Please Note: hziegenbein is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Electrical panel question

This panel is in a condo I inspected today. It looks good to me except I didn't see a ground of any sort. Am I right about calling out the ground? Did I miss anything else? Thanks for any input.

Hans
Attached Thumbnails
electrical-panel-question-panel-1.jpg   electrical-panel-question-panel-2.jpg  
Reply With Quote
  #2  
Old 3/12/07, 8:27 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,745
Default Re: Electrical panel question

Typically a condo is load-side equipment.

Maybe they used the conduit for the grounding?

Also, if load-side equipment, the neutral bar doesn't appear isolated with that green screw installed.



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #3  
Old 3/12/07, 9:01 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical panel question

If it's wired in pipe, the pipe is permitted to serve as the ground. He's right, that if this is an installation where the pipe is the ground, that bond screw needs to disappear.
Reply With Quote
  #4  
Old 3/12/07, 9:19 PM
hziegenbein hziegenbein is offline
New User
 
Join Date: Mar 2005
Location: Chicago, IL
Posts: 10
Please Note: hziegenbein is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical panel question

Thanks for the input on the conduit being used as the ground, it is attached to rigid metal conduit. The bond screw is attached to the neutral bar but not attached to or touching anything else, it just sticks out behind where you see ti screwed in, it didn't appear to really be doing anything. Do you still think it needs to be removed?
Thanks
Reply With Quote
  #5  
Old 3/12/07, 9:24 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 2,224
Default Re: Electrical panel question

It looks like it is all the way in, if not it must be too short.

I would make sure it is not reaching the panel hole and would still disclose that it is electrically correct but present where someone could tighten it therefore it should be removed.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207
Reply With Quote
  #6  
Old 3/16/07, 6:09 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Electrical panel question

Agreed....If that panel is indeed a "remote" distribution panel and the conduit is being used as the 4th conductor ( technically speaking ) then yes indeed the bonding screw needs to be removed.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #7  
Old 3/16/07, 9:23 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical panel question

Also that 60 amp back-feed breaker needs to be secured.
Reply With Quote
  #8  
Old 3/17/07, 3:11 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Electrical panel question

Quote:
Originally Posted by Speedy Petey
Also that 60 amp back-feed breaker needs to be secured.
Yeppers...

(F) Back-Fed Devices
Plug-in-type overcurrent protection devices or plug-in type main
lug assemblies that are backfed and used to terminate field-installed ungrounded supply
conductors shall be secured in place by an additional fastener that requires other than a
pull to release the device from the mounting means on the panel.




Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Download the videos here all about physics and electricity jtedesco1 Electrical 5 9/14/08 4:58 PM
Electrical Panel Installation csteele Electrical 11 9/19/06 10:30 AM
Electrical panel popping senomoto Electrical 17 6/18/06 12:17 PM
Chicagoland Electrical Code Ordinance jtedesco1 Electrical 0 6/16/06 3:10 PM
Sup panel question? jlybolt Electrical 23 6/12/06 9:42 PM


All times are GMT -4. The time now is 11:05 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts