Paul;

Comments, criticism and great thought on this? Please?


Electrical Home Inspection Checklist






Item


Inspection Point


Comments



Service Drop - Overhead




From Pole or Aerial Drop




Condition of Drop Cable




Obstruction by trees, buildings, etc




Clearances







Service Drop - Lateral




Service Pole Identifiable?




Enclosure of lateral run at pole




Exterior transformer on property, condition







Service Entrance




Service splice




Drip loop




Weatherhead




Service entrance conductor gauge




Service Entrance Conduit (support, secured, condition, sealed)




Service meter rating




Service meter condition




Grounding at service meter?




Main Connect at meter (rating)




Service exterior wall penetration sealed







Service Equipment




Exterior Condition (rust, physical damage, properly secured)




Missing punch-outs




Verify proper grounding (exterior)




Electrified




Proper mounting (secure, on fireproof backing)




Face (directory, manufacturer, rating, age)




Face screws (proper number, blunt point)




Verify gauge of service entrance conductors to exterior




Neutral properly color coded or taped as neutral




Service entrance conductors properly bonded, corrosion




If SEC are aluminum, is anti-oxide paste in place, corrosion




Main Disconnect (rating, 'six throws' rule)




Raceways secured, bonded




Ground conductor bonded to service equipment and with neutral (main)



Ground conductor bonded to service equipment and with neutral (sub-panel)



Branch wire type, gauge, suitability to overcurrent devices




Overcurrent devices of proper type for the panel




Double taps on overcurrent devices




Ground and neutral bus double taps




Number of neutrals to hot conductors




Type of overcurrent devices, GFCI, AFCI




Connection corrosion




Insulator condition




Excessive pigtails




Wiring orderly, sufficient space in panel







Raceways




Proper number of networks per raceway




Type (K&T, ROMEX, BX, EMT, Pipe)







Knob and tube




Wire age, insullation type, condition




Splices




Connections to newer wiring, junction box




Condition of knobs and tubes, cracks, missing







ROMEX




Properly secured at boxes, panels




Excessive covering in panel, boxes




Properly secured on runs, proper staples, crushed wire




Ground wire bonded







BX




Properly secured and bonded at boxes, panels




Bushings in place




Ground wire bonded




If, in conjunction with EMT, is BX only used in whips, 6' or less




Properly secured on runs




No unprotected wall penetrations







EMT




Properly secured, bonded at boxes and panels




Properly bonded on run




Proper connectors for use (interior, exterior)




Properly secured on runs




Total run bends do not exceed 360 degrees




Not in contact with water, gas pipes




Ground continuity to EMT




No interior splices







Pipe




Old gas pipe used, is the feed disconnected and capped




Bonding continuity at boxes, panels




Proper connectors for use (interior, exterior)




Properly secured on runs




Total bends do not exceed 360 degrees




Not in contact with water, gas pipes




Ground continuity to pipe




No interior splices







Junction Boxes, light fixture boxes, recepticle boxes




Proper binding to raceways, ground continuity




No missing punch-outs




Properly secured




Proper number of networks




Cover plates




Boxes proper for use (waterproof on exterior, depth, size)







Devices




UL listed




Ground continuity




Physically secure




Physical damage




Proper and secure cover plates




Waterproof boxes with covers on exterior and wet interior areas




Directly connected devices (disposer, furnace, doorbell transformers)










Receptcles




Physical damage




Proper for branch circuit amperage




Powered




Polarity




Grounding




Proper voltage




False Ground




Floating neutral




Properly installed (screwed connections and not back punched)




Proper location - Sinks, over electric baseboards, on open side of doors, height



In floor




Proper height above floor, countertop




Dedicated circuits for refrigerator, disposed, sump pump, washer, dryer



Voltage drop does not exceed 5% at 12 amps load




GFCI protection




AFCI protection




GFCI and AFCI have dedicated neutral







Light fixtures




Physical damage




Bare bulb fixtures




Fixture grounded




Chain chandelier, hanging by cord or chain




In proper location, not movable




Excessive bulb wattage







Ceiling fans




Physically secure




Balanced operation




Light and fan operation




Properly grounded







Switches




Coverplates proper and secure




Operation




If they don't work, is a light bulb burned out or is the switch defective




Grounded




Proper type dimmer switch for lights v.s. ceiling fan




Accessable - not behind furniture




Proper height




Proximity to water, sinks







General




Neatness of wiring




Evidence of owner or non-professional modifications / repair

Sorry for the format. Tried to insert an excell spreadsheet.



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #62  
Old 2/1/06, 10:39 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Electricians Check List

William,

Why not just send me the EXCEL sheet via e-mail and I will look it over, apply some corrections if needed...mostly on the spelling of "receptacle"...lol

Looks good for the most part but would prefer to get the excel file if possible and check it that way...much easier on the eyes I believe.



Paul W. Abernathy
Reply With Quote
  #63  
Old 2/1/06, 10:59 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Electricians Check List

Hi to all,

here it is sans scrolling, thanks Will:

Electrical Home Inspection Checklist
Inspection Point
Comments


Service Drop - Overhead
From Pole or Aerial Drop
Condition of Drop Cable
Obstruction by trees, buildings, etc
Clearances


Service Drop - Lateral
Service Pole Identifiable?
Enclosure of lateral run at pole
Exterior transformer on property, condition

Service splice
Drip loop
Weatherhead
Service entrance conductor gauge
Service Entrance Conduit (support, secured, condition, sealed)
Service meter rating
Service meter condition
Grounding at service meter?
Main Connect at meter (rating)
Service exterior wall penetration sealed


Service Equipment


Exterior Condition (rust, physical damage, properly secured)
Missing punch-outs
Verify proper grounding (exterior)
Electrified
Proper mounting (secure, on fireproof backing)
Face (directory, manufacturer, rating, age)
Face screws (proper number, blunt point)
Verify gauge of service entrance conductors to exterior
Neutral properly color coded or taped as neutral
Service entrance conductors properly bonded, corrosion
If SEC are aluminum, is anti-oxide paste in place, corrosion
Main Disconnect (rating, 'six throws' rule)
Raceways secured, bonded
Ground conductor bonded to service equipment and with neutral (main)
Ground conductor bonded to service equipment and with neutral (sub-panel)
Branch wire type, gauge, suitability to overcurrent devices
Overcurrent devices of proper type for the panel
Double taps on overcurrent devices
Ground and neutral bus double taps
Number of neutrals to hot conductors
Type of overcurrent devices, GFCI, AFCI
Connection corrosion
Insulator condition
Excessive pigtails
Wiring orderly, sufficient space in panel


Raceways


Proper number of networks per raceway
Type (K&T, ROMEX, BX, EMT, Pipe)
Knob and tube
Wire age, insullation type, condition
Splices
Connections to newer wiring, junction box
Condition of knobs and tubes, cracks, missing


ROMEX

Properly secured at boxes, panels
Excessive covering in panel, boxes
Properly secured on runs, proper staples, crushed wire
Ground wire bonded


BX

Properly secured and bonded at boxes, panels
Bushings in place
Ground wire bonded
If, in conjunction with EMT, is BX only used in whips, 6' or less
Properly secured on runs
No unprotected wall penetrations


EMT

Properly secured, bonded at boxes and panels
Properly bonded on run
Proper connectors for use (interior, exterior)
Properly secured on runs
Total run bends do not exceed 360 degrees
Not in contact with water, gas pipes
Ground continuity to EMT
No interior splices

Pipe
Old gas pipe used, is the feed disconnected and capped
Bonding continuity at boxes, panels
Proper connectors for use (interior, exterior)
Properly secured on runs
Total bends do not exceed 360 degrees
Not in contact with water, gas pipes
Ground continuity to pipe
no interior splices
Junction Boxes, light fixture boxes, recepticle boxes
Proper binding to raceways, ground continuity
No missing punch-outs
Properly secured
Proper number of networks
Cover plates
Boxes proper for use (waterproof on exterior, depth, size)


Devices


UL listed
Ground continuity
Physically secure
Physical damage
Proper and secure cover plates
Waterproof boxes with covers on exterior and wet interior areas
Directly connected devices (disposer, furnace, doorbell transformers)
Receptacles
Physical damage
Proper for branch circuit amperage
Powered
Polarity
Grounding
proper voltage
False Ground
Floating neutral
Properly installed (screwed connections and not back punched)
proper location - Sinks, over electric baseboards, on open side of doors, height In floor
Proper height above floor, countertop
Dedicated circuits for refrigerator, disposed, sump pump, washer, dryer
voltage drop does not exceed 5% at 12 amps load
GFCI protection
AFCI protection
GFCI and AFCI have dedicated neutral


Light fixtures


Physical damage
Bare bulb fixtures
Fixture grounded
Chain chandelier, hanging by cord or chain
In proper location, not movable
Excessive bulb wattage


Ceiling fans

Physically secure
Balanced operation
Light and fan operation
Properly grounded


Switches

Coverplates proper and secure
Operation
If they don't work, is a light bulb burned out or is the switch defective
Grounded
Proper type dimmer switch for lights v.s. ceiling fan
Accessable - not behind furniture
Proper height
Proximity to water, sinks



General

Neatness of wiring
Evidence of owner or non-professional modifications / repair

here it is as a word doc
Attached Files
File Type: doc Electrical Home Inspection Checklist.doc (38.5 KB, 188 views)



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106


Last edited by gbeaumont; 2/2/06 at 10:18 AM..
Reply With Quote
  #64  
Old 4/18/06, 12:40 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Electricians Check List

Bump...In case anyone missed it



Paul W. Abernathy
Reply With Quote
  #65  
Old 4/18/06, 12:58 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,785
Default Re: Electricians Check List

I did, Paul. Sorry.

E-mailed it to you.



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #66  
Old 4/18/06, 1:05 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Electricians Check List

Snap....Didn't Joe T look that over for you as well......Maybe it was one for Gerry I did.....heck I dont know....let me go back over and see if I can find that....

UPDATE- Ahh..I see you mailed it to me today...COOL...I will give it a gander......some how I thought you sent it to me before and i dropped the ball on it........hell I am sure I drop the ball on alot of things....

I will give it a gander Mr. Decker



Paul W. Abernathy
Reply With Quote
  #67  
Old 4/18/06, 1:44 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,785
Default Re: Electricians Check List

Thanks, Paul

Once you het it in a form you like, feel free to post it.



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #68  
Old 11/25/06, 8:28 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,049
Default Re: Electricians Check List

Thanks Paul A.
Came across this today and thought it was worthy of a bump

http://www.nachi.org/forum/attachmen...3&d=1136035954

Last edited by mlarson; 11/25/06 at 8:34 PM..
Reply With Quote
  #69  
Old 11/25/06, 9:14 PM
Greg Veal Greg Veal is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Woodstock, GA
Posts: 511
Default Re: Electricians Check List

Thanks Paul, this is good stuff.
Reply With Quote
  #70  
Old 11/26/06, 8:12 PM
mharris4's Avatar
mharris4 mharris4 is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: New Orleans, LA
Posts: 12
Default Re: Electricians Check List

Thanks Paul. I'm a new inspector and I really apreciate you sharing this with me. I hope I can repay the favor one day.



Mike Harris
Harris Property Inspections
New Orleans, LA
mike@harrispropertyinspections.com
LSHBI Lic# 10516 - NACHI ID# 06090383
Reply With Quote
  #71  
Old 12/5/07, 8:20 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Electricians Check List

Bump.....Newbies may want this......



Paul W. Abernathy
Reply With Quote
  #72  
Old 12/5/07, 12:25 PM
afrost afrost is offline
Active Poster
 
Join Date: Jan 2007
Location: Conway, NH
Posts: 356
Please Note: afrost is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electricians Check List

thank you, paul
Reply With Quote
  #73  
Old 12/5/07, 3:56 PM
mthomas2 mthomas2 is offline
Active Poster
 
Join Date: Oct 2005
Location: Evanston, IL
Posts: 703
Please Note: mthomas2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electricians Check List

Thanks
Reply With Quote
  #74  
Old 12/5/07, 6:06 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,908
Default Re: Electricians Check List

Old post I never saw either.
It pays to replay stuff this good.
So simple and basic yet essential as an aid in remembering what to go over.
Paul... you are a big asset.
Now you get a greenie.

Last edited by belliott; 12/6/07 at 1:23 AM..
Reply With Quote
  #75  
Old 12/5/07, 6:39 PM
Robert M. Delre Robert M. Delre is offline
New User
 
Join Date: Nov 2007
Location: Pittsburgh
Posts: 58
Please Note: Robert M. Delre is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electricians Check List

Thanks Paul!
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Electrical Check List - Probably posted before pabernathy Electrical Inspections 16 5/26/07 11:54 PM
Anyone created a Home Inspectors Electrical Check List jsieg Electrical Inspections 29 2/7/06 1:55 PM
Heat Pump Check list for inspecting dmacy Inspecting HVAC Systems 22 2/1/06 12:56 PM


All times are GMT -4. The time now is 3:30 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts