Old 12/30/09, 1:31 PM
Default Evaluating your home's wiring system
Fome this Old Web
The Old House Web
Is knob and tube wiring adequate for modern living? Is your home's electrical service panel adequate? Here's a guide to inspecting older wiring.
Editor's note: This story is adapted from theU.S. Department of Housing and Urban Development's Residential RehabilitationInspection Guide, 2000.
Foundfairly often in houses built before 1930, "knob and tube" wiringshould be carefully inspected to failed insulation and other safety issues. Ifit has adequate capacity and is otherwise safe, it is still legal in manyplaces.
Electrical systems for small residential buildings areusually simple in concept and layout. Primary components are the:
  • service entry,
  • panel board, and
  • branch circuits.
Get your wiring checked.
In unaltered buildings built since about 1940, the electrical system islikely to be intact and safe, although it may not provide the capacity requiredfor the planned reuse of the building. Electrical capacity can be easilyincreased by bringing additional capacity in from the street and adding a largerpanel board between the service entry and the existing panel. Existing circuitscan continue to use the existing panel and new circuits can be fed through thenew panel.
The electrical systems of small residential buildings built prior to about1940 may require overhaul or replacement, depending on rehabilitation plans andthe condition of the electrical system. Parts of these older systems mayfunction very adequately and they can often be retained if the rehabilitation isnot extensive and the load-carrying capacity is adequate.
A thorough and informed assessment of the electrical system will determinethe extent to which it can be reused. This assessment should be conducted onlyby a qualified electrician who is experienced in residential electrical work.
When universal design is a part of a rehabilitation, consult the Housing andUrban Development publication Residential Remodeling and Universal Designfor detailed information about electrical devices.
Assessing the electrical capacity (ampacity) of the building's existing electrical serviceTo determine the capacity (measured in amperes) of the building's existingelectrical service at the main panel-board, check the following:
  • The ampacity of the service entry conductor, which may be determined by noting the markings (if any) on the conductor cable and finding its rated ampacity in the National Electrical Code, Table 310-16, or applicable local code. If the service entry conductor is in conduit, look for markings on the conductor wires as they emerge from the conduit into the panel board. If all conductors are unmarked, have an electrician evaluate them.
  • The ampere rating on the panel board or service disconnect switch, as listed on the manufacturer's data plate.
  • The ampere rating marked on the main circuit breaker or main building fuse(s). This rating should never be higher than the above two ratings; if it is, the system should not be used until it is evaluated by an electrician.
The building's service capacity is the lowest of the above threefigures.
Once the service ampacity has been determined, compare it to the estimatedampacity the building will require after rehabilitation. If the estimatedampacity exceeds the existing ampacity, the building's electrical service willneed upgrading. The method for estimating required ampacity is found in the NationalElectrical Code, Article 220.
Similarly, the service capacity of each branch circuit can be determined bychecking the markings on each branch circuit conductor. If no markings can befound, a plastic wire gauge may be used to measure the wire size (with the powerdisconnected), although an experienced person can often determine the size byeye. Find the ampere rating of the conductor, either by its markings or wiresize, in the National Electrical Code, Table 310-16, or applicable localcode.
The safety standards for the fol-lowing assessment procedures are generallybased on the requirements of the National Electrical Code.
Service Entry
Typical service equipment
Inspect for the following conditions in the electrical service between thestreet and the main panelboard:
  • Overhead wires. Check that overhead wires from the street are no lower than 10 feet above the ground, not in contact with tree branches or other obstacles, and not reachable from nearby windows or other accessible areas. Make sure that the wires are securely attached to the building with insulated anchors, and have drip loops where they enter the weatherhead. Spliced connections at the service entrance should be well wrapped, and bare wires from the street should be replaced by the utility company. Wires should not be located over swimming pools.
  • Electric meter. Check that the electric meter and its base are weatherproof, and that the meter is functional, has not been tampered with, and is securely fastened. Advise the utility company of any problems with the meter.
  • Seismic vulnerability. If the building is in a seismic zone, check the electrical service for vulnerability to differential movement between the exterior and interior. Look for flexible connections.
  • Service entrance conductor. Ensure that the service entrance conductor has no splices and that its insulation is completely intact. If the main panel board is located inside the building, the conductor's passage through the wall should be sealed against moisture. Where aluminum conductors are used, their terminations at all service equipment should be cleaned with an oxide inhibitor and tightened by an electrician or replaced with equal capacity copper conductors. When it is necessary to replace an overhead service entry, have it replaced with an underground service entry.
  • Type of power available. Not every jurisdiction provides the same kind of electrical power. Philadelphia, for example, has two-phase electrical power in some locations rather than the more common single-phase. Check with the power company to determine the characteristics of the power available.
Main panel boardThe main panel board is the distribution center for electric service withinthe building and protects the house wiring from overloads. Inspect the panelboard as follows:
  • Condition and location. Check the overall condition of the panel board. Water marks or rust on a panel mounted inside the building may indicate water infiltration along the path of the service entrance conductor. Panel boards mounted outdoors should be watertight and tamper proof. Panels mounted indoors should be located as closely as possible to where the service entrance conductor enters the building and should be easily accessible. The panel board should have a workable and secure cover.
  • Amperage rating. The amperage rating of the main disconnect should not be higher than the amperage capacity of the service entrance conductor or the panel board. If the rating is higher (indicating unapproved work has been done), more branch circuits may be connnected to it than the service entrance conductor is capable of supplying. This is a serious hazard and should be corrected.
  • Voltage rating. The voltage rating of the panel board (as marked on the manufacturer's data plate) should match the voltage of the incoming electrical service.
  • Test: The actual voltage rating of the incoming electrical service can be checked with a voltmeter. This test should be performed by an electrician. Usually three service conductors indicates 120/240 volt current, and two conductors indicates 120 volt current.
  • Grounding. (See illustration below) Verify that the panel board is properly grounded. Its grounding conductor should run to an exterior grounding electrode or be clamped to the metal water service inlet pipe between the exterior wall and the water meter. If it is attached on the house side of the meter, the meter should be jumpered to ensure proper electrical continuity to the earth. Make sure that the ground conductor is securely and properly clamped to the pipe-often it is not, and occasionally it is disconnected altogether. Ensure also that the grounding conductor is not attached to a natural gas pipe, to an inactive pipe that may be cut off on the exterior side of the wall, or to a pipe that is connected to a plastic water service entry line. If the grounding conductor is attached to an exterior grounding electrode driven into the earth, verify that the electrode is installed in accordance with local code. Many older buildings will have the ground connected to the cold water pipe. If this is the case and the building needs to conform to the current code, an alternate ground is required. Typical electrical service entry and main panel board for a single family residence. This type of grounding applies only if the water pipe is metal. If the water pipe is plastic, a separate driven ground rod is required.
Typical electricalservice entry and main panel board for a single family residence. This type ofgrounding applies only if the water pipe is metal. If the water pipe is plastic,a separate driven ground rod is required.
  • Test. An electrical ground (resistance-to-ground) test may be used to determine whether the electrical system is well grounded to the earth. The test requires the use of an ohm-meter and should be performed by an electrician.
  • Over-current protection. Check the rating of the fuse or circuit breaker for each branch circuit. The amperage of the fuse or circuit breaker should not exceed the capacity of the wiring in the branch circuit it protects. Most household circuits use #14 copper wire, which should have 15 amp protection. There may be one or more circuits with #12 copper wire, which should have 20 amp protection. Large appliances, such as electric water heaters and central air conditioners, may require 30 amp service, which is normally supplied by #10 copper wire. If there is an electric range, it would require a 40 or 50 amp service with #6 copper wire. Central air conditioning equipment will have an over-current protection requirement on the nameplate. Aluminum wire must be one size larger than copper wire in each case (e.g., #14 to #12), but it should not be used for 15 and 20 amp circuits. Make sure that no circuit has a fuse or circuit breaker with a higher ampere rating than its wiring is designed to carry. Air conditioners and other equipment with motors may have circuit breakers up to 175 percent ampacity of the conductor rating to allow for starting current. Look near the panel board for an inordinate number of new or blown fuses, or breakers taped in the "on" position. Be suspicious of 20 or 25 amp fuses on household lighting circuits. These are signs of frequent overloads and inadequate electrical service. Other indications of overloading are the odor of burned insulation, evidence of melted insulation, discolored copper contact points in the fuse holders, and warm fuses or circuit breakers.
  • Test: Flip all circuit breakers on and off manually to make sure they are in good operating condition. A commercially available circuit breaker and resistance tester, which can simulate an overload condition, can be used to test each breaker. Such a test should be performed by an electrician. Note that this test is not recommended for computers, VCRs, clocks, and many similar devices.
  • Many older residential buildings have more than one panel-board or fused devices. Check that all supplementary over-current devices are located in metal boxes and that they are not in the vicinity of easily ignitable materials. All panel boards must have covers. It should be possible to turn off all electrical power to a dwelling from a single location.
Branch CircuitsThe oldest types of residential wiring systems are seldom encountered today.They include open wires on metal cleats, wiring laid directly in plaster, andwiring in wooden molding. These systems proved quite hazardous.
The oldest wiring system that may still be acceptable, and one still foundfairly often in houses built before 1930, is "knob and tube." This systemutilizes porcelain insulators (knobs) for running wires through unobstructedspaces, and porcelain tubes for running wires through building components suchas studs and joists.
Note whether knob and tube wiring splices are mechanicallytwisted, soldered, and taped, as required. Knob and tube wiring should bereplaced during rehabilitation; but if it is properly installed, needs nomodification, has adequate capacity, is properly grounded, has no failedinsulation, and is otherwise in good condition, it can be an acceptable wiringsystem and is still legal in many localities.
Check with local building code officials. Also check the terms and conditionsof the home insurance policy in force to see if knob and tube wiring isexcluded. The greatest problem with such wiring is its insulation, which turnsdry and brittle with age and often falls off on contact, leaving the wireexposed. Insulation that can be seen to have failed also will likely have failedwhere wiring is concealed. If any failed insulation is observed, the knob andtube wiring should be replaced.
Other approved wire types include:
  • NM (non-metallic) cable, often called by the trade name "Romex," a plastic covered-cable for use in dry locations (older NM cable may be cloth covered).
  • NMC, similar to NM but rated for damp locations.
  • UF (underground feeder), a plastic-covered waterproof cable for use underground.
  • AC (armored cable), also called BX, a flexible metal-covered cable.
  • MC (metal-clad cable), a flexible metal-covered cable with a green insulated ground conductor.
  • EMT (electrical metallic tubing), also called "thinwall," a metal conduit through which the wires are run in areas where maximum protection is required.
Inthe picture at right, the armored cable and junction box are in good shape andcan be reused, even if the lighting fixture is relocated.
Check branch circuits for the following:
  • Marking. The function of each branch circuit should be clearly and legibly marked at its disconnect, fuse, circuit breaker, or on the directory on the panel board.
  • Connected loads. Trace branch circuit conductors to determine that their connected load does not exceed their rating (e.g., a 30 amp clothes dryer connected to a 20 amp circuit). Generally speaking, each dwelling unit should have two to four 15 amp circuits for lighting and convenience outlets; two 20 amp circuits for appliances in the kitchen, dining, and laundry areas; and separate circuits of appropriate ampacity for large appliances such as dryers, ranges, disposals, dishwashers, and water heaters.
  • Check the size and length of all branch circuit wiring against the requirements of the local electrical code. Buildings built before 1980 may be considered to have an inadequate number of circuits because present day codes require a separate laundry circuit and a separate circuit for the bathroom receptacle. For air conditioning units, many local codes will allow one wire size smaller than called for in the disconnect.
  • Test: A voltmeter may be used to measure voltage drop due to excessive branch circuit length, poor wiring connections, or undersized wire. Measurements must be made under a connected load. This test should be performed by an electrician.
  • Grounding. It is best that all circuits be grounded to the panel board, but this was not required by the National Electrical Code prior to 1965. Do not assume that circuits in metal cable are grounded without testing each outlet. Also, do not assume that three-prong plug convenience outlets are connected to ground. Remove each one to observe the presence of a connected ground wire. Check to see whether GFI (ground fault interruption) type receptacles have been installed in laundries, kitchens, and bathrooms, and test their operation. These types of receptacles were not required before 1990, but are easily installed as replacements.
  • Test: Commercially available circuit analyzers can be used for checking thefollowing circuit conditions: open ground, open hot, open neutral, hot/groundreversed, hot/neutral reversed. Operation of these analyzers varies bymanufacturer.
  • Condition and safety. Check that all wire types and equipmentare installed properly in accordance with good practice. Check the conductors' exposure to possible damage or abrasion. Look for proper fastening, clearance,and frayed or damaged insulation. Make certain that all wire splices are madein work boxes and that all boxes for splices and switches have cover plates.Check all exterior receptacles to make sure they are of the waterproof type.
  • Test: A megohm test may be used for detecting deteriorated insulation. Itrequires a Megger tester and operates at high voltage. With the electricalservice disconnected, branch circuits should read at least one megohm to ground.If lights or appliances are connected to the circuit, readings should be atleast 500,000 ohms. This test should be performed by an electrician.
  • A visualinspection of insulation on accessible circuits will usually determine whether additional tests should be performed by an electrician. Look for unprotectedwire runs through ducts and other inappropriate areas. Inspect for evidence of"handyman tampering" (e.g., unconventional splices), and if found in onelocation, expect it to be more widespread. Check for surface-mounted lamp cordextension wiring. It is dangerous and must be removed. It is best to remove allunused wiring or wiring that will be abandoned during rehabilitation work toavoid future confusion or misuse.
  • Aluminum wire. Aluminum wire was used inresidential buildings primarily during the 1960s and early 1970s. Inspect withlocal code requirements in mind. Be sure that aluminum wire is attached only toapproved devices (marked "CO-ALR" or "ICU-AL") or to approvedconnectors. Problems with aluminum wiring occur at connections, so feel allcover plates for heat, smell for a distinctive odor in the vicinity of outletsand switches, and look for sparks and arcing in switches or outlets and forflickering lights. Also check for the presence of an oxide inhibitor on allaluminum wire connections. All such conditions should be corrected. Aluminumwire should not be used on 15 and 20 amp circuits. Whenever possible, aluminumwire and its devices should be replaced with copper wire and devices appropriatefor copper. If aluminum wiring is not replaced, it must be frequently inspectedand maintained.
  • Smoke Detectors. Check to see if buildings have functioningsmoke detectors. Detectors should be wired to a power source, and also should contain a battery. Most likely, buildings built before 1970 will not havedetectors, but they should be added.
Hope it helps some.
old wiring systems in homes? rlondon Electrical Inspections 4 5/20/09 6:07 PM
Top Ten Wiring Hazards jtedesco1 Electrical Inspections 6 9/1/08 8:26 PM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 9:24 AM
New Washington Legislation Submitted gdomagala Legislation, Licensing & Legal Issues for Inspectors 294 2/10/08 1:20 AM
Massachusetts Board of Registration of Home Inspectors jtedesco1 Legislation, Licensing & Legal Issues for Inspectors 0 2/14/06 3:38 AM