This panel is in a condo I inspected today. It looks good to me except I didn't see a ground of any sort. Am I right about calling out the ground? Did I miss anything else? Thanks for any input.
Hans |
|
#2
|
|||
|
|||
|
Typically a condo is load-side equipment.
Maybe they used the conduit for the grounding? Also, if load-side equipment, the neutral bar doesn't appear isolated with that green screw installed. InterNachi Awards Portal: http://co.nachi.org/inachiawards/ ____________________________________________ "An Education, not just an Inspection" Larry Kage, CMI Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector serving the Traverse City, Michigan area and beyond.
|
|
#3
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
If it's wired in pipe, the pipe is permitted to serve as the ground. He's right, that if this is an installation where the pipe is the ground, that bond screw needs to disappear.
|
|
#4
|
|||
|
|||
|
Please Note:
hziegenbein is a non-member guest and is in no way affiliated with InterNACHI or its members.
Thanks for the input on the conduit being used as the ground, it is attached to rigid metal conduit. The bond screw is attached to the neutral bar but not attached to or touching anything else, it just sticks out behind where you see ti screwed in, it didn't appear to really be doing anything. Do you still think it needs to be removed?
Thanks |
|
#5
|
||||
|
||||
|
It looks like it is all the way in, if not it must be too short.
I would make sure it is not reaching the panel hole and would still disclose that it is electrically correct but present where someone could tighten it therefore it should be removed. B.A. King Home Inspections, LLC www.BAKingHomeInspections.com Serving Charlotte NC area and Rock Hill SC areas. CMI Certified Master Inspector and Independent License NC2449 and SC1597 704 301-3207 "Discovery consists in seeing what everyone else has seen and thinking what no one else has thought." - Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937 |
|
#6
|
|||
|
|||
|
Agreed....If that panel is indeed a "remote" distribution panel and the conduit is being used as the 4th conductor ( technically speaking ) then yes indeed the bonding screw needs to be removed.
Paul W. Abernathy |
|
#7
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Also that 60 amp back-feed breaker needs to be secured.
|
|
#8
|
|||
|
|||
|
Quote:
(F) Back-Fed Devices Plug-in-type overcurrent protection devices or plug-in type main lug assemblies that are backfed and used to terminate field-installed ungrounded supply conductors shall be secured in place by an additional fastener that requires other than a pull to release the device from the mounting means on the panel. Paul W. Abernathy |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Download the videos here all about physics and electricity | jtedesco1 | Electrical Inspections | 5 | 9/14/08 3:58 PM |
| Electrical Panel Installation | csteele | Electrical Inspections | 12 | 9/19/06 9:30 AM |
| Electrical panel popping | senomoto | Electrical Inspections | 17 | 6/18/06 11:17 AM |
| Chicagoland Electrical Code Ordinance | jtedesco1 | Electrical Inspections | 0 | 6/16/06 2:10 PM |
| Sup panel question? | jlybolt | Electrical Inspections | 23 | 6/12/06 8:42 PM |