I was taught to use the lowest capacity device to estimate amperage. For instance, if the panel is rated for 100amps and the meter is rated for 200 amps, then the amperage is 100. Of course, the SE cables have to be considered too. My question is how to determine the amperage of the SE cables and the main disconnect. Typically the main will be labeled but what happens when the main disconnect is not labeled? How do we estimate that?
|
| Need a home inspection in Arkansas? Check out InterNACHI's listing of Arkansas certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
Mains are generally always labeled or the fuses for the main will have the ratings. WIies will also have marking to show gauge size. Every situation is different.
If you are ever not sure then you should take pics, do homework or disclaim you could not determine the amperage. Infraspection Institute Level 1 Certified Infrared Thermographer Fogarty Inspection Services Group of Knoxville TN Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas. 865-256-5397 www.homeinspectorknoxville.com www.moldandradon.com www.thermal-inspection.net www.commercial-building-inspector.net |
|
#3
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
As you gain more experience you should be able to visually gauge the wires compared to conductors and cables of a known size.
|
|
#4
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
You need to assess the conductor size and the Main OCPD size. It is possible to have over sized condcutors which would make the service ampacity the smaller of the two or the OCPD size. For most dwellings you could look at NEC {2008} Table 310.15(B)(6) and use that to find the service conductor ampacity.
|
|
#5
|
||||
|
||||
|
Based on type of wire and size ...
http://publicecodes.citation.com/ico..._36_sec003.htm Basically ... #4Cu = 100a, #1 Cu = 150A, and 2/0 Cu = 200A. Try some plastic gauges if you dont have a good feel for wire size or cant read any cable markings. Quote:
See this link for a good discussion ... http://www.inspectapedia.com/electric/ElecAmps.htm Robert O'Connor, PE Consulting Engineer & Inspector LIU CW Post Adjunct Professor NACHI Education Committee www.reporthost.com/-rjo I am absolutely amazed sometimes by how much thought goes into doing things wrong ... |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Determining Voltage as well as Amperage of a Service | twitt | Electrical Inspections | 10 | 6/30/11 2:36 PM |
| For New Inspectors doing Four-Point Inspection to dertermine wire size and Amperage | apelletier | Florida Inspectors | 3 | 3/17/11 7:12 AM |
| service amperage | tlemasters | Electrical Inspections | 1 | 3/20/10 1:51 PM |
| Amperage draw question | jbreazeale | Inspecting HVAC Systems | 5 | 7/26/07 3:02 AM |
| Service Entrance Amperage? | jfunderburk | Electrical Inspections | 18 | 6/16/06 10:16 PM |