  #31  
Old 1/5/06, 12:07 AM
jrivera's Avatar
jrivera jrivera is offline
Active Poster
 
Join Date: Jun 2004
Location: Shirley, NY
Posts: 1,340
Please Note: jrivera is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electricians Check List

Thanks, nice job

Mic
Reply With Quote
  #32  
Old 1/5/06, 12:34 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Smile Re: Electricians Check List

Quote:
Originally Posted by pabernathy
Good points Doug and I think Joe has posted one so if everyone feels that is fine for a check list then I will stop working on the one I have been working on. If not..let me know and I will keep working on it and adding things.
Paul: I was looking forward to the list you are developing. Please go for it! I did add similar items in the old forum and they may still be in the archives or were deleted. My post for NFPA 73 was to call attention to something that could be used.
Reply With Quote
  #33  
Old 1/5/06, 12:37 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Electricians Check List

Ok Joe......I thought someone said they used that for HI inspections...I believe I got confused...lol....

I will keep working on it...I did not want to work on something that maybe was not needed due to another post.

It is slow going..I have been home most of the week catching up on TONS of bids I have sitting on the table....just never enough time in the day. I pop on here for a STRESS break as pricing is my LEAST favorite thing about ELE contracting....the collection part is NICE however.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #34  
Old 1/5/06, 1:42 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Talking Re: Electricians Check List

Do your friends call you Paulie? I wondered if you knew the electrical inspector who is mentioned in the message at this link?

http://www.nachi.org/forum/showthread.php?p=2400#post2400 =D>
Reply With Quote
  #35  
Old 1/5/06, 1:45 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Electricians Check List

lol...no I do not believe I have ever been called Paulie...lol..My wife would not even call me that. I prefer her to call me Mr. Abernathy...thehehe

I think you asked that before...I have no idea who it is as I am in Virginia only.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #36  
Old 1/5/06, 6:43 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electricians Check List

Mr. Abernathy:

You didn't catch on yet? The question from the poster here, http://www.nachi.org/forum/showthrea...=2400#post2400 and my reply were the bait! Both you and Bob are implied in my comments about the AHJ and electricians "Bobby Paul" and "Paulie Bob" when it comes to the access to the disconnect.
Reply With Quote
  #37  
Old 1/5/06, 12:15 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Electricians Check List

ahhh..ok.....guess I missed that one.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #38  
Old 1/6/06, 2:34 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electricians Check List

I see you are pretty generous with wire sizes on the motor loads, exceeding 430
Reply With Quote
  #39  
Old 1/6/06, 3:12 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Electricians Check List

lol....Greg I didn't write it...thehehe...I just update it...lol

Oh...Generous is always good...lol...rather than stingy...tehhehehe



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #40  
Old 1/6/06, 3:17 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Electricians Check List

Actually greg I think the formula is to taking in the account of VD% as well and giving actual distances to take the table work out of it.

I think you will see that if you take 100' on a 1/2HP motor at 120V nominal...it is 9.8 Amps per 430.148

Now keeping the voltage drop below 3%....in this factor.....using 10/2UF would stay below 3% while going to 12/2UF would exceed it...

I believe this is the basis for the chart...it has already taken into account for the VD%, and breaker sizing....so if the distance was only half the distance...say 50' it would be less and 12/2UF would probably work...but I think the chart is trying to be general....as all the possible varibles would have a chart way to easy to work with.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year

Last edited by pabernathy; 1/6/06 at 3:23 PM..
Reply With Quote
  #41  
Old 1/10/06, 1:48 AM
jkormos's Avatar
jkormos jkormos is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Medinah, IL
Posts: 641
Default Re: Electricians Check List

Paul, thanks again for the great post

Joe
Reply With Quote
  #42  
Old 1/13/06, 9:05 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Electricians Check List

Bump



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #43  
Old 1/14/06, 10:33 AM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,103
Default Re: Electricians Check List

Don't forget westinghouse and sylvania panels can be actually Zinsco!

Ran into a westinghouse panel the other day that was sizzling inside where the main breaker bar screwed onto the left busbar. Total load at this time was probably less than 5 amps.

I called the owner and asked if he wanted me to turn off the power. I told him to get someone out there right away and gave him some phone numbers.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #44  
Old 1/14/06, 11:13 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Electricians Check List

To be honest with you I have seen some Sq D and Cut. Hammer breakers do some smokin also in my time. Moral of the story is all panels and breakers have a life span......they dont last forever so keep us electricians busy...lol



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #45  
Old 1/15/06, 5:43 PM
Frank J. Buttermore Frank J. Buttermore is offline
InterNACHI Member
 
Join Date: May 2005
Location: Howell, MI
Posts: 16
Default Re: Electricians Check List

Paul, Thanks again for sharing your knowledge and resources.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Electrical Check List - Probably posted before pabernathy Electrical Inspections 16 5/27/07 12:54 AM
Anyone created a Home Inspectors Electrical Check List jsieg Electrical Inspections 29 2/7/06 2:55 PM
Heat Pump Check list for inspecting dmacy Inspecting HVAC Systems 21 2/1/06 1:56 PM