Default Extension cords in a 'permanent' application

New Construction using an extension cord to plug in both garage door openers - how would you call it out?...
Attached Thumbnails
extension-cords-permanent-application-13-nov-07-078.jpg  



- Mike

Michael W. Gault, SC RBI 1728
A to Z Home Inspections
Charleston, Dorchester & Berkeley Counties in S.C.
NACHI05040682
www.atozinspector.com

(843) 442-9755
Charleston Home Inspector
Reply With Quote
  #2  
Old 11/13/07, 6:40 PM
Michael W. Gault's Avatar
Michael W. Gault Michael W. Gault is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Mount Pleasant, SC
Posts: 1,091
Default Re: Extension cords in a 'permanent' application

Here's a little better picture...
Attached Thumbnails
extension-cords-permanent-application-13-nov-07-079.jpg  



- Mike

Michael W. Gault, SC RBI 1728
A to Z Home Inspections
Charleston, Dorchester & Berkeley Counties in S.C.
NACHI05040682
www.atozinspector.com

(843) 442-9755
Charleston Home Inspector
Reply With Quote
  #3  
Old 11/13/07, 6:52 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Extension cords in a 'permanent' application

Temporary cords used as permanent wiring.
Reply With Quote
  #4  
Old 11/13/07, 6:56 PM
bzimbelman bzimbelman is offline
InterNACHI Member
 
Join Date: Mar 2007
Location: Silver City, NM
Posts: 353
Default Re: Extension cords in a 'permanent' application

Mike -

From the photo what I'm seeing is a case where the outlet has been placed next to the opener, but the opener's cord doesn't reach because the ceiling is too farther from the opener then the cord is long. Is that correct?

I routinely call out extension cords for ceiling fans and garage door openers where the extension cord runs all the way to a wall, then down the wall and into an outlet, as that is improper wiring and unsafe. But in this case, I don't see a problem, as from what I can see there is no way to supply power to the garage door opener which is better then what they chose, and it's not an unsafe or improper use of an extension cord since the cord isn't hanging in a way in which it is likely to be caught or damaged. I am making the assumption that the garage door opener is fairly high, out of reach to normal individuals of course.

Hope that helps!

-- bz
Reply With Quote
  #5  
Old 11/13/07, 7:21 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Extension cords in a 'permanent' application

Extension cords are specifically listed for temporary use only. The tag, next to the plug, says it all - not allowed.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #6  
Old 11/13/07, 7:26 PM
bzimbelman bzimbelman is offline
InterNACHI Member
 
Join Date: Mar 2007
Location: Silver City, NM
Posts: 353
Default Re: Extension cords in a 'permanent' application

Quote:
Originally Posted by jpope
Extension cords are specifically listed for temporary use only. The tag, next to the plug, says it all - not allowed.
Ok, so what would be the solution without an extension cord in this case?
Reply With Quote
  #7  
Old 11/13/07, 7:28 PM
Michael W. Gault's Avatar
Michael W. Gault Michael W. Gault is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Mount Pleasant, SC
Posts: 1,091
Default Re: Extension cords in a 'permanent' application

Agree with Jeff, but kinda agree with Brain too... I'm torn.

The height of the ceiling (slab plan built on a crawlspace with 'racquetball court' garage ceilings) allows only one way to wire it from the opener - Cut and install a new 'pig tail' for the opener...

And they have tried very hard to use a heavy duty (same gauge as the cord or better) extension cord as well as having tried to protect it from any physical damage...

Any other thoughts??

Thanks for the ones listed...



- Mike

Michael W. Gault, SC RBI 1728
A to Z Home Inspections
Charleston, Dorchester & Berkeley Counties in S.C.
NACHI05040682
www.atozinspector.com

(843) 442-9755
Charleston Home Inspector
Reply With Quote
  #8  
Old 11/13/07, 7:42 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: Extension cords in a 'permanent' application

Could probably drop a receptacle to it from above properly.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #9  
Old 11/13/07, 7:45 PM
Michael W. Gault's Avatar
Michael W. Gault Michael W. Gault is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Mount Pleasant, SC
Posts: 1,091
Default Re: Extension cords in a 'permanent' application

Quote:
Originally Posted by lkage
Could probably drop a receptacle to it from above properly.
Larry,
Can you elaborate on this?



- Mike

Michael W. Gault, SC RBI 1728
A to Z Home Inspections
Charleston, Dorchester & Berkeley Counties in S.C.
NACHI05040682
www.atozinspector.com

(843) 442-9755
Charleston Home Inspector
Reply With Quote
  #10  
Old 11/13/07, 7:51 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Extension cords in a 'permanent' application

Quote:
Originally Posted by bzimbelman
Ok, so what would be the solution without an extension cord in this case?
A longer cord-and-plug assembly would be a reasonable solution.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #11  
Old 11/13/07, 7:56 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Extension cords in a 'permanent' application

Quote:
Originally Posted by jpope
A longer cord-and-plug assembly would be a reasonable solution.
And so would a properly installed and supported pendant.
Reply With Quote
  #12  
Old 11/13/07, 7:57 PM
bzimbelman bzimbelman is offline
InterNACHI Member
 
Join Date: Mar 2007
Location: Silver City, NM
Posts: 353
Default Re: Extension cords in a 'permanent' application

Quote:
Originally Posted by jpope
A longer cord-and-plug assembly would be a reasonable solution.
Both this and Larry's solutions do make a slight improvement over the existing installation. I'm still not totally convinced I'd make a big deal out of it though. From what I see here regularly, this is far better then most. I'd probably tell the client it's not an issue, then write it up.
Reply With Quote
  #13  
Old 11/13/07, 7:58 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Extension cords in a 'permanent' application

Yep. A cord-pendant would work as well. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #14  
Old 11/13/07, 8:00 PM
Michael W. Gault's Avatar
Michael W. Gault Michael W. Gault is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Mount Pleasant, SC
Posts: 1,091
Default Re: Extension cords in a 'permanent' application

I'll offer both solutions as potentail 'fixes' to the 'problem'...

Thanks guys...



- Mike

Michael W. Gault, SC RBI 1728
A to Z Home Inspections
Charleston, Dorchester & Berkeley Counties in S.C.
NACHI05040682
www.atozinspector.com

(843) 442-9755
Charleston Home Inspector
Reply With Quote
  #15  
Old 11/13/07, 8:00 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: Extension cords in a 'permanent' application

Quote:
Originally Posted by mgault
Larry,
Can you elaborate on this?
http://www.woodcentral.com/bparticle...cepticle.shtml



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Help. What is the correct way to report a breaker that is too big. gromicko Electrical Inspections 77 5/10/12 6:13 PM
Steel post question sspradling Structural Inspections 42 3/2/07 8:59 PM
Extension Cords in Crawl Spaces Skip Erwin Electrical Inspections 10 6/25/06 3:39 PM
Joe F, update? jtedesco1 Electrical Inspections 54 4/10/06 10:35 AM


All times are GMT -4. The time now is 9:08 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts