Default Electrical receptacles / House built in 1953

I inpsected a house built in 1953, the recectacles were three prong,
but they all tested open ground.....would this be because back then the
houses were wired with two wires ? no ground wire.


if so how should I write it up.....


David
Reply With Quote
  #2  
Old 1/28/08, 10:48 PM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical receptacles / House built in 1953

If the receptacles were of the three wire type they should be protected by GFCI.

If they are not protected with a GFCI device then that is what your statement should point out as well as there is no Equipment grounding conductor.
Reply With Quote
  #3  
Old 1/28/08, 11:45 PM
rbrady's Avatar
rbrady rbrady is offline
Active Poster
 
Join Date: Feb 2007
Location: Eureka, CA
Posts: 619
Please Note: rbrady is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical receptacles / House built in 1953

Here is my report comment:
"Most of the electrical system does not incorporate a grounding conductor (*). Rewire, use 2-prong receptacles and/or separately grounded receptacles as required. Avoid use of ungrounded 3-prong receptacles and adapters to reduce risk of electrical shock and to provide protection for sensitive electronic equipment. See body of report for locations of 'open ground' and 'no ground' (two prong) receptacles."

At the beginning of my report I have a statement that says "The asterisk after certain report comments denotes items that were typically standard practice at the time of construction"

Personally, I don't like the GFCI approach. Surge protection devices do not work without a proper ground. GFCI can also trip with motor related surges.

Here is a link to a page I created which I use in my reports:
http://www.bradyinspects.com/house_electric.html

Reply With Quote
  #4  
Old 1/29/08, 2:50 PM
wsiegel wsiegel is offline
Active Poster
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 3,041
Please Note: wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical receptacles / House built in 1953

Why would you want ot rewire with 2 prong receptacles?
Reply With Quote
  #5  
Old 1/29/08, 3:04 PM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical receptacles / House built in 1953

In a system where there is no equipment grounding conductor present then the installation of a three wire device would require the installation of an equipment grounding conductor or the use of GFCI devices.

If an equipment grounding conductor is installed it must be installed to one of the following:
(1) Any accessible point on the grounding electrode system as described in 250.50
(2) Any accessible point on the grounding electrode conductor
(3) The equipment grounding terminal bar within the enclosure where the branch circuit for the receptacle or branch circuit originates
(4) For grounded systems, the grounded service conductor within the service equipment enclosure
(5) For ungrounded systems, the grounding terminal bar within the service equipment enclosure

If a GFCI device is used it must:
(c) A non–grounding-type receptacle(s) shall be permitted to be replaced with a grounding-type receptacle(s) where supplied through a ground-fault circuit interrupter. Grounding-type receptacles supplied through the ground-fault circuit interrupter shall be marked “GFCI Protected” and “No Equipment Ground.” An equipment grounding conductor shall not be connected between the grounding-type receptacles.


Any other replacement must be a two wire receptacle.

On a 120 volt circuit surge protection will dissipate the surge through the grounded (neutral) conductor and there is no need for an equipment grounding conductor to be present for them to work properly.
Reply With Quote
  #6  
Old 1/29/08, 3:06 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Missouri
Posts: 25,037
Default Re: Electrical receptacles / House built in 1953

Quote:
Originally Posted by rbrady
Surge protection devices do not work without a proper ground.

Yes, they do.
Reply With Quote
  #7  
Old 1/29/08, 5:20 PM
rbrady's Avatar
rbrady rbrady is offline
Active Poster
 
Join Date: Feb 2007
Location: Eureka, CA
Posts: 619
Please Note: rbrady is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical receptacles / House built in 1953

Quote:
Originally Posted by Mike Whitt
On a 120 volt circuit surge protection will dissipate the surge through the grounded (neutral) conductor and there is no need for an equipment grounding conductor to be present for them to work properly.


"A word about grounding: most suppressors and EFI filters require real grounds. Any that don't are next to useless. For example, most surge suppressors use MOVs (metal oxide varistors) to "clamp" overvoltages. Yes, you can have a suppressor that only has a MOV between neutral and hot to combat differential-mode voltage excursions, but that isn't enough. You need common-mode protection too. Good suppressors should have 3 MOVs, one between each pair of wires. Whichmeans you should have a good solid ground. Eg: a solidly connected 14ga wire back to the panel.
Not rusty BX armour or galvanized pipe with condensation turning the copper connection green. Without a ground, a surge or spike is free to "lift" your entire electronics system well away from ground. Which is ideal for blowing out interface electronics for printer ports etc. Secondly, static electricity is one of the major enemies of electronics. Having good frame grounds is one way of protecting against static zaps. If you're in the situation of wanting to install computer equipment on two wire groundless circuits take note: Adding a GFCI outlet to the circuit makes the circuit safe for you.
But it doesn't make it safe for your equipment - you need a ground to make surge suppressors or line filters effective."





Copyright 1991-2004 Steven Bellovin (smb(at)research.att.com) Chris Lewis (clewis(at)ferret.ocunix.on.ca)


Reply With Quote
  #8  
Old 1/29/08, 5:22 PM
rbrady's Avatar
rbrady rbrady is offline
Active Poster
 
Join Date: Feb 2007
Location: Eureka, CA
Posts: 619
Please Note: rbrady is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical receptacles / House built in 1953

Quote:
Originally Posted by wsiegel
Why would you want ot rewire with 2 prong receptacles?
You would not rewire with a 2-prong receptacle. You would either rewire (with new romex) or replace the 'open ground' receptacle with a 2-prong receptacle.

Last edited by rbrady; 1/29/08 at 5:38 PM..
Reply With Quote
  #9  
Old 1/29/08, 5:56 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 52,616
Default Re: Electrical receptacles / House built in 1953

Quote:
Originally Posted by rbrady
You would not rewire with a 2-prong receptacle. You would either rewire (with new romex) or replace the 'open ground' receptacle with a 2-prong receptacle.
It is also acceptable to replace them with GFCIs and label the outlets as "no equipment ground provided".
Reply With Quote
  #10  
Old 1/29/08, 6:36 PM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical receptacles / House built in 1953

Quote:
Originally Posted by rbrady
"A word about grounding: most suppressors and EFI filters require real grounds. Any that don't are next to useless. For example, most surge suppressors use MOVs (metal oxide varistors) to "clamp" overvoltages. Yes, you can have a suppressor that only has a MOV between neutral and hot to combat differential-mode voltage excursions, but that isn't enough. You need common-mode protection too. Good suppressors should have 3 MOVs, one between each pair of wires. Whichmeans you should have a good solid ground. Eg: a solidly connected 14ga wire back to the panel.
Not rusty BX armour or galvanized pipe with condensation turning the copper connection green. Without a ground, a surge or spike is free to "lift" your entire electronics system well away from ground. Which is ideal for blowing out interface electronics for printer ports etc. Secondly, static electricity is one of the major enemies of electronics. Having good frame grounds is one way of protecting against static zaps. If you're in the situation of wanting to install computer equipment on two wire groundless circuits take note: Adding a GFCI outlet to the circuit makes the circuit safe for you.
But it doesn't make it safe for your equipment - you need a ground to make surge suppressors or line filters effective."








Copyright 1991-2004 Steven Bellovin (smb(at)research.att.com) Chris Lewis (clewis(at)ferret.ocunix.on.ca)



No disrespect meant toward you or either of these fine authors but I believe that I would trust someone in the electrical field instead of someone that is a computer program designer.

Most of the surge protecters that are bought off the shelf at the local stores will operate on a 120 volt circuit regaurdless of an equipment grounding conductor.

Todays electonics are a lot more forgiving that those in the past.
Reply With Quote
  #11  
Old 1/29/08, 6:48 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 52,616
Default Re: Electrical receptacles / House built in 1953

Quote:
Originally Posted by Mike Whitt
No disrespect meant toward you or either of these fine authors but I believe that I would trust someone in the electrical field instead of someone that is a computer program designer.

Most of the surge protecters that are bought off the shelf at the local stores will operate on a 120 volt circuit regaurdless of an equipment grounding conductor.

Todays electonics are a lot more forgiving that those in the past.
Mike,
Not meant to argue in anyway but I was an electronic tec and later an engineer.
The post(Ralph's) you quoted is referring to common mode signals that would appear on both the grounded and ungrounded conductor at the same time. Without a path to ground from both damage to the equipment could occur.
Reply With Quote
  #12  
Old 1/29/08, 6:54 PM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 4,368
Default Re: Electrical receptacles / House built in 1953

as HI best to err on the side of caution instead of awaiting the right set of circumstances to disprove what you've stated in a report



badair

ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year
National Association of Commercial Building Inspectors & Thermographers™ Member ID 12011-14TX

life is the random lottery of events followed by numerous narrow escapes, accept the good
Reply With Quote
  #13  
Old 1/29/08, 7:55 PM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical receptacles / House built in 1953

Quote:
Originally Posted by badair
as HI best to err on the side of caution instead of awaiting the right set of circumstances to disprove what you've stated in a report
Words well spoken and some that we all (HIs and sparkys) including myself should listen to.
Reply With Quote
  #14  
Old 1/29/08, 8:47 PM
Joe Farsetta's Avatar
Joe Farsetta Joe Farsetta is offline
InterNACHI Member
 
Join Date: Oct 2002
Location: Pearl River, NY
Posts: 5,838
Default Re: Electrical receptacles / House built in 1953

Mike,

Chiming in with Mike L, I too have lived through the nightmare of dirty power sources on sophsticated electronic equipment, including communications and computer equipment.

I've gotten into plenty of discussions with commercial electricians in years past over the need for a clean, real ground.
Reply With Quote
  #15  
Old 1/29/08, 11:24 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical receptacles / House built in 1953

Quote:
Originally Posted by dnasser
I inpsected a house built in 1953, the recectacles were three prong,
but they all tested open ground.....would this be because back then the
houses were wired with two wires ? no ground wire.

I'm mildly shocked that nobody has expressed concern that the person who wrote the above information appears to be actively inspecting homes and charging money for it.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Electrical Fire Safety jtedesco1 Electrical Inspections 3 2/1/08 10:02 AM
Electrical Safety Principles pabernathy Electrical Inspections 8 1/1/07 2:13 PM
Electrical Safety Information jtedesco1 Electrical Inspections 0 2/19/06 2:48 AM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 10:26 PM
Wired for Safety Video jtedesco1 Electrical Inspections 0 1/4/06 7:31 AM

All times are GMT -4. The time now is 5:50 PM.
no new posts