Default Electrical tape balls?

Has anyone seen this? There are two awg10 wires coming from the 20amp double breaker to these tape balls where two, what seem to be larger gauge wires, no number written on sheathing, are spliced I guess. The circuit is labeled as oven(which is all electric). This is brand new construction. Anyone know if it's ok to have awg 10 with a 20amp(double terminal but not two 20amp breakers bonded)? What about the splice? and the use of en=ven larger gauge from there? Any help with this is appreciated.
Thanks,
Reese
Attached Thumbnails
electrical-tape-balls-panel2.jpg   electrical-tape-balls-balls2.jpg   electrical-tape-balls-breaker2.jpg  
Reply With Quote
  #2  
Old 8/23/07, 1:35 AM
Rick Maday Rick Maday is offline
New User
 
Join Date: May 2007
Location: Illinois
Posts: 48
Please Note: Rick Maday is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical tape balls?

Is the 20 amp breaker an AFCI? Hard to tell from the picture.

I haven't read the NEC but I'm pretty sure there is no section about splices being in base-ball sized balls of tape in lieu of a junction box. If they're in the panel though - who knows?
Seems like a licensed electrician can make that call.
</IMG>
Reply With Quote
  #3  
Old 8/23/07, 1:42 AM
rmc3inspection's Avatar
rmc3inspection rmc3inspection is offline
New User
 
Join Date: Jul 2006
Location: North Carolina
Posts: 24
Please Note: rmc3inspection is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical tape balls?

This isn't an arc fault circuit breaker.
Reply With Quote
  #4  
Old 8/23/07, 2:24 AM
Rick Maday Rick Maday is offline
New User
 
Join Date: May 2007
Location: Illinois
Posts: 48
Please Note: Rick Maday is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical tape balls?

I asked about AFCI because the second breaker from the bottom seems to have a test button.

I was just havin' a laugh about the tape balls - further evaluation and repair by a licensed electrician is in order.
Reply With Quote
  #5  
Old 8/23/07, 2:39 AM
rmc3inspection's Avatar
rmc3inspection rmc3inspection is offline
New User
 
Join Date: Jul 2006
Location: North Carolina
Posts: 24
Please Note: rmc3inspection is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical tape balls?

From what I can gather from SquareD webpage is that this is a two pole 20 amp breaker (QO220VH). Their specs say for copper wire #14-10 is allowed. So the pigtail being #10 is fine. But the conductor running from the splice to the outlet appears to be a larger gauge(no exposed wire, just size with sheathing is larger). So not rated for this circuit breaker. I'll defer it to an electrician of course, but wanted to learn something and be able to better explain to my client if asked.
Reply With Quote
  #6  
Old 8/23/07, 9:08 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Electrical tape balls?

Ok....

IF the breaker is a 20A 2-pole and the conductor going into it is 10 AWG then that is fine as the breaker will limit the conductor to 20A and it is rated for 30A....NOW...I can only speculate that the tape balls are split bolts possibly changing over the 10 AWG to the larger conductor which may have been done for voltage drop reasons...who knows but I will say this....if it is labeled OVEN then it makes me wonder if it is labeled properly.

Remember you can always put larger conductors on a smaller breaker as long as it is allowed by the size allowances of the breaker....all will give a range that can be connected to the breaker....if the amount of current is excessive even with the larger conductors it will still trip the OCPD in the event of a sustained overcurrent situation.

So.....unless you dig more which is probably outside the scope of your inspection...a 10 AWG can indeed be on a 20A breaker....and splicing like this is allowed within the enclosure as long as it meets the cross section allowances and it does.....The only problem I might investigate is the oven and it's draw.....because if this is new construction and we are talking about a 40A minimum oven......then you will have a breaker trip issue down the road the consumer might want to know about....

If we are talking about a simple single oven unit ( no cooktop ) then quite possibly the 20A 240V breaker is fine and they just oversized the conductors which is fine as well as long as the breaker is sized properly.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #7  
Old 8/23/07, 11:02 AM
rmc3inspection's Avatar
rmc3inspection rmc3inspection is offline
New User
 
Join Date: Jul 2006
Location: North Carolina
Posts: 24
Please Note: rmc3inspection is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical tape balls?

ok. Here is what I do know.
The oven is rated at 20amps. So it sounds like that is fine with the size breaker and awg 10 and the over size conductor running to it.
IF the larger conductor is aliuminum(which I don't know)
and the awg 10 is copper(I do know), are there specific connectors needed to bond these two different material conductors at the splice?
Do you suppose they made this pigtail of the awg 10 to fit it under the terminals at the circuit breaker or for voltage drop? (I know this is speculative)

Thanks,
Reese
Reply With Quote
  #8  
Old 8/23/07, 11:16 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Electrical tape balls?

read my post....



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #9  
Old 8/23/07, 11:20 AM
rmc3inspection's Avatar
rmc3inspection rmc3inspection is offline
New User
 
Join Date: Jul 2006
Location: North Carolina
Posts: 24
Please Note: rmc3inspection is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical tape balls?

Paul,
I just re-read what you wrote and would like to know if the circuit breaker is rated for use with size #14-10 conductor and the larger conductor running from the splice with the #10 to the oven is #8, then this is not in compliance with the size requirements of the breaker of #14-10? right?
If the #8 conductor is larger than rated for the breaker, what are the implications and possible safety issues?

Thanks,
Reese
Reply With Quote
  #10  
Old 8/23/07, 11:24 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Electrical tape balls?

The size requirement pertains to termination. The terminal is sized to fix a specific CM of the conductor being used. It is routine for larger conductors to be spliced onto smaller conductors in regards to voltage drop as long as the other considerations are taking into effect like increaseing the size of the EGC as well...which is probably taken care of with the use of the larger wire itself in a cable wiring method.

The larger wire simply has more capacity ( ie: less impedance ) but the OCPD ( ie: breaker ) wont care as it will trip if the continuous load exceeds the rating of the breaker ( ie: overcurrent ) ...so the breaker should protect the conductor regardless as that is is purpose really....Hope this helps....



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #11  
Old 8/23/07, 11:27 AM
rmc3inspection's Avatar
rmc3inspection rmc3inspection is offline
New User
 
Join Date: Jul 2006
Location: North Carolina
Posts: 24
Please Note: rmc3inspection is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical tape balls?

Thanks for the help. Any specific connectors for different material conductor splices(copper to aluminum)?
Reply With Quote
  #12  
Old 8/23/07, 11:29 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Electrical tape balls?

Ahh......well hard to tell unless you untape the balls ( not sure I like how I said that ...lol..) but some split bolts are AL/CU and some are not....We happen to use tap blocks that are insulated on their own for this and no need to wrap them in tape...maybe they are hiding something..who knows but unless you can prove it I would not worry much about that part.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #13  
Old 8/23/07, 11:37 AM
rmc3inspection's Avatar
rmc3inspection rmc3inspection is offline
New User
 
Join Date: Jul 2006
Location: North Carolina
Posts: 24
Please Note: rmc3inspection is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical tape balls?

Thanks again. I still referred it to an electrician for further investigation in the report beacause of the balls. It almost felt like they were rubber balls taped over with electrical tape. They were very symetrical.
anyway, thanks again for sharing your knowledge.

Reese
Reply With Quote
  #14  
Old 8/23/07, 11:45 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Electrical tape balls?

no problem.....you can NEVER go wrong by defering...better to be safe than sorry.

On a side not...those are some mighty ROUND balls.........would take a freakin entire roll of tape to make those with a split bolt.....

I would not be able to resist the temtation to CUT ONE OPEN to see whats inside....maybe they used a ping pong ball, yeah ping pong balls are not UL Listed..lol



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #15  
Old 8/23/07, 12:56 PM
mthomas2 mthomas2 is offline
Active Poster
 
Join Date: Oct 2005
Location: Evanston, IL
Posts: 703
Please Note: mthomas2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical tape balls?

Depending on the size of the larger wires, this could be correct (if spliced properly):

"Breakers usually accommodate one or two wire size larger than the size normally associated with the breaker. If too large a wire is used, sometimes a few stands of the conductor will be turned back instead of going into the breaker. Wires cannot be used in this manner. If an over-sized connector is for some reason actually necessary, and it is beyond the range of wire accepted by the breaker, it should be spliced inside the panel rather than cutting its strands at the breaker."

- Electrical Inspection of Existing Dwellings by Hansen, Kardon & Casey 3rd edition,
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 4:56 PM
Download the videos here all about physics and electricity jtedesco1 Electrical Inspections 5 9/14/08 4:58 PM
Handbook for Electrical Safety pabernathy Electrical Inspections 1 1/1/07 2:14 PM
electrical tape in panel dnice Electrical Inspections 5 3/17/06 11:41 AM
Electrical Safety Information jtedesco1 Electrical Inspections 0 2/19/06 2:48 AM


All times are GMT -4. The time now is 11:19 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts