Default Excused "Ganged Neutrals" from Electrician

Wrote up and kicked back... everyday it seems...

I clipped this from the pdf and didn't show his name...

Maybe he knows something different than


NEC 408.41 Each grounded conductor shall terminate within a panel board in an individual terminal that is not used for any other conductor. (Bold is mine)


Another day...



- Mike

Michael W. Gault, SC RBI 1728
A to Z Home Inspections
Charleston, Dorchester & Berkeley Counties in S.C.
NACHI05040682
www.atozinspector.com

(843) 442-9755
Charleston Home Inspector
Reply With Quote
  #2  
Old 12/3/07, 7:23 PM
Michael W. Gault's Avatar
Michael W. Gault Michael W. Gault is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Mount Pleasant, SC
Posts: 1,093
Default Re: Excused "Ganged Neutrals" from Electrician

Picture too big.

His statement:

"The National Electric Code allows this wiring method in homes not required to have an outside disconnect. I checked all of the connections and they were tight"

Is he correct?



- Mike

Michael W. Gault, SC RBI 1728
A to Z Home Inspections
Charleston, Dorchester & Berkeley Counties in S.C.
NACHI05040682
www.atozinspector.com

(843) 442-9755
Charleston Home Inspector
Reply With Quote
  #3  
Old 12/3/07, 7:39 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Excused "Ganged Neutrals" from Electrician

His statement doesn't make any sense.

Quote:
in homes not required to have an outside disconnect
This has no relevance to the issue of "ganged neutrals."



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #4  
Old 12/3/07, 7:49 PM
Michael W. Gault's Avatar
Michael W. Gault Michael W. Gault is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Mount Pleasant, SC
Posts: 1,093
Default Re: Excused "Ganged Neutrals" from Electrician

Below is what I sent the client (buyer)




Here’s a picture to explain and a quote from the NEC and another to show why they should not share a lug…

NEC 408.41 Each grounded conductor shall terminate within a panel board in an individual terminal
that is not used for any other conductor. (Bold is mine)


A Grounded Conductor is a Neutral (White wire) a Grounding Conductor is a bare wire.


They’re not correct and his NEC ‘quote’ is wrong.

-Mike



- Mike

Michael W. Gault, SC RBI 1728
A to Z Home Inspections
Charleston, Dorchester & Berkeley Counties in S.C.
NACHI05040682
www.atozinspector.com

(843) 442-9755
Charleston Home Inspector
Reply With Quote
  #5  
Old 12/3/07, 8:15 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Excused "Ganged Neutrals" from Electrician

Quote:
Originally Posted by mgault
A Grounded Conductor is a Neutral (White wire) a Grounding Conductor is a bare wire.
I would have omitted this part, but I agree with the rest of your assessment.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #6  
Old 12/3/07, 8:17 PM
Michael W. Gault's Avatar
Michael W. Gault Michael W. Gault is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Mount Pleasant, SC
Posts: 1,093
Default Re: Excused "Ganged Neutrals" from Electrician

My wife always says "Less is More"

or that I "Talk like a teenage girl on the telephone"...

Don't know where that came from; we have two grown sons...



- Mike

Michael W. Gault, SC RBI 1728
A to Z Home Inspections
Charleston, Dorchester & Berkeley Counties in S.C.
NACHI05040682
www.atozinspector.com

(843) 442-9755
Charleston Home Inspector
Reply With Quote
  #7  
Old 12/3/07, 8:40 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Excused "Ganged Neutrals" from Electrician

My bet is his reference to the outside disconnect was his way of saying this was not a sub panel and the grounds can be on the neutral bar. Maybe he doesn't know they codified the "individual terminal" language for grounded conductors in 2002. Plenty of electricians doubled up the neutral and ground for each circuit and lots of inspectors passed it. (not me, I was a Tedesco student)
Reply With Quote
  #8  
Old 12/3/07, 8:57 PM
Michael W. Gault's Avatar
Michael W. Gault Michael W. Gault is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Mount Pleasant, SC
Posts: 1,093
Default Re: Excused "Ganged Neutrals" from Electrician

Quote:
Originally Posted by Greg Fretwell
My bet is his reference to the outside disconnect was his way of saying this was not a sub panel and the grounds can be on the neutral bar. Maybe he doesn't know they codified the "individual terminal" language for grounded conductors in 2002. Plenty of electricians doubled up the neutral and ground for each circuit and lots of inspectors passed it. (not me, I was a Tedesco student)
Still seeing it nearly everyday (okay twice a week now, they're doing it correct in most New Construction)



- Mike

Michael W. Gault, SC RBI 1728
A to Z Home Inspections
Charleston, Dorchester & Berkeley Counties in S.C.
NACHI05040682
www.atozinspector.com

(843) 442-9755
Charleston Home Inspector
Reply With Quote
  #9  
Old 12/4/07, 1:29 AM
Erby Crofutt's Avatar
Erby Crofutt Erby Crofutt is offline
InterNACHI Member
 
Join Date: Sep 2002
Location: Georgetown, KY
Posts: 1,184
Default Re: Excused "Ganged Neutrals" from Electrician

Here's what I tell em. They can like it or not!

======
The problem(s) discovered in the panel such as
  • Item # 1 yada yada
  • Item # 2 yada yada
  • more than one “grounded conductor” (neutral /white) wire per screw on the neutral bus bar (double tapped/lugged) Each “grounded conductor” is supposed to have it’s very own screw on the bus bar, no other “grounded conductor” or “ungrounded conductor” (bare copper wire) should be under the screw with the “grounded conductor”.
    {Some electricians (who haven't done their homework) will tell you that it is OK to have more than one neutral (white) wire under a screw on the bus bar. They are wrong. It has long (at least as far back as 1967) been required by manufacturer's instructions and Underwriters Laboratories Standard 67 for panelboards. See this link for a narrative description of the reason for single neutral wire - single screw. Double Lugged Neutral Narrative Also see this link for a visual interpretation. Double Lugged Neutrals Visual}. Ensure the electrician is familiar with UL Standard 67 requirements
and any other problems that an electrician may discover while performing repairs need correcting. I recommend a licensed electrician repair as needed.
===========

So goes life. You can lead a horse to water. You can shove his head under the water, but you an't make them drink.
Reply With Quote
  #10  
Old 12/4/07, 2:09 AM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 6,929
Default Re: Excused "Ganged Neutrals" from Electrician

Quote:
Quote:
Originally Posted by ecrofutt
more than one “grounded conductor” (neutral /white) wire per screw on the neutral bus bar (double tapped/lugged) Each “grounded conductor” is supposed to have it’s very own screw on the bus bar, no other “grounded conductor” or “ungrounded conductor” (bare copper wire) should be under the screw with the “grounded conductor”.
{Some electricians (who haven't done their homework) will tell you that it is OK to have more than one neutral (white) wire under a screw on the bus bar.
Like this one built in 2003. Nice work, but a little lazy when there were plenty of screws left open on the bar.



Christopher Currins
Certified, Licensed

Proudly serving the Illinois Metro-East

Illinois Home Inspector

Top 5 Tasks for January

Last edited by ccurrins; 4/20/09 at 1:47 AM..
Reply With Quote
  #11  
Old 12/4/07, 2:57 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Excused "Ganged Neutrals" from Electrician

That is a guy who thinks that is the "right" way. I know it was a very popular way to wire circuits. They thought grouping them was a good thing for some reason. That guy even twisted them together. It certainly wasn't easier or faster
Reply With Quote
  #12  
Old 12/4/07, 8:25 AM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Excused "Ganged Neutrals" from Electrician

In NY this is not expressly forbidden in resi work. We follow the NY Residential Code and the wording in NEC 408.41 is absent.
You could quote the 408.41 all day long and you'd still be wrong by calling it out. I've even had one of the head inspectors in my area confirm this when I questioned HIM about it.
90% of the other guys I see do it this way.
Maybe SC is similar?

That said..... I used to do this in every panel. It makes for a nice neat panel and there is no searching for the paired ground and neutral when working on a circuit. It has ABSOLUTELY nothing to do with "laziness".

In recent years I have stopped doing it this way. Mainly because it is in the NEC and it is one less thing that can be questioned later. Obviously the NY code is lacking in some areas so I fill in with the NEC when I can.
Reply With Quote
  #13  
Old 12/4/07, 8:36 AM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,842
Default Re: Excused "Ganged Neutrals" from Electrician

this method must be infectious...just yesterday...some of the grounds aren't under their lug screw just twisted around the rest...looked like homer had been here



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good

Last edited by badair; 9/30/08 at 8:59 PM..
Reply With Quote
  #14  
Old 12/4/07, 9:14 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Excused "Ganged Neutrals" from Electrician

Speedy...what about 408.21 when it was in the 2002 NEC? Did NY also ignore its statement then as well?



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #15  
Old 12/4/07, 9:20 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: Excused "Ganged Neutrals" from Electrician

Even if NY ignored both how does that let them ignore UL67 and the mfgs. instructions?
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Electrician signs off 'ganged neutrals'...now what? mgault Electrical Inspections 16 6/3/07 12:09 AM
Electrician or handyman repair? srowe Electrical Inspections 8 1/4/07 10:21 AM