Thanks Wilfred;
Just so everyone else know what happened at last weeks' meeting, I advised my Employer, that by the way use to work for me back 36 years ago, and well understanding, that I had done research on this accessability to these test buttons. He took my concern serious and discussed it with the Architect. Beleive it or not as I mentioned in the earlier posts, the Architect did not have a clue as to why his Electrical Consultant had specified these type of emergency lights instead of the normal wall packs. The first call he made was to his Consultant, and off the cuff could not give him a straight answer. One area of the building, "Cafe' shop" had 12 down lights in a suspended ceiling along with their test buttons and visual lights next to it. No one like that, and the consensus was to remove them and leave them above the tile ceilings, all but three to light up the exit. The room is about 400 s.f. and should be adequate to light up they exit. Next question in my mind is, dose that provide enough foot candles to meet code? I believe it is in the area of 3 foot candles per square feet, but not sure. The other areas with these test lights in drywall area ceilings were left mounted in the attic that is only accessible with a 12 foot ladder in one area and a 16' extention ladder in the other. Seems like everyone wants to gamble that the State Electrical Inspector will let this fly as to wether or not accessiblity has been met. Closing will be at the end of this month and expect to let everyone know how it went. My concerns were expressed on the job using the information I received from everyone, and greatly appreciate it. Now they know where I stand on the Project as a Project Superintendant and issues at hand. The outcome is not my disicion to make. Thanks everyone. Marcel |
|
#17
|
|||
|
|||
|
Good for you!!! Let me know how it turns out. OK?
|
|
#18
|
||||
|
||||
|
I will.
Marcel |
|
#19
|
||||
|
||||
|
Marcel, this was in Mike Holts newsletter today.
By Mike Holt for EC&M Magazine Emergency Lighting What are they and what are the rules? Emergency Power Systems (Article 700) are at the top of the hierarchy of backup power systems. Legally required standby systems, which fall under Article 701, hold the number two spot. Optional standby systems (Article 702) are third in the pecking order. The level of importance is the order in which they appear in the NEC. A system is legally required when any government agency having jurisdiction says it is. The rules that dictate what kinds of loads are legally required (or emergency) are found in the locally adopted building code, such as the International Building Code or NFPA 101 Life Safety Code. Unlike emergency systems, legally required systems do not directly protect the lives of the public at large. They prevent shutting down specific loads, the loss of which would create hazards or impede rescue operations. Hospital communications systems, for example, fall under Article 701 because evacuation instructions announced over the public address system are part of a rescue operation. Article 701 governs the installation, operation, and maintenance of such systems. Legally required circuits and equipment supply illumination or power upon interruption of the normal electrical supply. They provide electric power to aid in firefighting, rescue operations, control of health hazards, and similar operations. They typically supply such loads as communications systems, ventilation and smoke removal systems, sewage disposal, lighting, and potentially dangerous industrial processes. Surprisingly enough, they might also include fire pumps and elevators, which many people automatically assume are emergency loads. The definition of “Legally Required Standby Systems” in 701.2 contains a Fine Print Note that lists some of the items that might be a legally standby system…but be careful—Fine Print Notes are informational only [90.5(C)]. Don’t depend on this Fine Print Note as a comprehensive list. Always consult the AHJ and/or Fire Marshall to find out what is and what is not legally required…never just guess. When it’s optional A standby power system is optional when it’s not required by Article 700 or Article 701. These systems protect public or private facilities or property where life safety doesn’t depend on the performance of the system. These systems are not required for rescue operations. They may supply on-site generated power to selected loads automatically or manually. These are typically installed to provide an alternate source of power. This can be for a variety of facilities, including industrial and commercial buildings, farms, and even residences. They serve such loads as heating and refrigeration systems, data-processing systems, communications systems, and industrial processes. They may also serve any load that the customer considers important enough to warrant a backup system, but not important enough for a building code to require it, such as break room refrigerator or that all important coffee maker. These systems may be permanently installed, or they may be arranged for a connection to a premises wiring system from a portable alternate power supply (Figure 702-10). A portable generator doesn’t fall within the scope of Article 702 unless the generator is connected to the premises wiring (Figure 702-2). It should come as no surprise that the AHJ must approve all equipment use in legally required systems [701.4]. What may surprise you is this same rule applies to optional systems [702.4]. Tests and Maintenance While there are compelling operational and economic reasons to conduct testing and maintenance of optional systems, doing so is not an NEC requirement. But for legally required systems, it is [701.5]. Legally required standby system testing consists of acceptance testing and operational testing. You must maintain records of testing and maintenance [701.5(D)]. Conduct or Witness Test. The AHJ must conduct or witness an acceptance test of the emergency system upon completion of the installation, and periodically thereafter [701.5(D)]. Tested Periodically. Legally required standby systems must be periodically tested to ensure they are in proper operating condition. Running the system to power the loads of the facility is a generally accepted method of operational testing. In fact, you must provide a means to test these systems under the maximum anticipated load condition [701.5(E)]. Capacity and Rating Legally required and optional standby systems must have adequate capacity to safely carry all loads that are expected to operate simultaneously [701.6 and 702.5]. Because optional standby systems are not critical, the user of the system can select which load(s) to connect to the system. Additionally, both legally required standby system and optional standby system equipment must be suitable for the maximum available fault current at line terminals. The legally required standby alternate power source can supply legally required standby and optional standby system loads under either of these conditions [701.6]:
To protect utility workers, the backup system must have approved transfer equipment. Legally required standby systems and optional standby systems can be on the same transfer switch (emergency systems must have their own [700.6(D)]). On legally required systems, transfer equipment must be identified for standby use and be approved by the AHJ [701.7]. Where an outdoor generator has a readily accessible disconnecting means within sight (within 50 ft) of the structure, you don’t need an additional disconnecting means for the generator feeder conductors that serve or pass through the structure [701.11(5) and 702.1] (Figure 701-3). Signage To warn emergency response personnel of multiple electrical supply systems, both legally required and optional standby systems are required to have a sign indicating the presence of the system. This signage must be placed at the service disconnecting means for the structure, and must indicate the physical location of the standby systems power source [701.9(A) and 702.8(A)]. The remaining Chapter 7 power source requirements apply to legally required systems [701.11], but not to optional power sources. If the normal supply fails, legally required power must be available within 60 seconds (as opposed to 10 seconds for emergency systems). The supply system for the legally required standby power source must be one of these seven types:
The wiring for these systems can be in raceways, cables, boxes, and cabinets with other general wiring [701.10 and 702.9]. You don’t need to provide ground-fault protection of equipment on the alternate source of legally required standby power systems [701.17]. But you must ensure selective coordination [Article 100] of the Overcurrent Protection Devices (OCPDs) of legally required power systems with all supply-side OCPDs [701.18]. Selective coordination for optional standby systems is not a code requirement. Grounding and bonding If the system is separately derived, ground it per 250.30 [250.20(D)]. If it’s not separately derived, bond it to the system grounding electrode. Nothing in 701 explicitly states this, yet it’s explicitly stated in 702.10(B). When you step back and take a look at what each kind of standby system is trying to accomplish, the requirements make sense. Article 700 applies to systems or equipment required to protect people who are in an emergency and are trying to get out, while Article 701 applies to systems or equipment needed to aid the people responding to the emergency. Article 700 lighting provides an exit path, but Article 701 lighting illuminates fire hydrants and switchgear areas. Article 702 systems don’t protect people—they protect against financial loss. During the mass power outage in Chicago a few years ago, food storage facilities and medical laboratories lost millions of dollars of inventory. Optional standby systems could have prevented those losses, which is one reason we see optional standby systems in facilities where loss of power causes business interruptions. In an extended outage, the logistics of fuel delivery becomes a problem and this can force you to abandon your optional standby system. In 1994, for example, an ice storm shut down Kentucky interstate highways for three days. Companies that ran out of fuel for their optional standby systems were barred from “borrowing” the fuel from their legally required or emergency systems. If you can’t supply your legally required systems, you can’t legally operate. If you can’t supply your emergency systems, you typically can’t occupy the premises. To ensure that you don’t confuse what’s optional with what’s legally required, walk down your systems and identify which non-emergency circuits and equipment prevent danger or aid in rescuing people. Review this list with the AHJ and/or Fire Marshall, making any necessary additions. Everything else is optional. |
|
#20
|
||||
|
||||
|
Thank you Dale;
Very impressive description of Emergency lighting. Thanks. Marcel |
|
#21
|
||||
|
||||
|
Quote:
|
|
#22
|
||||
|
||||
|
Just thought I would bring this subject up again to kind of update everyone on the Emergency Access lighting issue.
Had the punchlist on this Visitors Center this past Wenesday and the Electrical Engineer walked through and I pointed out to him all the emergency light buttons on pedestals in the attic. He said, oh! I remember that the Architect was pretty upset that these buttons were to be in the ceilings near the fixtures. He said, well, that's what he wanted to do, is shove them up in the attic. The Architect walked through and was happy with everything that he saw. The State Electrical Inspector was notified for final Inspection last week and as of yet has not replied. It appears that he might not even show up. That is none to happen up hear. AHJ only covers permitting and plumbing. No Electrical. Certificate of Occupancy will be issued based on all other Inspection reports by the designers. Like this?? Only in Maine. ha. ha. I guess the interpetation of the NEC on accessibility did not prevail on this one. Marcel |
|
#23
|
|||
|
|||
|
Boy!, here in Florida you bet the electrical inspector would be there!!! Thats to bad that they dont up there. It would be interesting to see what he would say., Will Hellner
|
|
#24
|
||||
|
||||
|
There are only three State Electrical Inspectors to cover the whole State of Maine.
Maine is the size of the rest of the New England States, go figure. Marcel |
|
#25
|
||||
|
||||
|
Dale- YEP...Mike Holt is the "MACK DADDY" of NEC Consultants...I can only dream to know what they fella knows off the top of his head.
Marcel- GUess they are swamped and short handed......but you can guess if they did not inspect it and something ever does happen like a fire and the emergency systems have issues....lol......someone is taking a BITE.... Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Commercial Real Estate Doing Better than Housing | jbushart | Miscellaneous Discussion for Inspectors | 3 | 10/23/07 10:34 AM |
| Commercial Building & Thermal Imaging Course Coming to New Hampshire | fcarrio | Commercial Inspections | 1 | 8/13/07 1:47 AM |
| Article on Commercial and Residential Inspections and Assessment | mcyr | Commercial Inspections | 2 | 8/6/07 2:26 AM |