Default Exterior meter

Just finished an inspection and need opinions. There is an exterior 60 amp panel next to the meter housing at the back of the home. It feeds the garage panel and is directly wired from the meter through the connecting conduit. Come to find out an electrition lived there at one point. Doesn't look right to me. Let me know. Stan
Reply With Quote
Need a home inspection in Louisiana? Check out InterNACHI's listing of Louisiana certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 7/22/11, 3:01 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Exterior meter

A picture would help. A 60 amp panel feeding a garage panel is perfectly acceptable.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 7/22/11, 3:07 PM
Stan Croenne Stan Croenne is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Springfield, IL
Posts: 60
Default Re: Exterior meter

The 60 amp panel is connected to the meter housing by conduit and the wires are fed to the 60 amp panel from the exterior meter, not from the interior main panel. Looks fishy to me. Stan
Reply With Quote
  #4  
Old 7/22/11, 3:08 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Exterior meter

Quote:
Originally Posted by scroenne View Post
Just finished an inspection and need opinions. There is an exterior 60 amp panel next to the meter housing at the back of the home. It feeds the garage panel and is directly wired from the meter through the connecting conduit. Come to find out an electrition lived there at one point. Doesn't look right to me. Let me know. Stan
Which part does not look right ?
Was there a separate meter for the home?

They may have been leasing out the garage.
Reply With Quote
  #5  
Old 7/22/11, 3:15 PM
Stan Croenne Stan Croenne is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Springfield, IL
Posts: 60
Default Re: Exterior meter

No, one meter for the home and garage. The 60 amp panel is fine that feeds the garage. My question is should the 60 amp panel be wired at the exterior directly from the exterior meter housing? Someone had to open the exterior meter housing to access the connections. Stan
Reply With Quote
  #6  
Old 7/22/11, 3:18 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Exterior meter

Quote:
Originally Posted by scroenne View Post
No, one meter for the home and garage. The 60 amp panel is fine that feeds the garage. My question is should the 60 amp panel be wired at the exterior directly from the exterior meter housing? Someone had to open the exterior meter housing to access the connections. Stan
OK ,so you figure they should have created a subpanel and instead they footballed or did they double tap?

60m amps is not enough for a home anymore.
I think some of these lenders are asking for 100 now.
Reply With Quote
  #7  
Old 7/22/11, 3:21 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Exterior meter

When you say "main panel," I assume you're referring to the service equipment.

If the 60 amp panel is not supplied from (or part of) the service equipment, it is improper.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #8  
Old 7/22/11, 3:31 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Exterior meter

Quote:
Originally Posted by belliott View Post
OK ,so you figure they should have created a subpanel and instead they footballed or did they double tap?

60m amps is not enough for a home anymore.
I think some of these lenders are asking for 100 now.
I don't think that's what he described. I picture double-tap at meter socket feeding 60 amp box and also interior panel.


A photo would sure help.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #9  
Old 7/22/11, 4:24 PM
Stan Croenne Stan Croenne is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Springfield, IL
Posts: 60
Default Re: Exterior meter

Not sure. Looks like it is a double tap off of the meter lugs. I can't tell, I can't see inside the meter box. One of the past owners was an electrition and I have a feeling he did it on his own. I have never seen it, so I thought I would see what you guys had to say. Stan
Reply With Quote
  #10  
Old 7/22/11, 4:29 PM
Stan Croenne Stan Croenne is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Springfield, IL
Posts: 60
Default Re: Exterior meter

150 amp main service panel at interior basement. Exterior 60 amp panel fed directly from exterior meter not from 150 amp panel in basement. Third panel in garage fed from 60 amp panel by meter. Sorry for the confusion. Stan
Reply With Quote
  #11  
Old 7/22/11, 8:02 PM
James E. Braun, CMI's Avatar
James E. Braun, CMI James E. Braun, CMI is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Jefferson City, MO
Posts: 6,945
Default Re: Exterior meter

I know they make meter bases with 2, 4 or 6 supply lugs, but I think they are on 325 amp bases and up. Could somebody stuck a 325 amp base on the house?



Braun Inspection Consultants
Serving Jefferson City, Columbia, Sedalia, Fulton and Lake of the Ozarks
Reply With Quote
  #12  
Old 7/22/11, 9:35 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Exterior meter

Quote:
Originally Posted by jbraun View Post
Could somebody stuck a 325 amp base on the house?
Possibly, but the point of connection is irrelevant. The 60A panel must be supplied from the service equipment, or it must be part of the service equipment.

There are cases where multiple panels can be used as the service equipment, but they must be grouped and bonded. They cannot be located in various locations throughout the residence.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #13  
Old 7/23/11, 7:48 AM
James E. Braun, CMI's Avatar
James E. Braun, CMI James E. Braun, CMI is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Jefferson City, MO
Posts: 6,945
Default Re: Exterior meter

In my area, you are allowed to run two separate service panels and they can be one inside for the house and one outside for the outer buildings. It is pretty common here.



Braun Inspection Consultants
Serving Jefferson City, Columbia, Sedalia, Fulton and Lake of the Ozarks
Reply With Quote
Need a home inspection in Louisiana? Check out InterNACHI's listing of Louisiana certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 7/23/11, 8:39 AM
Stan Croenne Stan Croenne is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Springfield, IL
Posts: 60
Default Re: Exterior meter

Thanks for the help guys, this is why I belong to this organization. Endless knowledge at the press of a button. Stan
Reply With Quote
  #15  
Old 7/23/11, 11:18 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Exterior meter

Quote:
Originally Posted by jbraun View Post
In my area, you are allowed to run two separate service panels and they can be one inside for the house and one outside for the outer buildings. It is pretty common here.
Is that because your area follows no model code, or do they have a code-section that allows for this?

There are exceptions that allow for additional "service disconnects," but those generally apply to emergency systems, fire pumps, required "stand-by" systems, etc.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net



Last edited by jpope; 7/23/11 at 11:21 AM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 9:08 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts