Default Electrician signs off 'ganged neutrals'...now what?

Town home (end unit of 5 units in a building) - 3 wire copper service to a SqD 125 amp box...
I wrote up the ganged neutrals and inoperative GFCI's in the bathrooms.

Client just sent me a fax of the 'letter' the electrician provided him saying what he fixed and didn't...

Looking for advice on how to continue (if I should)

I told the client earlier that if an electrician 'signs off' on it, that's all I called it out for...
but is it really? is it wrong and does it need to be corrected?
There a tripled Grounds already in the panel. Adequate room exists to triple the existing grounds and that would provide room to separate all the Neutrals...
Should he insist on it? if not why?


Sorry so many questions, I just get tired of dealing with this every other day; and yes this is the one I called you about Jeff P.


Sign off
Attached Thumbnails
electrician-signs-off-ganged-neutrals-now-20apr07-072.jpg   electrician-signs-off-ganged-neutrals-now-20apr07-071.jpg  



- Mike

Michael W. Gault, SC RBI 1728
A to Z Home Inspections
Charleston, Dorchester & Berkeley Counties in S.C.
NACHI05040682
www.atozinspector.com

(843) 442-9755
Charleston Home Inspector
Reply With Quote
  #2  
Old 5/30/07, 6:09 PM
rdawes's Avatar
rdawes rdawes is offline
Active Poster
 
Join Date: Nov 2004
Location: Plano, TX
Posts: 427
Please Note: rdawes is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrician signs off 'ganged neutrals'...now what?

By today's national standards, it is incorrect as you well know. It may have been OK by the standards in place when the structure was built in the jurisdiction that it was built in. Will it burn the house down? Not likely. Let it go. You have shifted the responsibility to the electrician who says it's OK. That's all you can do.
Reply With Quote
  #3  
Old 5/30/07, 7:01 PM
Michael W. Gault's Avatar
Michael W. Gault Michael W. Gault is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Mount Pleasant, SC
Posts: 1,091
Default Re: Electrician signs off 'ganged neutrals'...now what?

Thanks Ron...

I need to play with my Grand Daughter more...

She makes me smile....
Attached Thumbnails
electrician-signs-off-ganged-neutrals-now-pict0228-small.jpg  



- Mike

Michael W. Gault, SC RBI 1728
A to Z Home Inspections
Charleston, Dorchester & Berkeley Counties in S.C.
NACHI05040682
www.atozinspector.com

(843) 442-9755
Charleston Home Inspector
Reply With Quote
  #4  
Old 5/31/07, 10:18 AM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Electrician signs off 'ganged neutrals'...now what?

IMHO:

I wish residential 'ground bars' came 3 feet long, and made of 1" steel, so I can smack 'other' electricians up side their heads. The double neutrals I run into often, and when I mention this to 'other' electricians, they say there aren't enough terminal screws on the neutral bars. I say install a ground bar fool, and I get, "that's $3 out of my pocket!"

Good call Mike. I suggest the client takes the photos, your report, the electricians letter, and a brief summery about terminals with neutrals(Paul might post one from Holt), go see a lawyer for advice. This can be clearly settled in small claims court, and I would max out the 'amount' to ensure punitive damages. Since this electrician needs to be taught a lesson, and his current practices exposes clients to 'danger'.

Tom <not a lawyer, and not a brother to stupid electricians>
Reply With Quote
  #5  
Old 5/31/07, 10:33 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Electrician signs off 'ganged neutrals'...now what?




Paul W. Abernathy
Reply With Quote
  #6  
Old 5/31/07, 10:37 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Electrician signs off 'ganged neutrals'...now what?

I write up double lugged nuetrals on 90% of the homes I inspect.

408.21 specially states "Each grounded conductor [neutral] shall terminate within the panelboard in an individual terminal that is not also used for another conductor".
Reply With Quote
  #7  
Old 5/31/07, 10:59 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Electrician signs off 'ganged neutrals'...now what?

Yep...and if they say.....But David...this house was built in the 80's...not required to meet todays standards of the NEC...you say...

Dear Sir.....( thinking to yourself...Dear Pinhead ) the NEC ( a minimum safety stanard ) stated back many years ago under 110.3(B) that it should be installed according to the manufactures specs....via Standard 67 of the UL.

And if they say...But David this house was built in 1940....no standards for UL were set at that time......Your answer would be.....BUT did the panel in question say you could double tap the "grounded" conductor specifically...and then explain WHY it can be a bad thing if it comes loose due to someone messing with it ( ie: shared neutral ) or if two different conductors are sharing the same termination point...and the problems associated with that as well.....THEN........if they choose to do anything about it...well...atleast you made your voice be heard...



Paul W. Abernathy
Reply With Quote
  #8  
Old 5/31/07, 3:16 PM
John Allingham John Allingham is offline
InterNACHI Member
 
Join Date: Jun 2004
Location: Milton, ON
Posts: 574
Default Re: Electrician signs off 'ganged neutrals'...now what?

Shows what can happen.
Attached Thumbnails
electrician-signs-off-ganged-neutrals-now-neutrals1.jpg  
Reply With Quote
  #9  
Old 6/1/07, 9:32 AM
mthomas2 mthomas2 is offline
Active Poster
 
Join Date: Oct 2005
Location: Evanston, IL
Posts: 703
Please Note: mthomas2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrician signs off 'ganged neutrals'...now what?

John,

Can I have permission to use that photo when this question comes up?
Reply With Quote
  #10  
Old 6/1/07, 10:08 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Electrician signs off 'ganged neutrals'...now what?

Quote:
Originally Posted by jallingham
Shows what can happen.
Wonderful Example.......Most Excellent !



Paul W. Abernathy
Reply With Quote
  #11  
Old 6/1/07, 12:42 PM
John Allingham John Allingham is offline
InterNACHI Member
 
Join Date: Jun 2004
Location: Milton, ON
Posts: 574
Default Re: Electrician signs off 'ganged neutrals'...now what?

Quote:
Originally Posted by mthomas2
John,

Can I have permission to use that photo when this question comes up?
No problem. If you send me your E-mail address I can send you a higher resolution copy. Mine is inspect@peelhomeinspection.com.
Reply With Quote
  #12  
Old 6/1/07, 12:52 PM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Electrician signs off 'ganged neutrals'...now what?

John,

Is the 'offer' open to us all? I would love the free use of the higher resolution example too.

Thank you,

Tom
Reply With Quote
  #13  
Old 6/1/07, 10:58 PM
John Allingham John Allingham is offline
InterNACHI Member
 
Join Date: Jun 2004
Location: Milton, ON
Posts: 574
Default Re: Electrician signs off 'ganged neutrals'...now what?

Quote:
Originally Posted by tdietrich1
John,

Is the 'offer' open to us all? I would love the free use of the higher resolution example too.

Thank you,

Tom
Sure Tom, and anyone else.
Reply With Quote
  #14  
Old 6/1/07, 11:37 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,908
Default Re: Electrician signs off 'ganged neutrals'...now what?

Just out of curiosity was that caused due to one of the neutrals becoming detached thus creating an arc fault.
Reply With Quote
  #15  
Old 6/1/07, 11:48 PM
Christian F. Mettel Christian F. Mettel is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Aurora, On
Posts: 486
Default Re: Electrician signs off 'ganged neutrals'...now what?

Quote:
Originally Posted by jallingham
Sure Tom, and anyone else.
Nice picture John!

Chris
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Affordable CoroPlast Signs - MoveInCertified, etc rspriggs Miscellaneous Discussion for Inspectors 30 9/25/07 8:28 AM
MoveInCertified Signs inxil Miscellaneous Discussion for Inspectors 0 9/20/07 3:28 PM
HOT PIC: MoveInCertified.com signs popping up along side REALTOR signs. gromicko Miscellaneous Discussion for Inspectors 1 9/19/07 10:05 PM
Electrician or handyman repair? srowe Electrical Inspections 8 1/4/07 9:21 AM


All times are GMT -4. The time now is 3:30 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts