Default Exterior outlets in soffit

New home inspected today, found (4) exterior outlets in the soffits (for heat tape, holiday decorations, etc.) that are not GFCI. Shouldn't all exterior outlets be GFCI? Or are there some exceptions?
Gerald Wilcox
Reply With Quote
  #2  
Old 8/28/07, 8:02 AM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Exterior outlets in soffit

Quote:
Originally Posted by gwilcox
New home inspected today, found (4) exterior outlets in the soffits (for heat tape, holiday decorations, etc.) that are not GFCI. Shouldn't all exterior outlets be GFCI? Or are there some exceptions?
Gerald Wilcox
Hi Gerald,

yes there are some exceptions and I believe that what you have seen is one of them, the best rule of thumb without getting into the code, is that if the receptacles are above a normaly reachable height (not generaly accessable) they do not have to be GFCI potected.

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #3  
Old 8/28/07, 8:31 AM
Greg Bell's Avatar
Greg Bell Greg Bell is offline
InterNACHI Member
 
Join Date: Oct 2002
Location: Titusville, FL
Posts: 4,155
Default Re: Exterior outlets in soffit

Hi Gerald,

2006 IRC
E3802.3 Outdoor receptacles. All 125-volt, single-phase, 15 and 20-Ampere receptacles installed outdoors shall have ground-fault circuit-interrupter protection for personnel.

Exception: Receptacles as covered in Section E4001.7

E4001.7 Snow-melting and deicing equipment protection.
Outdoor receptacles that are not readily accessible and are supplied from a dedicated branch circuit for electric snow-melting or deicing equipment shall be permitted to be installed without ground-fault protection for personnel. However, ground-fault protection of equipment shall be provided for fixed outdoor electric deicing and snow-melting equipment.



Greg Bell
Titusville, Fl
02111507

Serving Central Florida
Reply With Quote
  #4  
Old 8/28/07, 8:50 AM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Exterior outlets in soffit

Hi Greg,

thanks for the clarification, I was not awake enough to look it up. I had not realised that the current code required fixed heating strips to be GFCI, I thought all dedicated non accessible outlets could be unprotected.

Interestingly I think that the code has it backasswards, as the receptacle used for temporary/seasonal use could be used to plug in an extention lead and power any other appliance, including those that should be GFCI protected whilst being used outside.

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #5  
Old 8/28/07, 9:43 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Exterior outlets in soffit

If it's outside (period-no exceptions) or within 6 feet of water, it's automatically a recommendation to install GFCI's.
Reply With Quote
  #6  
Old 8/28/07, 9:49 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Exterior outlets in soffit

Yeah...basically you have Class A and Class B GFI's ....

The Class A device is your standard GFCI which has a GFCI trip rating of 4-6MA while a Class B device has a trip rating of 20 MA and higher for some manufacturers.

The Class B is for equipment protection afforded your situation by Article 426, Section 426.28 Equipment Protection for fixed outdoor electric deicing and snow melting equipment.



Paul W. Abernathy
Reply With Quote
  #7  
Old 8/28/07, 11:49 AM
Jason A. Sieg, CMI's Avatar
Jason A. Sieg, CMI Jason A. Sieg, CMI is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Davison, MI
Posts: 839
Default Re: Exterior outlets in soffit

I personally, for my mother like to put all exterior receptacles on a switch & GFCI protect them for her.

I have found kids plugging cords into her home instead of their own home.

Also the switch makes it easy for her to control Holiday lighting etc.



Jason Sieg, CMI
Davison, MI
NACHI05091399


Knowing the current condition,
to make a wise decision.

President, Great Lakes-East Chapter
Join NACHI Great Lakes - East Chapter

http://mi.nachi.org/greatlakes-east/about.html
ssieg@gfn.org
Reply With Quote
  #8  
Old 8/28/07, 12:57 PM
dchew dchew is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: San Ramon, CA
Posts: 317
Default Re: Exterior outlets in soffit

I live in sunny California, so we don't have much need for snow melting outlets except for the Lake Tahoe area. Do you guys in the snow country call out for "in-use" covers for outside outlets like the one mentioned in this thread? Just curious.
Reply With Quote
  #9  
Old 8/28/07, 1:24 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Exterior outlets in soffit

Quote:
Originally Posted by dchew
I live in sunny California, so we don't have much need for snow melting outlets except for the Lake Tahoe area. Do you guys in the snow country call out for "in-use" covers for outside outlets like the one mentioned in this thread? Just curious.
I recommend weather tight covers on all exterior GFCI's, but not so much in the upper eave areas.

Reply With Quote
  #10  
Old 8/28/07, 1:40 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Exterior outlets in soffit

Quote:
Originally Posted by dchew
I live in sunny California, so we don't have much need for snow melting outlets except for the Lake Tahoe area. Do you guys in the snow country call out for "in-use" covers for outside outlets like the one mentioned in this thread? Just curious.
no, not if it is under the eaves and installed IN the soffit ....that would be a damp location and would not require an inuse cover.



Paul W. Abernathy
Reply With Quote
  #11  
Old 8/28/07, 2:19 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Exterior outlets in soffit

This is one place where I dissagree with NFPA. I think the snap covers are better for seldom used outside receptacles that will almost never be used unattended. They do a whole lot better job of keeping out the weather when closed and they are not natural wasp condos. Certainly the in use cover is a great idea for places where you leave something plugged in. That was the original intent but it got perverted.
Reply With Quote
  #12  
Old 8/28/07, 2:42 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Exterior outlets in soffit

lol.....got perverted did it...lol....yeah I agree it should be more like the requirement for wet locations indoors that are used for service rendering only but then again...who are we Greg...



Paul W. Abernathy
Reply With Quote
  #13  
Old 8/28/07, 5:38 PM
bdoles2's Avatar
bdoles2 bdoles2 is offline
Active Poster
 
Join Date: Aug 2006
Location: Atlanta, GA
Posts: 3,071
Please Note: bdoles2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Exterior outlets in soffit

Quote:
Originally Posted by jsieg
I personally, for my mother like to put all exterior receptacles on a switch & GFCI protect them for her.

I have found kids plugging cords into her home instead of their own home.

Also the switch makes it easy for her to control Holiday lighting etc.
I hear that!! That's very good advice depending on where you live. I caught my neighbor last winter stealing my power (because he couldn't pay his bill, and thought it would be ok ). He can buy a BMW, but can't afford the power for his own home.
Reply With Quote
  #14  
Old 8/30/07, 8:33 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Exterior outlets in soffit

In Baltimore City any exterior receptacle within 10 foot of the sidewalk is required to be switch controlled to prevent people borrowing your power.
Reply With Quote
  #15  
Old 9/2/07, 10:17 PM
gporter's Avatar
gporter gporter is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Orlando, fl
Posts: 3,281
Default Re: Exterior outlets in soffit

If you are worried a would put the metal faceplate with the loop for locking with padlock.



Gary Porter

GLP's Home and Mold Inspections
321-239-0621

Certified Commercial Mold Inspector

Serving Orlando, Kissimmee, Winter Park, Winter Springs, Oviedo, Titusville, Celebration, Harmony, Avalon, Windermere, Deltona, Debary, Sanford
Orange County, Seminole County, Volusia County, Osceola County

www.homeandmoldinspections.com
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Eaves, Soffit, Fascia Mike Jewett Exterior Inspections 1 9/6/07 3:14 PM
minus soffit vents lcannizzaro Exterior Inspections 10 5/15/07 3:15 PM
Siding and soffit staining pominspections Exterior Inspections 8 2/21/07 5:22 PM
Gap in Soffit carolinainspector Exterior Inspections 6 6/23/06 8:56 AM
Soffit vents too small. Jay Moge Structural Inspections 2 4/2/06 12:28 AM


All times are GMT -4. The time now is 9:08 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts