Wrote up and kicked back... everyday it seems...
I clipped this from the pdf and didn't show his name... Maybe he knows something different than NEC 408.41 Each grounded conductor shall terminate within a panel board in an individual terminal that is not used for any other conductor. (Bold is mine) Another day... - Mike Michael W. Gault, SC RBI 1728 A to Z Home Inspections Charleston, Dorchester & Berkeley Counties in S.C. NACHI05040682 www.atozinspector.com (843) 442-9755 Charleston Home Inspector |
|
#2
|
||||
|
||||
|
Picture too big.
His statement: "The National Electric Code allows this wiring method in homes not required to have an outside disconnect. I checked all of the connections and they were tight" Is he correct? - Mike Michael W. Gault, SC RBI 1728 A to Z Home Inspections Charleston, Dorchester & Berkeley Counties in S.C. NACHI05040682 www.atozinspector.com (843) 442-9755 Charleston Home Inspector |
|
#3
|
||||
|
||||
|
His statement doesn't make any sense.
Quote:
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ℠ Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#4
|
||||
|
||||
|
Below is what I sent the client (buyer)
Here’s a picture to explain and a quote from the NEC and another to show why they should not share a lug… NEC 408.41 Each grounded conductor shall terminate within a panel board in an individual terminal that is not used for any other conductor. (Bold is mine) A Grounded Conductor is a Neutral (White wire) a Grounding Conductor is a bare wire. They’re not correct and his NEC ‘quote’ is wrong. -Mike - Mike Michael W. Gault, SC RBI 1728 A to Z Home Inspections Charleston, Dorchester & Berkeley Counties in S.C. NACHI05040682 www.atozinspector.com (843) 442-9755 Charleston Home Inspector |
|
#5
|
||||
|
||||
|
Quote:
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ℠ Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#6
|
||||
|
||||
|
My wife always says "Less is More"
or that I "Talk like a teenage girl on the telephone"... Don't know where that came from; we have two grown sons... - Mike Michael W. Gault, SC RBI 1728 A to Z Home Inspections Charleston, Dorchester & Berkeley Counties in S.C. NACHI05040682 www.atozinspector.com (843) 442-9755 Charleston Home Inspector |
|
#7
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
My bet is his reference to the outside disconnect was his way of saying this was not a sub panel and the grounds can be on the neutral bar. Maybe he doesn't know they codified the "individual terminal" language for grounded conductors in 2002. Plenty of electricians doubled up the neutral and ground for each circuit and lots of inspectors passed it. (not me, I was a Tedesco student)
|
|
#8
|
||||
|
||||
|
Quote:
- Mike Michael W. Gault, SC RBI 1728 A to Z Home Inspections Charleston, Dorchester & Berkeley Counties in S.C. NACHI05040682 www.atozinspector.com (843) 442-9755 Charleston Home Inspector |
|
#9
|
||||
|
||||
|
Here's what I tell em. They can like it or not!
====== The problem(s) discovered in the panel such as
=========== So goes life. You can lead a horse to water. You can shove his head under the water, but you an't make them drink. -- Erby Crofutt B4U Close Home Inspections Georgetown, Kentucky KY Lic# HI-2041 www.b4uclose.com http://www.kentuckyradon.com Kentucky Home Inspections Kentucky Home Inspectors NACHI02090301 Read my Active Rain Blog here: Erby, The Central Kentucky Home Inspector Join Active Rain HERE and I'll get some points for your participation. Please! I did ask nice! |
|
#10
|
||||
|
||||
|
Please Note:
ccurrins is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Last edited by ccurrins; 4/20/09 at 1:47 AM.. |
|
#11
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
That is a guy who thinks that is the "right" way. I know it was a very popular way to wire circuits. They thought grouping them was a good thing for some reason. That guy even twisted them together. It certainly wasn't easier or faster
|
|
#12
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
In NY this is not expressly forbidden in resi work. We follow the NY Residential Code and the wording in NEC 408.41 is absent.
You could quote the 408.41 all day long and you'd still be wrong by calling it out. I've even had one of the head inspectors in my area confirm this when I questioned HIM about it. 90% of the other guys I see do it this way. Maybe SC is similar? That said..... I used to do this in every panel. It makes for a nice neat panel and there is no searching for the paired ground and neutral when working on a circuit. It has ABSOLUTELY nothing to do with "laziness". In recent years I have stopped doing it this way. Mainly because it is in the NEC and it is one less thing that can be questioned later. Obviously the NY code is lacking in some areas so I fill in with the NEC when I can. |
|
#13
|
||||
|
||||
|
this method must be infectious...just yesterday...some of the grounds aren't under their lug screw just twisted around the rest...looked like homer had been here
badair ADAIR INSPECTION 972-487-5634 Residential-Commercial-Construction-EIFS-Infrared Thermography TREC # 4563 EDI: EIFS-MA TX # 39 2008 US Member of the Year life is the random lottery of events followed by numerous narrow escapes...accept the good Last edited by badair; 9/30/08 at 8:59 PM.. |
|
#14
|
||||
|
||||
|
Speedy...what about 408.21 when it was in the 2002 NEC? Did NY also ignore its statement then as well?
Paul W. Abernathy,CMI,CEI,CEPE NEC® Consultant/Columnist www.twitter.com/ElectricalGuru - ICC & IAEI Certified Electrical Inspector - ICC & IAEI Certified Electrical Plans Examiner - Look for my article in the Nov/Dec 2009 IAEI Magazine - 2007 "Top Gun" Winner - Mike Holt Enterprises " visit www.TheElectricalGuru.com Today !" |
|
#15
|
||||
|
||||
|
Even if NY ignored both how does that let them ignore UL67 and the mfgs. instructions?
|
![]() |