Paul;
Comments, criticism and great thought on this? Please? Electrical Home Inspection Checklist Item Inspection Point Comments Service Drop - Overhead From Pole or Aerial Drop Condition of Drop Cable Obstruction by trees, buildings, etc Clearances Service Drop - Lateral Service Pole Identifiable? Enclosure of lateral run at pole Exterior transformer on property, condition Service Entrance Service splice Drip loop Weatherhead Service entrance conductor gauge Service Entrance Conduit (support, secured, condition, sealed) Service meter rating Service meter condition Grounding at service meter? Main Connect at meter (rating) Service exterior wall penetration sealed Service Equipment Exterior Condition (rust, physical damage, properly secured) Missing punch-outs Verify proper grounding (exterior) Electrified Proper mounting (secure, on fireproof backing) Face (directory, manufacturer, rating, age) Face screws (proper number, blunt point) Verify gauge of service entrance conductors to exterior Neutral properly color coded or taped as neutral Service entrance conductors properly bonded, corrosion If SEC are aluminum, is anti-oxide paste in place, corrosion Main Disconnect (rating, 'six throws' rule) Raceways secured, bonded Ground conductor bonded to service equipment and with neutral (main) Ground conductor bonded to service equipment and with neutral (sub-panel) Branch wire type, gauge, suitability to overcurrent devices Overcurrent devices of proper type for the panel Double taps on overcurrent devices Ground and neutral bus double taps Number of neutrals to hot conductors Type of overcurrent devices, GFCI, AFCI Connection corrosion Insulator condition Excessive pigtails Wiring orderly, sufficient space in panel Raceways Proper number of networks per raceway Type (K&T, ROMEX, BX, EMT, Pipe) Knob and tube Wire age, insullation type, condition Splices Connections to newer wiring, junction box Condition of knobs and tubes, cracks, missing ROMEX Properly secured at boxes, panels Excessive covering in panel, boxes Properly secured on runs, proper staples, crushed wire Ground wire bonded BX Properly secured and bonded at boxes, panels Bushings in place Ground wire bonded If, in conjunction with EMT, is BX only used in whips, 6' or less Properly secured on runs No unprotected wall penetrations EMT Properly secured, bonded at boxes and panels Properly bonded on run Proper connectors for use (interior, exterior) Properly secured on runs Total run bends do not exceed 360 degrees Not in contact with water, gas pipes Ground continuity to EMT No interior splices Pipe Old gas pipe used, is the feed disconnected and capped Bonding continuity at boxes, panels Proper connectors for use (interior, exterior) Properly secured on runs Total bends do not exceed 360 degrees Not in contact with water, gas pipes Ground continuity to pipe No interior splices Junction Boxes, light fixture boxes, recepticle boxes Proper binding to raceways, ground continuity No missing punch-outs Properly secured Proper number of networks Cover plates Boxes proper for use (waterproof on exterior, depth, size) Devices UL listed Ground continuity Physically secure Physical damage Proper and secure cover plates Waterproof boxes with covers on exterior and wet interior areas Directly connected devices (disposer, furnace, doorbell transformers) Receptcles Physical damage Proper for branch circuit amperage Powered Polarity Grounding Proper voltage False Ground Floating neutral Properly installed (screwed connections and not back punched) Proper location - Sinks, over electric baseboards, on open side of doors, height In floor Proper height above floor, countertop Dedicated circuits for refrigerator, disposed, sump pump, washer, dryer Voltage drop does not exceed 5% at 12 amps load GFCI protection AFCI protection GFCI and AFCI have dedicated neutral Light fixtures Physical damage Bare bulb fixtures Fixture grounded Chain chandelier, hanging by cord or chain In proper location, not movable Excessive bulb wattage Ceiling fans Physically secure Balanced operation Light and fan operation Properly grounded Switches Coverplates proper and secure Operation If they don't work, is a light bulb burned out or is the switch defective Grounded Proper type dimmer switch for lights v.s. ceiling fan Accessable - not behind furniture Proper height Proximity to water, sinks General Neatness of wiring Evidence of owner or non-professional modifications / repair
Sorry for the format. Tried to insert an excell spreadsheet. Will Decker, CMI ILL License # 450.0002240 Board Certified Master Inspector Decker Home Services, LLC Chicago and Northern Suburban Home Inspections Office: (847) 676-8393 Cell: (847) 609-2345 Home: (847) 673-2702 wjd@DeckerHomeServices.com www.DeckerHomeServices.com Learn, Educate, Serve and have fun doing it! |
|
#62
|
|||
|
|||
|
William,
