Default Electrical Service Panels. Please proof this new inspection article.

http://www.nachi.org/electrical-service-panels.htm



Nick Gromicko, Certified Master Inspector

Find a Home Inspector
"Just as iron sharpens iron, one man sharpens another." Proverbs 27:17
Reply With Quote
Need a home inspection in Hawaii? Check out InterNACHI's listing of Hawaii certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 1/6/10, 10:35 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Electrical Service Panels. Please proof this new inspection article.

Just remember that service equipment can have circuit breakers or fuses as well. Also in many older panels with poor connections due to oxidation in the case of a aluminum buss bar of a zinsco...you may also hear arching as well and could be a sign of problems.

In some panels be it old and new, the physical contact points of the OCPD to the contact point of the buss may not be making good contact which will generate an arch which over time will increase in heat and become a potential fire hazard to be aware of. This can come from improperly listed devices in the panels as well or over time due to age where the tension of the contact points weaken.



Paul W. Abernathy
Reply With Quote
  #3  
Old 1/7/10, 8:28 AM
Rob London Rob London is offline
InterNACHI Member
 
Join Date: May 2009
Posts: 237
Default Re: Electrical Service Panels. Please proof this new inspection article.

Quote:
Originally Posted by pabernathy View Post

In some panels be it old and new, the physical contact points of the OCPD to the contact point of the buss may not be making good contact

How can inspectors check for that?

Thanks Paul



Researcher and Technical Writer, InterNACHI
Reply With Quote
  #4  
Old 1/7/10, 9:19 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical Service Panels. Please proof this new inspection article.

Inspectors can check for the following defective conditions during an electrical panel inspection:
  • insufficient clearance. According to the 2008 National Electrical Code, most residential electrical panels require at least a 3-foot clearance or working space in front, 30 inches on either side,The width is 30" total or the width of the equipment, not 30" on either side and a minimum headroom clearance of 6 feet, or the height of the equipment, whichever is greater. If obstacles would make it unsafe for you to inspect the service panel, you have the right to disclaim it.
  • sharp-tipped panel box screws. Panel box cover screws must have blunt ends so they do not pierce the wires inside the box. Also, look for wires that pass too closely to the screw openings inside the electrical panel.
  • circuit breakers that are not properly sized. Circuit breakers should not be too large or too small for the wires they serve. Breakers can be smaller than required, ie #12 protected by a 15 amp. Breakers for air conditioners are sized under different rules and will appear to be oversized for the wire size. Check the AC nameplate for the proper minimum circuit ampacity and maximum overcurrent protection size.
Reply With Quote
  #5  
Old 1/7/10, 9:23 AM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,749
Default Re: Electrical Service Panels. Please proof this new inspection article.

1. Why is Zinsco called out but not Federal Pacific?
2. "Circuit breakers should not be too large or too small for the wires they serve" - should be made clear this refers to the electrical characteristics, not the physical.
3. "While removing the panel, inspectors should" - should say 'panel cover' or 'deadfront'.



Excellence in Inspections
Mike Boyett, TREC #7290
mikeb@capcityinspections.com
Capital City Inspections
Austin, Texas
(512) 577-2579

Company blog is: www.capcityinspections.com/blog

Last edited by mboyett; 1/7/10 at 9:27 AM..
Reply With Quote
  #6  
Old 1/7/10, 9:38 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical Service Panels. Please proof this new inspection article.

I don't see anything about even basic protective equipment like safety glasses.
Reply With Quote
  #7  
Old 1/7/10, 9:50 AM
Philippe G. Heller's Avatar
Philippe G. Heller Philippe G. Heller is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: San Diego, CA
Posts: 171
Default Re: Electrical Service Panels. Please proof this new inspection article.

We call out both Zinsco and Federal Pacific panels. But you have to be careful. Neither of these panels was recalled. They are just the subject of debate, with evidence that they are unsafe.

If you say it was recalled and "must" be replaced, you could end up paying for it. Just say that they have a reeputation of being problematic. Recommend further eval.



Philippe Heller
The San Diego Real Estate Inspection Co.
http://www.sdinspections.com
www.facebook.com/sdinspections
Reply With Quote
  #8  
Old 1/7/10, 9:57 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Electrical Service Panels. Please proof this new inspection article.

Quote:
Originally Posted by Jim Port View Post
Inspectors can check for the following defective conditions during an electrical panel inspection:
  • insufficient clearance. According to the 2008 National Electrical Code, most residential electrical panels require at least a 3-foot clearance or working space in front, 30 inches on either side,The width is 30" total or the width of the equipment, not 30" on either side and a minimum headroom clearance of 6 feet, or the height of the equipment, whichever is greater. If obstacles would make it unsafe for you to inspect the service panel, you have the right to disclaim it.
  • sharp-tipped panel box screws. Panel box cover screws must have blunt ends so they do not pierce the wires inside the box. Also, look for wires that pass too closely to the screw openings inside the electrical panel.
  • circuit breakers that are not properly sized. Circuit breakers should not be too large or too small for the wires they serve. Breakers can be smaller than required, ie #12 protected by a 15 amp. Breakers for air conditioners are sized under different rules and will appear to be oversized for the wire size. Check the AC nameplate for the proper minimum circuit ampacity and maximum overcurrent protection size.
Remember also that at one point in time the clearance was less than 36" in front of electrical panels. At one point it was 24 inches back I believe in the 1940's and 50's..



Paul W. Abernathy
Reply With Quote
  #9  
Old 1/7/10, 9:59 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Electrical Service Panels. Please proof this new inspection article.

Quote:
Originally Posted by rlondon View Post
How can inspectors check for that?

Thanks Paul
You can hear it from the arching....makes a popping sound and crackling sound due to the gap an arch jumping across the poor contact points. You can also see this with an infrared temp. gun as well like i explained in the video I did for NACHI.



Paul W. Abernathy
Reply With Quote
  #10  
Old 1/8/10, 10:49 AM
Rob London Rob London is offline
InterNACHI Member
 
Join Date: May 2009
Posts: 237
Default Re: Electrical Service Panels. Please proof this new inspection article.

thanks guys



Researcher and Technical Writer, InterNACHI
Reply With Quote
  #11  
Old 1/17/10, 12:28 AM
tneyedli1's Avatar
tneyedli1 tneyedli1 is offline
Active Poster
 
Join Date: Mar 2006
Location: Port Alberni, BC
Posts: 279
Please Note: tneyedli1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical Service Panels. Please proof this new inspection article.

Quote:
Originally Posted by gromicko View Post
Service Panel Inspection:
look for any nicked wires near the screw as this may reduce the ampacity and
look for any aluminum branch wiring etc.

should be added.

T.N
Reply With Quote
  #12  
Old 1/17/10, 2:51 AM
Matthew K. Klein's Avatar
Matthew K. Klein Matthew K. Klein is offline
InterNACHI Member
 
Join Date: Dec 2009
Posts: 91
Default Re: Electrical Service Panels. Please proof this new inspection article.

Nick, what about the presence of rodents or their damage. I have not seen that in any articles; but I have not seen it in a panel yet either. As far as damage, I have seen in one of my past homes where a rodent has chewed he insulation off of a wire down to the wire. Whatever it was that did the damage seemed to have a preference for the insulation, and amazingly was able to chew off quite a bit of it without getting electrocuted. At least, I did not see a dead animal around the damage.
Reply With Quote
  #13  
Old 1/17/10, 1:43 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Electrical Service Panels. Please proof this new inspection article.

lol...if you are not going to add our comments then why give them....lol



Paul W. Abernathy
Reply With Quote
Need a home inspection in Hawaii? Check out InterNACHI's listing of Hawaii certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 1/18/10, 10:02 AM
Rob London Rob London is offline
InterNACHI Member
 
Join Date: May 2009
Posts: 237
Default Re: Electrical Service Panels. Please proof this new inspection article.

Made those additions.

Sometimes I lose track of an old "pleas proof" thread if no one has added to it in awhile and I'm more concerned with the newer ones. But you're right, I'll try not to let that happen.



Researcher and Technical Writer, InterNACHI
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Some good questions that always need answers jtedesco1 Electrical Inspections 5 6/16/06 9:10 PM
Old electrical panels? ysoltis Electrical Inspections 3 1/14/06 11:00 AM
Old electrical panels? ysoltis General Inspection Discussion 2 1/14/06 10:58 AM
Old electrical panels? ysoltis Electrical Inspections 0 1/13/06 11:38 AM


All times are GMT -4. The time now is 9:03 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts