Default Electrical sub panel

Have this electrical sub panel for an electric water heater. Is this grounded correctly? There ground has been screwed to the panel and it looks like to the neutral buss bar. See picture.
Attached Thumbnails
electrical-sub-panel-picture-032.jpg  
Reply With Quote
Find an InterNACHI certified Alaska Home Inspector (and anywhere else in North America)
  #2  
Old 12/10/09, 5:09 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,207
Default Re: Electrical sub panel

No neutral is connected so it does not matter at this point. Where is the ground from the feeder circuit? Is it connected with metal conduit back to the main panel?



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #3  
Old 12/10/09, 6:26 PM
Ron Chorey II's Avatar
Ron Chorey II Ron Chorey II is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Las Cruces, NM eating chili!!
Posts: 638
Default Re: Electrical sub panel

I do not know. There is the main panel and next to it the sub panel. Two meters on for the main and one for the sub panel. 2 meters has something to do with the electric company and giving a break with the electric water heater. The ground comes in from the back of the sub panel, through the wall. I am thinking about recommending an electrician verify that it is wired correctly.
Reply With Quote
  #4  
Old 12/11/09, 2:32 PM
Craig Vecchione Craig Vecchione is offline
New User
 
Join Date: Dec 2009
Posts: 1
Please Note: Craig Vecchione is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical sub panel

The installation doesn't meet Code even as viewed because the equipment gounding conductor is run around a wood screw and then continues to the ground bus. The wood screw is not an approved method for making ground to the enclosure, assuming the enclosure is grounded via EMT from the meter. It's at best a weak and ineffective connection.

The equipment ground conductor from the water heater should be freed from that screw and remain connected at the ground bus.

The grounding electrode conductor you described as "comes in from the back of the sub panel, through the wall" should be connected directly to the ground bus. I don't see that conductor, so you should provide some more info; what's it connected to at each end?

The bus should then be bonded to the enclosure with an approved bonding bolt.
Reply With Quote
  #5  
Old 12/13/09, 3:04 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Electrical sub panel

Firsty, It appears that no EGC was run to this disconnect. Now, if for a second we assumed it was connected with EMT then we could say thats fine and while the EGC from the circuit is wrapping around non-compliant 250.8 screw termination and then onto a buss bar that is isolated anyway...so if you did remove it from the screw it would then have ZERO chance of doing anything without a proper bonding jumper.

I would venture to say that it is not EMT feeding it and no EGC was run so call it out as it is and let the licensed electrical contractor deal with it.



Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Download the videos here all about physics and electricity jtedesco1 Electrical Inspections 5 9/14/08 3:58 PM
Electrical Safety Foundation International Links jtedesco1 Electrical Inspections 5 12/8/07 3:10 PM
It's not necassary to remove Electrical Panel Cover. dvalley Electrical Inspections 15 7/3/07 3:22 PM
Electrical Safety Information jtedesco1 Electrical Inspections 0 2/19/06 1:48 AM


All times are GMT -4. The time now is 9:03 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts