Default electrical quandry for the GURU

"quandry" instersting word, isnt it.

Here is what I have:

New construction. Square D 400 amp rate Box. The plans call for the main disconnect to be 22,000 Vac. Max (whatever that is).The listed breaker for that is a QO-OH breaker. There area two distribution panels, and one service pane. There is one 125 amp QB125 breaker and one 150 amp QB150 breaker.

On the plans it states that the interrupting short circuit amps at the meter bank = 17812 AMPS. Use 22,00 ALL Minumuim

According to the electrical inspector, these breakers will not trip if there is a power surge to the box but they will burn, leaving the house unprotected.

Any thoughts on this.
Reply With Quote
  #2  
Old 6/15/07, 4:22 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: electrical quandry for the GURU

Interupting capacity has to do with the ability of the breaker to "clear" a short circuit and is rated in Amps.
The plan is calling for breakers rated to intterupt a 22,000A short circuit.

Last edited by mlarson; 6/15/07 at 4:39 PM..
Reply With Quote
  #3  
Old 6/15/07, 4:29 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: electrical quandry for the GURU

This refers to the maximum current the breaker can "break" without burning up or arcing over.
This is the same thing I was talking to Marc about a couple days ago. Service conductors are not really protected against overcurrent so the utility will provide the installer information about the maximum available fault current if you have a dead short. This is based on the service conductor size, length and transformer serving the building.
It is not uncommon to get a blanket answer of "greater than 10,000a, less than 22,000" if you are not willing to buy "engineering" and that precludes the regular 10ka breaker.
Reply With Quote
  #4  
Old 6/15/07, 4:34 PM
William E. Siegel William E. Siegel is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 1,788
Default Re: electrical quandry for the GURU

So then they are using the wrong breakers at the service panel??
Reply With Quote
  #5  
Old 6/15/07, 6:11 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: electrical quandry for the GURU

Quote:
Originally Posted by wsiegel
So then they are using the wrong breakers at the service panel??
So far, you're giving us about half of what we'd need to say for sure, and some of what you've provided is bad information. You talk about QB breakers. A type QB breaker is a Zinsco breaker. Perhaps you mean QOB? There is a 22K AIC rated version of a QOB. What is the catalog number of the panel that concerns you?
Reply With Quote
  #6  
Old 6/15/07, 7:11 PM
William E. Siegel William E. Siegel is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 1,788
Default Re: electrical quandry for the GURU

Mark,

I do not have the catalogue number of the panel. The breaker i listed was copied from the panel cover and it was a Square D. If it helps, this is a 400 amp rated panel that was installed within the last year and a half. I wish I had pictures, but I left my camera home today. The concern is if these breakers are the right size for the feeds if there is a short. As you can tell, this is not my area of expertise. Let me know what information you need and I will try and get it.
Reply With Quote
  #7  
Old 6/15/07, 10:29 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: electrical quandry for the GURU

Looks like an ENG has already done a one line diagram for the installation and has listed the SCC as 17812 for that figure. If this is the case the 22KVA AIC is fine for the application on THAT bank......now it is important to have a full and detailed one line diagram drawing as I am guessing this is an industrial application or high end commerical layout.

What you need to do is contact the manufacturer or supply house and they can give you the rating of the breakers in question. But depending on their location the ratings can change.....the 17812 is at the first main I am guessing......once it gets down stream the SCC changes from point to point and it will need to be calculated out....



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #8  
Old 6/21/07, 3:25 AM
John Burgess John Burgess is offline
New User
 
Join Date: Apr 2007
Posts: 1
Please Note: John Burgess is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: electrical quandry for the GURU

Marc,
Square D renamed it's Q2 frame brakers
QB is 10k interupt
QD is 25 k interupt
a QBL200 is a 200 amp 10 k breaker.
Reply With Quote
  #9  
Old 6/21/07, 8:25 AM
William E. Siegel William E. Siegel is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 1,788
Default Re: electrical quandry for the GURU

I have been on the phone with Square D for two days. The information first listed above is correct. The service breakers are not rated for the system or the plans. Looks like the electrician tried to take the cheap way out, as the installed breakers are much less expensive than what should be in this box
Reply With Quote
  #10  
Old 7/14/07, 12:15 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: electrical quandry for the GURU

Interesting point here also to be considered.....since many commerical and industrial buildings are changing their transformers and so on to more low eff. rated units...we are seeing more transformers going from 5% imp. to low 2% and 3% imp.....and the result of less impedance is higher ampacity and thus higher AIC flash issues......so important to remember this.....

If you know they change the transformers or make additions to the layout the entire safety plan needs to be updated, single line drawings need to be updated and so on.....it becomes a chain of events.

While we are making transformers BETTER.....we have to remember if someone changes the unit....it effects everything else down stream even the AIC issues.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #11  
Old 7/15/07, 9:15 AM
Pierre Belarge Pierre Belarge is offline
Active Poster
 
Join Date: Apr 2006
Posts: 202
Please Note: Pierre Belarge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: electrical quandry for the GURU

Quote:
Originally Posted by pabernathy
Interesting point here also to be considered.....since many commerical and industrial buildings are changing their transformers and so on to more low eff. rated units...we are seeing more transformers going from 5% imp. to low 2% and 3% imp.....and the result of less impedance is higher ampacity and thus higher AIC flash issues......so important to remember this.....

If you know they change the transformers or make additions to the layout the entire safety plan needs to be updated, single line drawings need to be updated and so on.....it becomes a chain of events.

While we are making transformers BETTER.....we have to remember if someone changes the unit....it effects everything else down stream even the AIC issues.
To add to Paul's post, the transformers are also being installed closer to buildings (including the larger homes) and this lowers the impedance as well.
I think that not enough effort by some in our industry is being applied just to this sort of scenario.



I do not think that the electrical contractor was ignoring the ratings specified, maybe he just is not used to the differences, especially if this is a large home. Is it a large home or commercial?
I also see he is going to have an expensive change coming his way.
Reply With Quote
  #12  
Old 7/15/07, 9:51 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: electrical quandry for the GURU

You know Pierre....I agree so much with that statement my friend. The sad thing in our OWN industry is the lack of education on this growing concern with NFPA 70E and Electrical Safety.........the facts remain it is still the most neglected area looked at in safety concern today in many industrial and commerical settings and it is even growing more of a concern with like you said CLOSE installations to dwellings....

I noticed a HUGE jump in my NFPA 70E class requests as the years went on....people are slowly starting to understand the concerns.......



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical 6 9/15/08 8:57 AM
Download the videos here all about physics and electricity jtedesco1 Electrical 5 9/14/08 4:58 PM
Handbook for Electrical Safety pabernathy Electrical 1 1/1/07 2:14 PM
Chicagoland Electrical Code Ordinance jtedesco1 Electrical 0 6/16/06 3:10 PM
Electrical Safety Information jtedesco1 Electrical 0 2/19/06 2:48 AM


All times are GMT -4. The time now is 2:51 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts