support requirement is still their.....

Note: their is an exception for single gang non-metallic boxes just in case anyone wants to know...no cable securing means are needed if stapled within 8" of the box.....but I wont dable in that..if anyone wants to review the exception check out Sec 314.17(C)Ex



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 4:56 PM
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 8:28 PM
Access to Electrical Panel in Ontario by HVAC Contractors Nalliah Thayabharan Canadian Inspectors 8 5/21/07 4:01 PM
Electrical Safety Information jtedesco1 Electrical Inspections 0 2/19/06 2:48 AM