Angry Electrocution Hazard

Today’s panel inspection:
  1. Checked cover and screws with non contact and direct contact testers OK no response
  2. Carefully removed 3 of the 4 coarse thread pointed sheet metal screws without a hitch
  3. 4th screw was ¾ of the way out when the 4th of July fireworks started
  4. Sparks and the lovely aroma of welding gases mixed with vaporized plastic insulation
  5. What happened is the coarse threads cut through the insulation and made contact with the energized wire, blew the tip off of the screw
  6. Lost the other good screw in the flash and did not reinstall cover
  7. 89-year-old homeowner called her 71-year-old Bastard I mean Master Electrician son who built the house with his dad, he was missing all 5 digits and had burned scar tissue on his right hand down to the first knuckle. Wonder how that happened? He said, “Panel flash”
  8. His response was, “I wonder who used those unapproved screws?”
  9. Yeah, like anyone else had ever worked on the house
  10. Meter had it’s own 50 Amp disconnect and there was a fused service disconnect
  11. When I de-energized both none of the power was terminated to the entire house. Something’s fishy in Pottsboro, Texas
  12. I asked him how this could be seeing as how he wired the place and he grinned and said, “I dunno”
  13. Luckily I have all of my screw/nut drivers insulated with shrink-wrap from the tips back to the insulated handles minor ZAP and blacked my fingers but didn’t burn them
  14. BE CAREFUL OUT THERE
I thought things were safe after testing and this is what happened

ElectrocutionHazard.JPG



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good

Last edited by badair; 7/16/08 at 6:03 PM..
Reply With Quote
  #2  
Old 7/5/06, 9:58 PM
Doug Edwards's Avatar
Doug Edwards Doug Edwards is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Florida panhandle
Posts: 4,846
Default Re: Electrocution Hazard

Barry,
Glad to hear you are okay. You probably will just have to throw those underwear away...not fit to wash or wear again. I find sheetmetal screws all the time in panel covers. Always pulls my pucker string. Again, glad you survived. Take care.
Reply With Quote
  #3  
Old 7/5/06, 10:03 PM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,932
Default Re: Electrocution Hazard

I go COMMANDO tmi
Levi's stock will climb tomorrow!



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good
Reply With Quote
  #4  
Old 7/6/06, 12:04 AM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrocution Hazard

Quote:
Originally Posted by badair
Today’s panel inspection:

When I de-energized both none of the power was terminated to the entire house. Something’s fishy in Pottsboro, Texas
Are you thinking they are stealing power? If so, you should tip off the POCO.
Reply With Quote
  #5  
Old 7/6/06, 6:27 AM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,932
Default Re: Electrocution Hazard

What's a POCO?



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good
Reply With Quote
  #6  
Old 7/6/06, 8:43 AM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Electrocution Hazard

Glad to hear you are okay. It's usually putting the screws back in on a packed panel where things get interesting. I keep some blunt universal panel screws in my bag just so I don't have to re-install any pointy screws used.

Every HI should have a set of good insulated screwdrivers for working those panel screws (in addition to a pair of gloves, safety glasses, and insulated boots). It is probably the best $10 an HI will ever spend (available at Sears) ...

Quote:
Originally Posted by badair
What's a POCO?
Power Company

...
Attached Thumbnails
electrocution-hazard-gb_insulated_screwdrivers.jpg  



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #7  
Old 7/6/06, 8:47 AM
rwand1 rwand1 is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,861
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrocution Hazard

You can also put plastic tubing over shanks of screw drivers or electricians tape or plastic shrink tubes.
Reply With Quote
  #8  
Old 7/6/06, 8:55 AM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Electrocution Hazard

That may help keep hot wires from touching the shank, but if the tip goes hot (like when turning a panel screw that contacts a hot wire) you need a special insulated screwdriver to help keep you from becoming energized also ...

It's just not worth putting your life on the line to save just a few bucks. JMO



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #9  
Old 7/6/06, 9:23 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,923
Default Re: Electrocution Hazard

If there are zip screws in the dead panel, I won't open the panel.

I had one blow in my face when I was inspecting "home alone".

The Radon Mitigation Contractor was the culprit on that one!
Reply With Quote
  #10  
Old 7/6/06, 9:28 AM
rwand1 rwand1 is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,861
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrocution Hazard

Hi Robert,

Excuse my ignorance but with tape on the shank or plastic and a plastic handle how can the screw driver be energized let alone become a shock hazard?
Reply With Quote
  #11  
Old 7/6/06, 11:07 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Electrocution Hazard

Ray, the insulated screwdrivers like the ones I posted have a special construction and double non-conductive insulation between the shaft and the grip to keep electricity from jumping to your hand. Normal screwdrivers do not have that same protection. Compare the warnings/descriptions on insulated verses non-insulated electricians screwdrivers (some Klein examples attached).
Attached Thumbnails
electrocution-hazard-klein_insulated_screwdriver.jpg   electrocution-hazard-klein_non-insulated_screwdriver.jpg  
Attached Files
File Type: pdf Klein_Insulated_Screwdriver.pdf (130.6 KB, 140 views)
File Type: pdf Klein_Non-Insulated_Screwdriver.pdf (129.4 KB, 138 views)



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #12  
Old 7/6/06, 11:13 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Electrocution Hazard

Quote:
Originally Posted by badair
What's a POCO?
Short for Power Company.......lol



Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Maytag Recalls Dishwashers Due to Fire Hazard pabernathy Electrical Inspections 1 2/2/07 1:13 PM
Square D Electrocution Hazard Safety Switch Recall jtedesco1 Miscellaneous Discussion for Inspectors 5 12/16/06 12:09 AM
no ground (safety hazard?) brepanshek Electrical Inspections 1 6/12/06 3:30 PM


All times are GMT -4. The time now is 3:31 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts