I have a few electrical questions that I hope someone can help me with. I am sorry for being lengthy. I tried elsewhere before posting here, but short of going to the county office, this is the best bet out there.

1.) I have read on codecheck(which sounds like info may be flaw after some research) that any wall greater than 2 ft must have a receptacle unless the wall is not useable. Is this true? I have a wall that is 38" long from corner to entrance opening (no framed door) and the only purpose placing a receptacle there may serve is for vacuuming. This wall is actually in the dinning room.

2.) If I have to put a receptacle on that wall, can I get away with branching a second line off of another receptacle to power the added receptacle. This rec, would have a power wire, a wire going to a second rec, and then a third going to new recepticle. All boxes are 20.3 In. cubed. All wiring is new 12-2.

3.) When the term "wall" is used, does that mean on that particular side of the wall? I have a recepacle on the opposite side of the wall that could easily be accessed through the room entrance.

4.) I have a rather odd kitchen (House was added onto at some point and the rooms were changed around). The kitchen is 9X9 wall to wall and U shapped layout. The kitchen has only one light above the sink and is controlled by a switch that requires you to walk to the opposite side of the room to turn on. I am replacing this light, plus adding a central light. Because of the layout, the only place to put a switch at room opening is on the hallway wall right before you enter the room. Does this sound like an acceptable practice?

5.) Also, I am planning on moving my kitchen in 5-7 yrs, but I am planning parts of the circuit now. Is it acceptable to have both the kitchen and the dinning room lights only on the same circuit? Keep in mind I am in full understanding (I think) of the rest of the kitchen circuit reqiurements, but I am unclear on lighting. To me, It sounds extremely overkill if I am required to have a separate circuit for both the kitchen and dinning room lights.

6.) Does anyone see any showstoppers with what I describe above that I would be required to fix if I sold my house? My intent is to re-wire these areas as correctly as possible so when I sell, the buyer has most correct house instead of the rats nest I am dealing with.

7.) If a room is remodeled, what is the code requirements now for that particular room? Is it grandfatered, but recommended to update to current code?

Thanks for all your help.
Reply With Quote
  #2  
Old 2/22/07, 10:13 AM
jbreazeale jbreazeale is offline
Active Poster
 
Join Date: Aug 2006
Location: Sardis, MS
Posts: 618
Please Note: jbreazeale is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical Questions - Please help

Well, Adam...you really are full of questions, aren't you? You sound pretty handy, and I can answer all your questions, but I encourage you to get yourself a copy of the 2006 International Residential Code, and the NEC (National Electrical Code). They make for boring and ambiguous reading, but there is a lot of good info in there for the amateur remodeler that may save you some heartache down the road. The answers to your questions, in order, are:

1) Yes. An exception is that there is another receptacle within 6 feet of any appliance that may be located on the 38" wall, so you may be ok.

2) NO! nuff sed

3) Yes. Always, it is the SURFACE that is considered, not the whole structural unit.

4) That's ok---but is there REALLY NO place to locate a switch inside the kitchen? Why not control both lights with the existing switch leg? This should not create a load problem, as switches are general rated at 15 amps. I know of no lighting you might locate in a kitchen that would come near that.

5) Yes, as long as the total amps for your lighting circuit does not exceed 80% of the listed load capacity of the overcurrent device. For instance, if you are using a 15 amp breaker, make sure that the total lighting load does not exceed 12 amps, or 80% of 15.

6) The inconvenience of having the kitchen light switch located outside the room might turn some buyers off, especially the person who is going to be IN the kitchen the most. We know who that usually is, and if Mama ain't happy, ain't nobody happy.

7) This depends on the requirements of your local authority. Check with them about permit requirements. Some jurisdictions have no local restrictions or permit requirements at all.

Hope this helps. And make sure you know what you are doing BEFORE you begin!
Reply With Quote
  #3  
Old 2/22/07, 8:00 PM
Adam Demarco Adam Demarco is offline
New User
 
Join Date: Feb 2007
Posts: 4
Please Note: Adam Demarco is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical Questions - Please help

Thanks for the response! It has helped me a lot. I am sorry for so many questions! I was worried no one would respond because of it. I need to get a copy of those codes bad! I want to do things the right way. Let me know if you know a shortcut to finding it. I am going to look on this site. I like this site and I am glad I ran across it.

This kitchen is wierd. There is a switch in the kitchen, but you have to walk through the kitchen to get to it. Right now, we naturally turn the light on in the dinning room (accross the hall) so we can see the kitchen switch at night. When you walk in, the left wall is lined with the fridge then the pantry. On the right side you have the stove and 2 ft of counter on each side. Maybe I can get a switch in there some how for the general lighting and leave the over sink light switch where it is at. Is there any code requirements for distance of switch to actual sink. I know it all needs to be GFI.

Thanks.

Last edited by Adam Demarco; 2/22/07 at 8:30 PM..
Reply With Quote
  #4  
Old 2/22/07, 10:35 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical Questions - Please help

You might want to think about a motion controlled light in the kitchen. That makes the location of the switch less important. It also keeps the wife and kids from using the refrigerator as a night light. I have them everywhere.
Reply With Quote
  #5  
Old 2/24/07, 5:59 PM
smcarthur smcarthur is offline
New User
 
Join Date: Jul 2006
Location: Rock Hill, SC
Posts: 96
Please Note: smcarthur is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical Questions - Please help

Why the no answer to question #2. Adding another receptacle to an existing circuit is perfectly acceptable in most situations. In the dining room, I don't see a problem as long as the receptacle is added to a 20 amp circuit, since all dining room circuits are required to be 20 amps. The box fill would be 20.25 cu.in. which would not exceed the limit on the box.
Reply With Quote
  #6  
Old 2/24/07, 10:23 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Electrical Questions - Please help

Quote:
Originally Posted by Adam Demarco
I have a few electrical questions that I hope someone can help me with. I am sorry for being lengthy. I tried elsewhere before posting here, but short of going to the county office, this is the best bet out there.

1.) I have read on codecheck(which sounds like info may be flaw after some research) that any wall greater than 2 ft must have a receptacle unless the wall is not useable. Is this true? I have a wall that is 38" long from corner to entrance opening (no framed door) and the only purpose placing a receptacle there may serve is for vacuuming. This wall is actually in the dinning room.

ANSWER: 210.52(A)(2) says that any space 2 feet or more in width ( includeding space measured around corners) and unbroken along the floorline by doorways, fireplaces and similar openings.....so to be honest with you if this space you speak of has lets say a door on one side and an opening on the other.......then it would need a receptacle in this space....thats not Codecheck..thats the NEC.

2.) If I have to put a receptacle on that wall, can I get away with branching a second line off of another receptacle to power the added receptacle. This rec, would have a power wire, a wire going to a second rec, and then a third going to new recepticle. All boxes are 20.3 In. cubed. All wiring is new 12-2.

Answer: That really depends on the circuit you are adding from...if space is part of the dining room and you are going to ADD the receptacle from the dining room and the receptacle will STAY in the dining room then it is fine, if it leaves the dining room...NOPE you can't add it then. Remember you can't add that receptacle IN a dining room from lets say the living back to back with it........would Have to be added from the dining room circuit if the wall space is IN the dining room area.

3.) When the term "wall" is used, does that mean on that particular side of the wall? I have a recepacle on the opposite side of the wall that could easily be accessed through the room entrance.

Answer: The doorway of the other room requires you to start the measurement OVER again at the doorway...nope..you can't WRAP around it into another room and use that receptacle location to meet the space requirement...sorry...not that easy...

4.) I have a rather odd kitchen (House was added onto at some point and the rooms were changed around). The kitchen is 9X9 wall to wall and U shapped layout. The kitchen has only one light above the sink and is controlled by a switch that requires you to walk to the opposite side of the room to turn on. I am replacing this light, plus adding a central light. Because of the layout, the only place to put a switch at room opening is on the hallway wall right before you enter the room. Does this sound like an acceptable practice?

Answer: sure, if thats where you want it....nothing says that the switch has to be in the same room with the light....BUT in a kitchen you really MUSt have a switched light......but if you wish to add it at that location thats really your choice.....just make sure you are not adding these lights onto the same circuit as your small appliance circuit since it is a old kitchen....if adding additional lights and so on.....and by chance it is ON with the small appliance circuit ( may happen sometimes in older homes ) then I would suggest you possibly feeding the lights from another location....just some advice.

5.) Also, I am planning on moving my kitchen in 5-7 yrs, but I am planning parts of the circuit now. Is it acceptable to have both the kitchen and the dinning room lights only on the same circuit? Keep in mind I am in full understanding (I think) of the rest of the kitchen circuit reqiurements, but I am unclear on lighting. To me, It sounds extremely overkill if I am required to have a separate circuit for both the kitchen and dinning room lights.

Answer: as long as you are sizing the circuits properly and so on....nothing says you can't have the lighting in the kitchen and dining room on the same circuit.....no problem at all...

6.) Does anyone see any showstoppers with what I describe above that I would be required to fix if I sold my house? My intent is to re-wire these areas as correctly as possible so when I sell, the buyer has most correct house instead of the rats nest I am dealing with.

Answer: just read the above answers and you should be fine.

7.) If a room is remodeled, what is the code requirements now for that particular room? Is it grandfatered, but recommended to update to current code?

Answer: tough question....you need to call your local building official and see what they say....we can only GUESS as some states have different requirements and some local government offices have their own AHJ requirements....better to check with them than to listen to us GUESS for you...usually if you add a light or so it is not a problem.....anything thats an improvment is a enhancement in many AHJ's eyes...in our area to bring it up to CURRENT "CODE" you have to gut down the walls.....and do a true remodel of the room....if you are planning on doing that then chances are yes you would need to have a permit and may be required to bring it up to current standards.

Thanks for all your help.
Here are my REPLIES- They are in RED



Paul W. Abernathy
Reply With Quote
  #7  
Old 2/24/07, 11:41 PM
jbreazeale jbreazeale is offline
Active Poster
 
Join Date: Aug 2006
Location: Sardis, MS
Posts: 618
Please Note: jbreazeale is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical Questions - Please help

This one is for Steve Mc.

Steve, the reason I said no stems from the description of how it would be done. As I understand what was said in the original question, the receptacle that would be wired FROM already in in the line of an existing circuit...meaning, wiring in, wiring out already in place. The poster is talking about feeding a THIRD receptacle for the dining area from that receptacle, which means that he would either have to pigtail out. Actually, I was afraid he might try to backwire it out, and that the wired-from receptacle might eventually get cooked!

As for the short wall, the way I read the post, the room comes to a corner from the door, and there is a receptacle on the right angle wall within 6 feet, which makes him ok on that. Maybe I read it wrong. IF the wall space is broken, and that 38" stands alone, then one should be installed.

Isn't it amazing how one or two words can change the whole meaning of things? My brother, an ace auto mechanic, calls me about electrical stuff all the time. He has his cell in one hand, tools in the other while I try to take him through stuff. Sometimes it gets agonizing, because his terminology and descriptions aren't "trade", but somehow we have managed to succeed most of the time. Managed to trouble shoot his heat system about two months ago...my knowledge, his eyes and hands, step by step...once we knew we were on the same page with words.

Language made civilization possible
EFFECTIVE language makes it possible to work smoothly.
Reply With Quote
  #8  
Old 2/25/07, 12:52 PM
smcarthur smcarthur is offline
New User
 
Join Date: Jul 2006
Location: Rock Hill, SC
Posts: 96
Please Note: smcarthur is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical Questions - Please help

Quote:
Originally Posted by jbreazeale
This one is for Steve Mc.

Steve, the reason I said no stems from the description of how it would be done. As I understand what was said in the original question, the receptacle that would be wired FROM already in in the line of an existing circuit...meaning, wiring in, wiring out already in place. The poster is talking about feeding a THIRD receptacle for the dining area from that receptacle, which means that he would either have to pigtail out. Actually, I was afraid he might try to backwire it out, and that the wired-from receptacle might eventually get cooked!
I still don't see a problem, yes it would have to be pigtailed and I didn't think about back stabbing because back stabbing 12awg is not allowed, but I should have included that in my answer. I also should have included that he should have the work performed by a licensed electrician.
Reply With Quote
  #9  
Old 2/25/07, 9:59 PM
David C. Mull, CMI's Avatar
David C. Mull, CMI David C. Mull, CMI is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Lititz, PA
Posts: 33
Default Re: Electrical Questions - Please help

After all that, "good stuff", I completely agree, he should have the work performed by a licensed electrician. Homeowners can only get so far before they get out there to far. Then the branch breaks....
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Download the videos here all about physics and electricity jtedesco1 Electrical Inspections 5 9/14/08 3:58 PM
Handbook for Electrical Safety pabernathy Electrical Inspections 1 1/1/07 1:14 PM
Some good questions that always need answers jtedesco1 Electrical Inspections 5 6/16/06 9:10 PM
Electrical Safety Information jtedesco1 Electrical Inspections 0 2/19/06 1:48 AM


All times are GMT -4. The time now is 3:27 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts