InterNACHI


Go Back   InterNACHI Message Board > Specific Inspection Topics > Electrical

Notices

Electrical Contains discussions about electrical systems. This includes outlets, panels, wiring, et cetera.

Reply
 
LinkBack Thread Tools
  #1  
Old 4/7/06, 8:46 PM
Steven Brewster Steven Brewster is offline
New User
 
Join Date: Aug 2005
Location: Southside, AL
Posts: 57
Please Note: Steven Brewster is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default False Ground

Inspected this 1960's home today and thought that the home had been rewired with grounded circuits. The 3-prong receptacles tested OK (grounded) with my 3 lite tester. When I opened the distribution panel, I did not see any grounding conductors, all 2 wire. Removed a receptacle and here is what I found. My question is would a sure-test indicate this false ground? What would this set up do to a appliance with a ground (3-prong plug) if current traveled back and energized the appliance. Looks to me like a real safety hazard. What do you guy/gals think?
Attached Thumbnails
false-ground-hpim3050-small-.jpg.JPG
Views:	137
Size:	50.7 KB
ID:	2716  
Reply With Quote
  #2  
Old 4/7/06, 8:49 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,038
Default Re: False Ground

Yes, a SureTest would have indicated this condition.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #3  
Old 4/7/06, 8:54 PM
Gerry Beaumont's Avatar
Gerry Beaumont Gerry Beaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 5,749
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: False Ground

Quote:
Originally Posted by Steven Brewster
Inspected this 1960's home today and thought that the home had been rewired with grounded circuits. The 3-prong receptacles tested OK (grounded) with my 3 lite tester. When I opened the distribution panel, I did not see any grounding conductors, all 2 wire. Removed a receptacle and here is what I found. My question is would a sure-test indicate this false ground? What would this set up do to a appliance with a ground (3-prong plug) if current traveled back and energized the appliance. Looks to me like a real safety hazard. What do you guy/gals think?
Hi Steve,

Yes my Suretest 61-165 will show false/bootleg grounds but I believe that the cheaper ones do not, it would be worth researching the ideal website to check.

Any appliance that has a three prong plug is designed to work with a gronded conductor. Some electronic components especially computer equipment does not work well on 2 wire circuits. and yes there are angers associated with connecting the Neutral to the ground at any location other than the service panel.

Regards

Gerry



Virtue is more to be feared than vice, because its excesses are not subject to the regulation of conscience.
Adam Smith (1723-1790)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106
Reply With Quote
  #4  
Old 4/7/06, 8:59 PM
Steven Brewster Steven Brewster is offline
New User
 
Join Date: Aug 2005
Location: Southside, AL
Posts: 57
Please Note: Steven Brewster is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: False Ground

This find today has convinced me to invest in a Sure-test. Thanks for your help.
Reply With Quote
  #5  
Old 4/7/06, 9:05 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,038
Default Re: False Ground

Quote:
Originally Posted by gbeaumont
Any appliance that has a three prong plug is designed to work with a gronded conductor.
Gerry meant to say groundING conductor. . . Oh, and I'm sure he meant Danger rather than anger. .

Startin' Friday a little early eh Gerry



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #6  
Old 4/7/06, 9:19 PM
Gerry Beaumont's Avatar
Gerry Beaumont Gerry Beaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 5,749
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: False Ground

Quote:
Originally Posted by jpope
Gerry meant to say groundING conductor. . . Oh, and I'm sure he meant Danger rather than anger. .

Startin' Friday a little early eh Gerry
Yeah what Jeff says

I have been writing a class all week and I'm getting punchy now I am going for a brew

Regards

Gerry



Virtue is more to be feared than vice, because its excesses are not subject to the regulation of conscience.
Adam Smith (1723-1790)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106
Reply With Quote
  #7  
Old 4/7/06, 9:45 PM
Richard L. Bennett Richard L. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Frostproof, Fl
Posts: 2,323
Default Re: False Ground

An off the shelf VOM will show the boot leg ground

Cost about $25.00 from radio shack

If you have the $$ spend it on the big boys

rlb
Reply With Quote
  #8  
Old 4/7/06, 9:46 PM
Jae Williams's Avatar
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 3,859
Default Re: False Ground

Gerry -- Warm pint, no doubt.



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
  #9  
Old 4/7/06, 10:14 PM
Gerry Beaumont's Avatar
Gerry Beaumont Gerry Beaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 5,749
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: False Ground

Quote:
Originally Posted by jwilliams4
Gerry -- Warm pint, no doubt.
Jae, no, in fact they kicked me out of England because I don't like warm ale, and I am sure as hell not drinking the tea

I spent way too long in Belgium, Holland and Germany sinking tall frosty lagers

I'm just going to raid the fridge and see if I have any Stella left

Regards

Gerry



Virtue is more to be feared than vice, because its excesses are not subject to the regulation of conscience.
Adam Smith (1723-1790)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106
Reply With Quote
  #10  
Old 4/7/06, 11:26 PM
Richard L. Bennett Richard L. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Frostproof, Fl
Posts: 2,323
Default Re: False Ground

Please people

Do we all have to spend $$ to find this problem or can we find it cheap and dirty way with out doing a lot of work liking taking the plug apart?

rlb
Reply With Quote
  #11  
Old 4/7/06, 11:29 PM
Jay Moge's Avatar
Jay Moge Jay Moge is offline
Active Poster
 
Join Date: Aug 2005
Location: Derry New Hampshire
Posts: 761
Please Note: Jay Moge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: False Ground

Quote:
Originally Posted by rbennett
Please people

Do we all have to spend $$ to find this problem or can we find it cheap and dirty way with out doing a lot of work liking taking the plug apart?

rlb
i don't think i'm going to pull duplex outlets out of the wall. if you get a ground reading on you little tester, and theres not ground wire in the panel..... guess what?
Reply With Quote
  #12  
Old 4/7/06, 11:34 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,038
Default Re: False Ground

Quote:
Originally Posted by rbennett
Do we all have to spend $$ to find this problem
I would say yes. But that's just me



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #13  
Old 4/7/06, 11:35 PM
Richard L. Bennett Richard L. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Frostproof, Fl
Posts: 2,323
Default Re: False Ground

Jay

What if one could show you how to check for this problem is about 5 seconds??

Will someone else - Jeff Poe etc come in with the answer to the problem?????


The ac voltage differenct between the ground and the neutral - Hi Z ???

rlb
Reply With Quote
  #14  
Old 4/7/06, 11:37 PM
tneumann's Avatar
tneumann tneumann is offline
Active Poster
 
Join Date: Jan 2006
Location: Woodland Park, co
Posts: 2,074
Please Note: tneumann is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: False Ground

Edgar Allan Pope will be along shortly...

I want a sure test just cuz it's cool....sorta the same reason Jeff is Mr. Wireless now...

I don't think I'll be taking receptacles apart any time soon.....the lack of ground in the panel would have been a red flag eh?
Reply With Quote
  #15  
Old 4/7/06, 11:39 PM
Richard L. Bennett Richard L. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Frostproof, Fl
Posts: 2,323
Default Re: False Ground

Tony

I feel the answer is comming --- stand by

rlb
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical 6 9/15/08 8:57 AM
False Ground / Bootleg Ground mmorris Electrical 12 5/17/07 1:11 PM
Grounding Myths Quiz pabernathy Electrical 33 1/26/07 7:59 PM
Harmonized Ground Fault Circuit Interrupters jtedesco1 Electrical 5 3/21/06 9:48 AM


All times are GMT -4. The time now is 10:44 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts