Default Re: Exterior Shower light

Quote:
Originally Posted by jhagarty View Post
Are exterior fixtures required to be caulked in Florida?
Who cares,it would be dumb not to.Anyone here a code inspector ?

Best practice certainly could not be to allow water intrusion in to the substrate.
Reply With Quote
Need a home inspection in Kansas? Check out InterNACHI's listing of Kansas certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #17  
Old 5/24/11, 6:02 AM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,932
Default Re: Exterior Shower light

Quote:
Originally Posted by jhagarty View Post
Are exterior fixtures required to be caulked in Florida?
nationally: all penetrations must be sealed with a compatible sealant as recommended by the stucco system manufacturer and required by model codes

strongly advised at all wet location penetrations through other bldg. materials also, but you knew this



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good
Reply With Quote
  #18  
Old 5/24/11, 7:09 AM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,636
Default Re: Exterior Shower light

So an Inspector in Illinois and Texas "Knows" that "Florida requires caulking of light fixtures" ....

Wondering what Florida Inspectors know about Florida requirements...



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #19  
Old 5/24/11, 8:17 AM
Blaine Wiley Blaine Wiley is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Rotonda West, FL
Posts: 3,186
Send a message via MSN to bwiley
Default Re: Exterior Shower light

AHJ passes them all of the time here without caulk, even on the brand new home yesterday that just got a CO. Since this is almost always stucco over cement block (never seen EIFS here) it isn't an issue for the wall.

That looks like a standard exterior fixture that would be mounted on just about any home anywhere in this area. I would not write it up as anything of concern. I probably see that type of installation on 8 out of 10 houses here.

The darn thing might even get some condensation on it if it's metal at various times of the year...



Don't interfere with anything in the Constitution. That must be maintained, for it is the only safeguard of our liberties.
Abraham Lincoln



www.qualityhomeinspectionsfl.com
Reply With Quote
  #20  
Old 5/24/11, 12:17 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Exterior Shower light

Quote:
Originally Posted by bwiley View Post
AHJ passes them all of the time here without caulk, even on the brand new home yesterday that just got a CO. Since this is almost always stucco over cement block (never seen EIFS here) it isn't an issue for the wall.

That looks like a standard exterior fixture that would be mounted on just about any home anywhere in this area. I would not write it up as anything of concern. I probably see that type of installation on 8 out of 10 houses here.

The darn thing might even get some condensation on it if it's metal at various times of the year...
So because the AHJ says nothing that makes it all good?.

For crying out loud we have porches collapse and kill people weeks after approval of the AHJ around here so if you inspect you would just leave it be and not write up anything the guy approved?

They have no liability but you do.
Reply With Quote
  #21  
Old 5/24/11, 6:52 PM
Blaine Wiley Blaine Wiley is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Rotonda West, FL
Posts: 3,186
Send a message via MSN to bwiley
Default Re: Exterior Shower light

Tell me what the issue is, Bob. I've never seen any water in any fixture installed in this manner. I've never seen corrosion on the wiring connections. I've never moved a metal fixture after a rain storm and seen any moisture at all.

None of the outdoor fixtures at either house today were caulked. I can't even think of the last time I saw an outdoor light fixture caulked to the masonry. I do see it on frame construction, and would expect to.



Don't interfere with anything in the Constitution. That must be maintained, for it is the only safeguard of our liberties.
Abraham Lincoln



www.qualityhomeinspectionsfl.com
Reply With Quote
  #22  
Old 5/24/11, 8:28 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Exterior Shower light

Quote:
Originally Posted by bwiley View Post
Tell me what the issue is, Bob. I've never seen any water in any fixture installed in this manner. I've never seen corrosion on the wiring connections. I've never moved a metal fixture after a rain storm and seen any moisture at all.

None of the outdoor fixtures at either house today were caulked. I can't even think of the last time I saw an outdoor light fixture caulked to the masonry. I do see it on frame construction, and would expect to.
The issue is that you need to keep out water intrusion to prevent brick and mortar damage along with associated spalling, efflorescence,not to mention insect entry.

http://www.chicagopropertyinspection...#1204833809332.

I suggest you make use of this info for the report.
Reply With Quote
  #23  
Old 5/25/11, 9:11 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Exterior Shower light

Quote:
Originally Posted by bwiley View Post
Tell me what the issue is, Bob. I've never seen any water in any fixture installed in this manner. I've never seen corrosion on the wiring connections. I've never moved a metal fixture after a rain storm and seen any moisture at all.

None of the outdoor fixtures at either house today were caulked. I can't even think of the last time I saw an outdoor light fixture caulked to the masonry. I do see it on frame construction, and would expect to.
So water doesn't enter electrical penetrations in masonry but does enter the same holes in wood based sidings???????
Reply With Quote
  #24  
Old 5/25/11, 9:17 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Exterior Shower light

Quote:
Originally Posted by jhagarty View Post
So an Inspector in Illinois and Texas "Knows" that "Florida requires caulking of light fixtures" ....

Wondering what Florida Inspectors know about Florida requirements...
I agree with Bob. The top of all exterior light fixtures should be sealed. It's an NEC requirement. (Please don't make me look it up.)



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #25  
Old 5/25/11, 9:18 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Exterior Shower light

Quote:
Originally Posted by lkage View Post
Did you look to see if the luminary is marked "suitable for wet locations"?
Could that light be installed in an interior shower? What's the difference?

Is the circuit even GFCI protected? What's to keep someone from resting their hand on it while they fondle, I mean wash, themselves?



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #26  
Old 5/25/11, 9:36 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: Exterior Shower light

Quote:
Originally Posted by jfunderburk View Post
Could that light be installed in an interior shower? What's the difference?

Is the circuit even GFCI protected? What's to keep someone from resting their hand on it while they fondle, I mean wash, themselves?

This is what I see...
Attached Thumbnails
exterior-shower-light-elec-bathtub-fixture-small-.jpg.jpg
Views:	25
Size:	36.5 KB
ID:	44963  



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #27  
Old 5/25/11, 9:45 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Exterior Shower light

I would call it out as being within the shower area. Would you trust your life to a luminary made by the chicoms?



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com



Last edited by jfunderburk; 5/25/11 at 10:17 AM..
Reply With Quote
  #28  
Old 5/25/11, 9:52 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,252
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Exterior Shower light

Quote:
Originally Posted by jfunderburk View Post
I would call it out as being in a restricted zone.

That type of fixture is likely permitted in the shower zone. There are a few factors here:
1-Forget the shower for a moment, is the location wet or damp?
2-Is it subject to shower spray?
3-Is it permitted in the shower zone?
4-Is GFCI protection required?

Answer:
1-If the location is wet then the fixture is required to be listed for wet locations. If it's location is covered by a roof then the location is damp.
2-IMO it is not subject to shower spray therefore if this is a damp location then only a damp location fixture is required.
3-Wall mounted fixtures are permitted in the shower zone if damp or wet listed. Wet location fixtures are required if subject to shower spray.
4-GFCI protection is not required for fixtures in the shower zone unless the fixture manufacturer requires it as part of the listing of the fixture.
Reply With Quote
Need a home inspection in Kansas? Check out InterNACHI's listing of Kansas certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #29  
Old 5/25/11, 9:54 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Exterior Shower light

Quote:
Originally Posted by jfunderburk View Post
I would call it out as being in a restricted zone.
You did see that wall mounted fixtures are ok in the graphic above?
Reply With Quote
  #30  
Old 5/25/11, 10:12 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Exterior Shower light

Quote:
Originally Posted by Jim Port View Post
You did see that wall mounted fixtures are ok in the graphic above?
Larry's illustration shows the light outside the immediate shower area. That's not my interpretation of the OP's exterior light. You wouldn't be wrong to disagree. It's a judgement call.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com



Last edited by jfunderburk; 5/25/11 at 10:18 AM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Flickering CFL jallingham Electrical Inspections 34 12/5/08 2:40 PM
Trouble Shooting the Simple Light Bulb mcyr Electrical Inspections 20 1/6/08 3:47 AM
End of the light bulb as we know it!! mcyr General Inspection Discussion 3 12/19/07 3:42 PM
Light Bulbs- All Ya Wanna Know pabernathy Electrical Inspections 9 4/18/07 7:22 PM
How many forum members to change a light bulb? kshepard Miscellaneous Discussion for Inspectors 9 8/2/06 9:56 AM


All times are GMT -4. The time now is 9:30 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts