Default Electrical panel question

This panel is in a condo I inspected today. It looks good to me except I didn't see a ground of any sort. Am I right about calling out the ground? Did I miss anything else? Thanks for any input.

Hans
Attached Thumbnails
electrical-panel-question-panel-1.jpg   electrical-panel-question-panel-2.jpg  
Reply With Quote
  #2  
Old 3/12/07, 7:27 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: Electrical panel question

Typically a condo is load-side equipment.

Maybe they used the conduit for the grounding?

Also, if load-side equipment, the neutral bar doesn't appear isolated with that green screw installed.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #3  
Old 3/12/07, 8:01 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical panel question

If it's wired in pipe, the pipe is permitted to serve as the ground. He's right, that if this is an installation where the pipe is the ground, that bond screw needs to disappear.
Reply With Quote
  #4  
Old 3/12/07, 8:19 PM
hziegenbein hziegenbein is offline
New User
 
Join Date: Mar 2005
Location: Chicago, IL
Posts: 10
Please Note: hziegenbein is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical panel question

Thanks for the input on the conduit being used as the ground, it is attached to rigid metal conduit. The bond screw is attached to the neutral bar but not attached to or touching anything else, it just sticks out behind where you see ti screwed in, it didn't appear to really be doing anything. Do you still think it needs to be removed?
Thanks
Reply With Quote
  #5  
Old 3/12/07, 8:24 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,206
Default Re: Electrical panel question

It looks like it is all the way in, if not it must be too short.

I would make sure it is not reaching the panel hole and would still disclose that it is electrically correct but present where someone could tighten it therefore it should be removed.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #6  
Old 3/16/07, 5:09 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Electrical panel question

Agreed....If that panel is indeed a "remote" distribution panel and the conduit is being used as the 4th conductor ( technically speaking ) then yes indeed the bonding screw needs to be removed.



Paul W. Abernathy
Reply With Quote
  #7  
Old 3/16/07, 8:23 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical panel question

Also that 60 amp back-feed breaker needs to be secured.
Reply With Quote
  #8  
Old 3/17/07, 2:11 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Electrical panel question

Quote:
Originally Posted by Speedy Petey
Also that 60 amp back-feed breaker needs to be secured.
Yeppers...

(F) Back-Fed Devices
Plug-in-type overcurrent protection devices or plug-in type main
lug assemblies that are backfed and used to terminate field-installed ungrounded supply
conductors shall be secured in place by an additional fastener that requires other than a
pull to release the device from the mounting means on the panel.




Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Download the videos here all about physics and electricity jtedesco1 Electrical Inspections 5 9/14/08 3:58 PM
Electrical Panel Installation csteele Electrical Inspections 12 9/19/06 9:30 AM
Electrical panel popping senomoto Electrical Inspections 17 6/18/06 11:17 AM
Chicagoland Electrical Code Ordinance jtedesco1 Electrical Inspections 0 6/16/06 2:10 PM