Why not just send me the EXCEL sheet via e-mail and I will look it over, apply some corrections if needed...mostly on the spelling of "receptacle"...lol Looks good for the most part but would prefer to get the excel file if possible and check it that way...much easier on the eyes I believe. Paul W. Abernathy |
|
#63
|
||||
|
||||
|
Hi to all,
here it is sans scrolling, thanks Will: Electrical Home Inspection Checklist Inspection Point Comments Service Drop - Overhead From Pole or Aerial Drop Condition of Drop Cable Obstruction by trees, buildings, etc Clearances Service Drop - Lateral Service Pole Identifiable? Enclosure of lateral run at pole Exterior transformer on property, condition Service splice Drip loop Weatherhead Service entrance conductor gauge Service Entrance Conduit (support, secured, condition, sealed) Service meter rating Service meter condition Grounding at service meter? Main Connect at meter (rating) Service exterior wall penetration sealed Service Equipment Exterior Condition (rust, physical damage, properly secured) Missing punch-outs Verify proper grounding (exterior) Electrified Proper mounting (secure, on fireproof backing) Face (directory, manufacturer, rating, age) Face screws (proper number, blunt point) Verify gauge of service entrance conductors to exterior Neutral properly color coded or taped as neutral Service entrance conductors properly bonded, corrosion If SEC are aluminum, is anti-oxide paste in place, corrosion Main Disconnect (rating, 'six throws' rule) Raceways secured, bonded Ground conductor bonded to service equipment and with neutral (main) Ground conductor bonded to service equipment and with neutral (sub-panel) Branch wire type, gauge, suitability to overcurrent devices Overcurrent devices of proper type for the panel Double taps on overcurrent devices Ground and neutral bus double taps Number of neutrals to hot conductors Type of overcurrent devices, GFCI, AFCI Connection corrosion Insulator condition Excessive pigtails Wiring orderly, sufficient space in panel Raceways Proper number of networks per raceway Type (K&T, ROMEX, BX, EMT, Pipe) Knob and tube Wire age, insullation type, condition Splices Connections to newer wiring, junction box Condition of knobs and tubes, cracks, missing ROMEX Properly secured at boxes, panels Excessive covering in panel, boxes Properly secured on runs, proper staples, crushed wire Ground wire bonded BX Properly secured and bonded at boxes, panels Bushings in place Ground wire bonded If, in conjunction with EMT, is BX only used in whips, 6' or less Properly secured on runs No unprotected wall penetrations EMT Properly secured, bonded at boxes and panels Properly bonded on run Proper connectors for use (interior, exterior) Properly secured on runs Total run bends do not exceed 360 degrees Not in contact with water, gas pipes Ground continuity to EMT No interior splices Pipe Old gas pipe used, is the feed disconnected and capped Bonding continuity at boxes, panels Proper connectors for use (interior, exterior) Properly secured on runs Total bends do not exceed 360 degrees Not in contact with water, gas pipes Ground continuity to pipe no interior splices Junction Boxes, light fixture boxes, recepticle boxes Proper binding to raceways, ground continuity No missing punch-outs Properly secured Proper number of networks Cover plates Boxes proper for use (waterproof on exterior, depth, size) Devices UL listed Ground continuity Physically secure Physical damage Proper and secure cover plates Waterproof boxes with covers on exterior and wet interior areas Directly connected devices (disposer, furnace, doorbell transformers) Receptacles Physical damage Proper for branch circuit amperage Powered Polarity Grounding proper voltage False Ground Floating neutral Properly installed (screwed connections and not back punched) proper location - Sinks, over electric baseboards, on open side of doors, height In floor Proper height above floor, countertop Dedicated circuits for refrigerator, disposed, sump pump, washer, dryer voltage drop does not exceed 5% at 12 amps load GFCI protection AFCI protection GFCI and AFCI have dedicated neutral Light fixtures Physical damage Bare bulb fixtures Fixture grounded Chain chandelier, hanging by cord or chain In proper location, not movable Excessive bulb wattage Ceiling fans Physically secure Balanced operation Light and fan operation Properly grounded Switches Coverplates proper and secure Operation If they don't work, is a light bulb burned out or is the switch defective Grounded Proper type dimmer switch for lights v.s. ceiling fan Accessable - not behind furniture Proper height Proximity to water, sinks General Neatness of wiring Evidence of owner or non-professional modifications / repair here it is as a word doc "To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future." (Mark B Adams) Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida. NACHI cell 484-429-5466 NACHI02121106 Last edited by gbeaumont; 2/2/06 at 10:18 AM.. |
|
#64
|
|||
|
|||
|
Bump...In case anyone missed it
Paul W. Abernathy |
|
#65
|
||||
|
||||
|
I did, Paul. Sorry.
E-mailed it to you. Will Decker, CMI ILL License # 450.0002240 Board Certified Master Inspector Decker Home Services, LLC Chicago and Northern Suburban Home Inspections Office: (847) 676-8393 Cell: (847) 609-2345 Home: (847) 673-2702 wjd@DeckerHomeServices.com www.DeckerHomeServices.com Learn, Educate, Serve and have fun doing it! |
|
#66
|
|||
|
|||
|
Snap....Didn't Joe T look that over for you as well......Maybe it was one for Gerry I did.....heck I dont know....let me go back over and see if I can find that....
UPDATE- Ahh..I see you mailed it to me today...COOL...I will give it a gander......some how I thought you sent it to me before and i dropped the ball on it........hell I am sure I drop the ball on alot of things.... I will give it a gander Mr. Decker Paul W. Abernathy |
|
#67
|
||||
|
||||
|
Thanks, Paul
Once you het it in a form you like, feel free to post it. Will Decker, CMI ILL License # 450.0002240 Board Certified Master Inspector Decker Home Services, LLC Chicago and Northern Suburban Home Inspections Office: (847) 676-8393 Cell: (847) 609-2345 Home: (847) 673-2702 wjd@DeckerHomeServices.com www.DeckerHomeServices.com Learn, Educate, Serve and have fun doing it! |
|
#68
|
||||
|
||||
|
Thanks Paul A.
Came across this today and thought it was worthy of a bump http://www.nachi.org/forum/attachmen...3&d=1136035954 Last edited by mlarson; 11/25/06 at 8:34 PM.. |
|
#69
|
|||
|
|||
|
Thanks Paul, this is good stuff.
|
|
#70
|
||||
|
||||
|
Thanks Paul. I'm a new inspector and I really apreciate you sharing this with me. I hope I can repay the favor one day.
Mike Harris Harris Property Inspections New Orleans, LA mike@harrispropertyinspections.com LSHBI Lic# 10516 - NACHI ID# 06090383 |
|
#71
|
|||
|
|||
|
Bump.....Newbies may want this......
Paul W. Abernathy |
|
#72
|
|||
|
|||
|
Please Note:
afrost is a non-member guest and is in no way affiliated with InterNACHI or its members.
thank you, paul
|
|
#73
|
|||
|
|||
|
Please Note:
mthomas2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Thanks
|
|
#74
|
||||
|
||||
|
Old post I never saw either.
It pays to replay stuff this good. So simple and basic yet essential as an aid in remembering what to go over. Paul... you are a big asset. Now you get a greenie. www.chicagopropertyinspection.com www.elliotthomeinspection.com www.chicagolandhomeinspection.com www.homeandcondoinspector.com www.homeandcondoinspection.com http://www.homeinspectorpro.com/ (Report Software) Bob Elliott http://www.chicagolandhomeinspector.com/ Last edited by belliott; 12/6/07 at 1:23 AM.. |
|
#75
|
|||
|
|||
|
Please Note:
Robert M. Delre is a non-member guest and is in no way affiliated with InterNACHI or its members.
Thanks Paul!
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Electrical Check List - Probably posted before | pabernathy | Electrical Inspections | 16 | 5/26/07 11:54 PM |
| Anyone created a Home Inspectors Electrical Check List | jsieg | Electrical Inspections | 29 | 2/7/06 1:55 PM |
| Heat Pump Check list for inspecting | dmacy | Inspecting HVAC Systems | 22 | 2/1/06 12:56 PM |