Question Exterior Service Disconnect Clearances?

I know the correct clearance for an interior panel is 30” on each side and 36” in front, but is the same clearances required for an exterior main disconnect. As you can see by the picture the main disconnect is under the meter base and is partially behind the ac unit. I could not open the cover to the main disconnect and access the breaker normally, as the cover had the screws missing at the top where it hinged, so the cover would fall straight down instead of flipping up like normal. I guess they did this so there would be access to the breaker. If the AC unit was to be moved about three inches to the right, the cover could open normally. Are any other clearances required? This is a brand new home.
Attached Thumbnails
exterior-service-disconnect-clearances-youngwon-her-inspection-030.jpg  



Robert Cramer
Five Star Property Inspections
Your Best & Safest Choice
www.fivestarpi.com
1-877-378-2774
Reply With Quote
  #2  
Old 7/18/07, 9:10 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Exterior Service Disconnect Clearances?

Quote:
Originally Posted by rcramer
I know the correct clearance for an interior panel is 30” on each side and 36” in front, but is the same clearances required for an exterior main disconnect. As you can see by the picture the main disconnect is under the meter base and is partially behind the ac unit. I could not open the cover to the main disconnect and access the breaker normally, as the cover had the screws missing at the top where it hinged, so the cover would fall straight down instead of flipping up like normal. I guess they did this so there would be access to the breaker. If the AC unit was to be moved about three inches to the right, the cover could open normally. Are any other clearances required? This is a brand new home.
If the acess cover is unable to be accessed, I would simply recommend moving the condenser for adequate access to electrical SE panel. There must be 36 inches of unobstructed space in front of the meter and there must be at least 2 inches of space on both sides of the meter.

Last edited by dvalley; 7/18/07 at 9:17 AM..
Reply With Quote
  #3  
Old 7/18/07, 9:16 AM
rcramer's Avatar
rcramer rcramer is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Belleville, IL
Posts: 128
Default Re: Exterior Service Disconnect Clearances?

Hey David,

Yes that would be the simple choice, but the condenser can not be moved due to the basement windows. ( See Pic.) my question is are there and required clearances other than being able to open the cover normally.
Attached Thumbnails
exterior-service-disconnect-clearances-youngwon-her-inspection-026.jpg  



Robert Cramer
Five Star Property Inspections
Your Best & Safest Choice
www.fivestarpi.com
1-877-378-2774
Reply With Quote
  #4  
Old 7/18/07, 9:20 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Exterior Service Disconnect Clearances?

Quote:
Originally Posted by rcramer
Hey David,

Yes that would be the simple choice, but the condenser can not be moved due to the basement windows. ( See Pic.) my question is are there and required clearances other than being able to open the cover normally.
As I stated, 36" in front and 2" to the sides is required at a meter.
Reply With Quote
  #5  
Old 7/18/07, 9:30 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Exterior Service Disconnect Clearances?

I've never seen bracketry attached to a building in order to support condensers.

Is that a norm in your area?

We use simple pads under our condensers.
Reply With Quote
  #6  
Old 7/18/07, 9:31 AM
rcramer's Avatar
rcramer rcramer is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Belleville, IL
Posts: 128
Default Re: Exterior Service Disconnect Clearances?

Thanks David



Robert Cramer
Five Star Property Inspections
Your Best & Safest Choice
www.fivestarpi.com
1-877-378-2774
Reply With Quote
  #7  
Old 7/18/07, 9:33 AM
rcramer's Avatar
rcramer rcramer is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Belleville, IL
Posts: 128
Default Re: Exterior Service Disconnect Clearances?

Yep, brackets have become the norm, we use pads too, but in new construction brackets have become very popular.



Robert Cramer
Five Star Property Inspections
Your Best & Safest Choice
www.fivestarpi.com
1-877-378-2774
Reply With Quote
  #8  
Old 7/18/07, 9:34 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Exterior Service Disconnect Clearances?

Quote:
Originally Posted by rcramer
Yep, brackets have become the norm, we use pads too, but in new construction brackets have become very popular.
Can you tell me why?
Reply With Quote
  #9  
Old 7/18/07, 9:39 AM
rcramer's Avatar
rcramer rcramer is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Belleville, IL
Posts: 128
Default Re: Exterior Service Disconnect Clearances?

1. Security, in our area there have been a rash of thefts of new units. When mounted on the brackets the units can easily be thru bolted and deturs thefts.

2. Helps keep the unit from being damaged due to lawn mowing debris.

3. Better air circulation.



Robert Cramer
Five Star Property Inspections
Your Best & Safest Choice
www.fivestarpi.com
1-877-378-2774
Reply With Quote
  #10  
Old 7/18/07, 9:59 AM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Exterior Service Disconnect Clearances?

110.26 of the NEC gives the clearances for electrical equipment.

Table 110.26(A)(1) gives the depth. In this table for voltages of 150 to ground we must have 36 inches of depth.

110.26(A) (2) Width of Working Space. The width of the working space in front of the electric equipment shall be the width of the equipment or 750 mm (30 in.), whichever is greater. In all cases, the work space shall permit at least a 90 degree opening of equipment doors or hinged panels.

These 30 inches can start on the edge of one side of the panel and move toward the other side or from the center of the panel 15 inches in either direction as long as there is 30 inches total.

In my area the gas meter can be no closer than 36 inches of the electrical panel. This is not an electrical rule but a gas company rule.

Good call
Reply With Quote
  #11  
Old 7/18/07, 10:34 AM
rcramer's Avatar
rcramer rcramer is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Belleville, IL
Posts: 128
Default Re: Exterior Service Disconnect Clearances?

Thanks Mike, good info.....



Robert Cramer
Five Star Property Inspections
Your Best & Safest Choice
www.fivestarpi.com
1-877-378-2774
Reply With Quote
  #12  
Old 7/18/07, 11:16 AM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Exterior Service Disconnect Clearances?

Quote:
Originally Posted by dvalley
I've never seen bracketry attached to a building in order to support condensers.

Is that a norm in your area?

We use simple pads under our condensers.
Hi Dave, we see them alot down here on new construction, it keeps them above the snow line

But seriously, they run more efficiently off the ground, don't rust as fast as they drain better, plus down here we need to install with hurricane strapping which is easier to do on a purpose built mount.

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #13  
Old 7/18/07, 11:25 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Exterior Service Disconnect Clearances?

Quote:
Originally Posted by gbeaumont
Hi Dave, we see them alot down here on new construction, it keeps them above the snow line


Regards

Gerry
I forgot...You do get some serious blizzards in Florida.

Reply With Quote
  #14  
Old 7/18/07, 11:46 PM
cduphily's Avatar
cduphily cduphily is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Dingmans Ferry, PA
Posts: 2,486
Please Note: cduphily is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Exterior Service Disconnect Clearances?

Quote:
Originally Posted by dvalley
Can you tell me why?
Take a walk down some of the back alleys in the financial district/China Town/Bay Village in Boston... during the day of course.

I know , I know your reference to brackets was for residential use .... but I couldn't resist commenting.
Reply With Quote
  #15  
Old 7/19/07, 8:27 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Exterior Service Disconnect Clearances?

Quote:
Originally Posted by cduphily
Take a walk down some of the back alleys in the financial district/China Town/Bay Village in Boston... during the day of course.

I know , I know your reference to brackets was for residential use .... but I couldn't resist commenting.
Yeah, I've been there many times and I know exactly what you're referring to.


I really like those rugged metal shelves and I'd like to see them come to my area. I'm just surprised that they're not here today.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Well pump disconnect sfalvey Plumbing Inspections 0 11/17/06 1:23 AM
A/C Disconnect question rslocum Inspecting HVAC Systems 15 9/21/06 1:16 AM
100 Amp Meter, 200 Amp Disconnect jweinberg Electrical Inspections 8 8/15/06 1:32 PM
HVAC Disconnect kgore Inspecting HVAC Systems 11 7/11/06 7:58 PM
Disconnect and Main panel srowe Electrical Inspections 10 6/13/06 8:49 PM