Default Ever wonder if the conductor is sized properly?

This was a 40 amp breaker to an evap cooler. Often I see conductors with no awg size on the insulation and no way to view the conductor.
Attached Thumbnails
ever-wonder-if-conductor-sized-properly-arrows.jpg   ever-wonder-if-conductor-sized-properly-text-arrow.jpg  
Reply With Quote
Find an InterNACHI certified Wyoming Home Inspector (and anywhere else in North America)
  #2  
Old 3/26/09, 9:32 PM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 668
Default Re: Ever wonder if the conductor is sized properly?

Yes, I have often wondered, but knowing that I can't comment on what I can't see.....



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #3  
Old 3/26/09, 10:45 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,342
Send a message via Yahoo to jfunderburk
Default Re: Ever wonder if the conductor is sized properly?

Personally, my policy is to never put my hands inside the panel box. Little chance for error.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #4  
Old 3/30/09, 8:21 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,206
Default Re: Ever wonder if the conductor is sized properly?

Who would you pose the question to Joe?

Do you really think one of those service wires is going to jump up in that crack and get damaged? LOL

Seriously, thanks for the code reference but please don't make posts that might cause some rookie inspector to make a ridiculous writeup.

The part has not failed in a way that matters to anyone.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #5  
Old 4/5/09, 1:32 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Ever wonder if the conductor is sized properly?

Agreed. I would spend my concern on the conductors sized to that breaker. Since their is a dramatic size difference in those conductors you would not really need to know the nameplate rating of the equipment to know something smells fishy here.

Call it out to be evaluated, if you are able to see a nameplate then thats just a bonus as it should tell you the size minimums and OCPD maximums.

Now I am not an expert on Evaporator Equipment...to be quite honest I have never seen one...lol.....but based on UL it should have a label giving the information needed and if it does not then leave it to the electrician to determine motor size and OCPD compliance....you have done your job in finding it....Nice Job !

One thing I would look for is are the two different size conductors pulled in a conduit to the equipment and other things but beyond what you really need to do. Quite possibly they used a conduit and while the nameplate says maximum OCPD is 40 and minimum ampacity is lets say 26A...so they put a 10 AWG on one and had some spare 8 AWG laying around....and used it......who knows as I can't see it.....but it is was 8AWG and solid....and in a conduit we could atleast bang them for 310.3 standed conductor in raceways.....

Alas...all good things but if you walk away scratching your head, always remove your liability to the electrical contractor....maybe it is compliant and the electrician laughs and so on...who cares...if it concerns you...it needs to concern your client until someone else says otherwise and removes your liability.



Paul W. Abernathy
Reply With Quote
  #6  
Old 4/6/09, 2:49 AM
Frank M. Carrio, CMI's Avatar
Frank M. Carrio, CMI Frank M. Carrio, CMI is offline
ESOP Committee Member
 
Join Date: Jan 2004
Posts: 4,364
Default Re: Ever wonder if the conductor is sized properly?

Quote:
Originally Posted by gheller View Post
This was a 40 amp breaker to an evap cooler. Often I see conductors with no awg size on the insulation and no way to view the conductor.
No AWG size.... That is why I ALWAYS carry a PLASTIC "Wire Gauge" that will tell you the size!

You can insert the wire into the appropriate slot until you get a "snug fit" and then you will eliminate ANY and ALL guess work!

Those who advocate carrying around a “bundle of cut wires” and trying to VISUALLY MATCH the wire in their hands to the wires in the panel box usually wind up in court when something happens and they say;

…. Well your Honor…. Lookie here…. I just grabbed that ol bundle of wires and took a wild a** guess as to which one it was!
Why heck… I have been doing that for years and years!
Now I know that that this New Fangled “Wire Gauge” came out over 30-years ago but….. My Daddy used to carry around a handful of wires and… he told me that there is no use of trying EVERY New Fangled thing that comes out!
Why they cost about $17.50 and there is no reason to be throwing my money away for no reason!

{I testify as an Expert Witness in the judicial systems of Rhode Island, Massachusetts, New Hampshire and Maine. I just paraphrased what I have heard from at least 7-country bumpkins / handymen / home inspectors who got sued when valuable equipment “got fried” and or a panel box went up in flames! They ALL lost in court! }

My suggestion?
By a PLASTIC "Wire Gauge" and eliminate ALL of the guesswork!

Good Luck!








Signed, Frank Carrio, CMI
Certified Master Inspector & Consultant
Certified Commercial Building Inspector
Certified, WDI Inspector
Founder & Current President, New Hampshire State Chapter NACHI
NACHI, State Representative for Legislative Affairs
Retired: ICC Certified Member
Retired: Code Compliance Inspector.
Retired: ASTM Committee Member
New Hampshire License #0096
Reply With Quote
  #7  
Old 4/7/09, 12:07 AM
Marc Benz Marc Benz is offline
Active Poster
 
Join Date: Sep 2007
Location: Paris France for now
Posts: 138
Please Note: Marc Benz is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Ever wonder if the conductor is sized properly?

If you look at the photo little more closer look like they used unshrunked tube to fit over white conductor to remark it as hot conductor.

And that methold is Legit in some area.

Yeah the heatshrink tubing is good way to use the indentify the conductors.

[ It is a standard pratice we done that for very long time in France ]

Merci,Marc
Reply With Quote
  #8  
Old 6/25/09, 10:36 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Ever wonder if the conductor is sized properly?

Quote:
Originally Posted by fcarrio View Post
No AWG size.... That is why I ALWAYS carry a PLASTIC "Wire Gauge" that will tell you the size!

You can insert the wire into the appropriate slot until you get a "snug fit" and then you will eliminate ANY and ALL guess work!

Those who advocate carrying around a “bundle of cut wires” and trying to VISUALLY MATCH the wire in their hands to the wires in the panel box usually wind up in court when something happens and they say;

…. Well your Honor…. Lookie here…. I just grabbed that ol bundle of wires and took a wild a** guess as to which one it was!
Why heck… I have been doing that for years and years!
Now I know that that this New Fangled “Wire Gauge” came out over 30-years ago but….. My Daddy used to carry around a handful of wires and… he told me that there is no use of trying EVERY New Fangled thing that comes out!
Why they cost about $17.50 and there is no reason to be throwing my money away for no reason!

{I testify as an Expert Witness in the judicial systems of Rhode Island, Massachusetts, New Hampshire and Maine. I just paraphrased what I have heard from at least 7-country bumpkins / handymen / home inspectors who got sued when valuable equipment “got fried” and or a panel box went up in flames! They ALL lost in court! }

My suggestion?
By a PLASTIC "Wire Gauge" and eliminate ALL of the guesswork!

Good Luck!





So you are basically telling NACHI members to stick their hands inside a live panel to use your "Plastic" wire gage. How about learning what the size of the wires look like and train your eye versus telling members to remove a conductor from a termination and put it in a gage as you say.....to determine wire size.

I guess you lost your copy of the SOP....I would say learn the sizes and if you can't tell...dont guess at all and list as such...that you are not able to determine. insulation will change the results of the gages in many cases.



Paul W. Abernathy

Last edited by pabernathy; 6/25/09 at 10:56 PM..
Reply With Quote
  #9  
Old 6/25/09, 10:43 PM
Ben J. Gromicko's Avatar
Ben J. Gromicko Ben J. Gromicko is offline
InterNACHI Member
 
Join Date: Nov 2003
Location: Boulder, CO
Posts: 2,224
Default Re: Ever wonder if the conductor is sized properly?

ever-wonder-if-conductor-sized-properly-white-neutral-re-identified.jpgI agree with Marc. In the picture, I see a white neutral that was re-identified.
This wire was loose or did you disconnect and pull it out?

http://www.nachi.org/electrical-pane...-challenge.htm



BEN GROMICKO
InterNACHI Director of Education
"
Now That You've Had a Home Inspection" Book
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Electricians Check List pabernathy Electrical Inspections 74 12/5/07 6:39 PM
Canadians for Properly Built Homes (CPBH). New Home Warranty. gromicko Canadian Inspectors 4 2/24/07 9:33 PM
Another reason to recommend CO testers rnewman1 Interior Inspections 2 10/12/06 7:47 AM
4 Custom sized NACHI shirts available... lendza Miscellaneous Discussion for Inspectors 16 4/26/06 6:46 PM


All times are GMT -4. The time now is 3:31 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts