Default Electrician made repairs

At a listing inspection I noted at "sub" panel that grounds/neutrals need to be separated at bus bar, with neutrals isolated from panel.

First photo is before, 2nd is after repairs.
Attached Thumbnails
electrician-made-repairs-copy-hpim1348.jpg   electrician-made-repairs-hpim2442.jpg  



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!

Last edited by ccurrins; 8/6/11 at 4:27 PM..
Reply With Quote
Need a home inspection in Illinois? Check out InterNACHI's listing of Illinois certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 8/6/11, 1:48 PM
Russell J. Hensel's Avatar
Russell J. Hensel Russell J. Hensel is offline
InterNACHI Member
 
Join Date: Jul 2008
Location: Fort Myers, FL
Posts: 5,576
Default Re: Electrician maid repairs

LMAO........thats some funny stuff!



Comprehensive Building Consultants
Naples Home Inspection, Naples Mold Inspection, Naples Radon Inspection, Bonita Springs Home Inspection, Bonita Springs Mold Inspection, Bonita Springs Radon Inspection.



Donate here:

or send checks to the
Fl Home and Insurance Inspector Chapter
1103 W Hibiscus Blvd Ste 311
Melbourne, Fl 32901
Reply With Quote
  #3  
Old 8/6/11, 1:51 PM
James F. McKee's Avatar
James F. McKee James F. McKee is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Amherst, Oh
Posts: 5,568
Default Re: Electrician maid repairs

Your fault Chris...you're the one that said they had to be seperated....



Classic Home inspections

Jim Mckee
Amherst, Ohio

www.amhersthomeinspector.com
Reply With Quote
  #4  
Old 8/6/11, 1:57 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrician maid repairs

Wow, the repair looks more unsafe then the original installation.
Reply With Quote
  #5  
Old 8/6/11, 2:28 PM
Steven C. Waskewicz's Avatar
Steven C. Waskewicz Steven C. Waskewicz is offline
InterNACHI Member
 
Join Date: Apr 2006
Location: Colorado Springs, CO
Posts: 1,948
Default Re: Electrician maid repairs

Title had me fooled....I thought the Electrician repaired the maid...




Steven Waskewicz

Professional Building Analyst, BPI
Colorado Springs, Colorado
719-510-7703
Rest Assured Inspection Services, LLC.
719-510-7703 mobile all the time





Reply With Quote
  #6  
Old 8/6/11, 4:29 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Electrician maid repairs

Quote:
Originally Posted by swaskewicz View Post
Title had me fooled....I thought the Electrician repaired the maid...
...



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #7  
Old 8/6/11, 4:31 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Electrician maid repairs

Quote:
Originally Posted by Robert Meier View Post
Wow, the repair looks more unsafe then the original installation.
What would be the easiest way to salvage this mess?



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #8  
Old 8/6/11, 5:45 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrician maid repairs

Quote:
Originally Posted by ccurrins View Post
What would be the easiest way to salvage this mess?

The EGC's can be spliced and pigtailed to the bus as long as the tail is the same size or larger than the largest conductor in the splice. Also the wirenut would need to be listed for the number of condcutors spliced together. So maybe you would need to combine all of the EGC's into two or three groups. Otherwise a simple ground bus bolted to the enclosure could be installed for all of the EGC's only. The neutrals need to be installed in a separate hole for each conductor in the neutral bus.

Reply With Quote
  #9  
Old 8/6/11, 6:25 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,107
Default Re: Electrician made repairs

This is a case of redo and start all over again.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #10  
Old 8/6/11, 8:08 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Electrician maid repairs

Quote:
Originally Posted by Robert Meier View Post
The EGC's can be spliced and pigtailed to the bus as long as the tail is the same size or larger than the largest conductor in the splice. Also the wirenut would need to be listed for the number of condcutors spliced together. So maybe you would need to combine all of the EGC's into two or three groups. Otherwise a simple ground bus bolted to the enclosure could be installed for all of the EGC's only. The neutrals need to be installed in a separate hole for each conductor in the neutral bus.
So basically the easiest way is what should have been done the first time, which is install a ground bus bonded to panel for EGC's. Like Kevin said start over.

Can't believe someone went to all the trouble they did removing the EGC's from the bus, twisting them, and then reconnecting them to the same bus with an individual wire.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #11  
Old 8/6/11, 8:22 PM
Kenneth R. Brittain Kenneth R. Brittain is offline
InterNACHI Member
 
Join Date: Jul 2011
Location: Charlotte NC
Posts: 224
Default Re: Electrician made repairs

Wow! so what's with all the extra wire nut splices? I think who ever did this made it worse. Guess all you can do is report that is not done correctly, recommend rework/repair again, and hint that they should report this guy to the electrical board. I bet he was not a licensed electrican but a helper who works for a licensed electrican.
Reply With Quote
  #12  
Old 8/6/11, 9:36 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Electrician made repairs

Quote:
Originally Posted by kbrittain View Post
Wow! so what's with all the extra wire nut splices? I think who ever did this made it worse. Guess all you can do is report that is not done correctly, recommend rework/repair again, and hint that they should report this guy to the electrical board. I bet he was not a licensed electrican but a helper who works for a licensed electrican.
Wire nuts in 2nd photo is the result of removing triple taps at breakers in 1st photo.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #13  
Old 8/6/11, 11:25 PM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 8,261
Default Re: Electrician made repairs

Quote:
Originally Posted by ccurrins View Post
At a listing inspection I noted at "sub" panel that grounds/neutrals need to be separated at bus bar, with neutrals isolated from panel.

First photo is before, 2nd is after repairs.
Dammit Chris...I had Iced Tea squirting out my nostrils-------

I need to save that picture....once in a lifetime-----------
Reply With Quote
Need a home inspection in Illinois? Check out InterNACHI's listing of Illinois certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 8/7/11, 12:39 AM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Electrician made repairs

Hmmmm .... maybe installing a new ground/neutral bar would have been helpful ... ... and it looks like there are still double lug neutrals ...



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...

Last edited by roconnor; 8/7/11 at 12:44 AM..
Reply With Quote
  #15  
Old 8/7/11, 3:43 PM
David Hays David Hays is offline
InterNACHI Member
 
Join Date: Feb 2010
Location: Denver, CO
Posts: 353
Default Re: Electrician maid repairs

Quote:
Originally Posted by rhensel View Post
LMAO........thats some funny stuff!
My thoughts also!



David Hays
All Points Home Inspections LLC
Denver, CO
720-670-0366
allpointshomeinspect@yahoo.com
www.allpointshomeinspections.org
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Home Inspector law suit rcooke Canadian Inspectors 0 2/18/10 11:48 AM
Repairs made by a LICENCED electrician cduphily Electrical Inspections 45 1/13/08 3:09 PM