Default Re: False Ground

Quote:
Originally Posted by brian winkle
The suretest uses a resistance measurement to reveal a bootleg ground, won't it lie on a receptacle located very close to the panel?
As with any instrument, learning to interpret the readings is an important factor. The SureTest will give a "false ground" indication" when the resistance between the grounded conductor and the grounding conductor is too low. This may occur at close proximity to the service equipment or where a bootleg ground is present.

Is it lying? No, it's simply giving a reading. It's up to the HI to try and determine if the reading is actually a problem. If it is questionable, it should be deferred.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #32  
Old 4/10/06, 10:37 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: False Ground

Great stuff by Jeff....Lets BUMP this puppy



Paul W. Abernathy
Reply With Quote
  #33  
Old 4/10/06, 11:31 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: False Ground

I guess I would have to disagree with you there Jeff, if the instrument displays a false ground reading in close proximity to the panel when there is no false ground present, I would call that lying

What about the HI who reports it as a false ground and causes additional expense of an electrician when one was not needed?
Reply With Quote
  #34  
Old 4/11/06, 12:00 AM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,785
Default Re: False Ground

How about the HI that does not call it out and does not have a licensed and insured electrician evaluate it (and assume the liability) and gets wacked?

HIs are like general practicioners. Electricians are specialists.




Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #35  
Old 4/11/06, 7:21 AM
Richard L. Bennett Richard L. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Frostproof, Fl
Posts: 2,304
Default Re: False Ground

Remember we are only dealing with three conductors here


A lot different than checking computer network cabling that is wired by the same "professional"

PULL THE COVER OFF AND LOOK AT IT

You pulled the cover off the electrical panel didn't you?? What is a little piece of plastic and one screw?




rlb
Reply With Quote
  #36  
Old 4/11/06, 9:02 AM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,206
Default Re: False Ground

Consider a case where some of the receptacles are switched from a 3 or 4 gang wall switch box with more than one hot feed to the box. You have 3-wire plus ground cables present, different neutral circuits etc.

It is not just simply 3 wires sometimes, if you do not remove the outlet and look at the splices that may be behind it you could miss a lot.

If you are going to remove cover plates you should remember that you are still only seeing a small portion of the picture. House can have many junction boxes and splices.

Another note:
Installing an AFCI on a circuit that operates and tests ok can be a learning experience when it trips due to a shared neutral somewhere.
Reply With Quote
  #37  
Old 4/11/06, 9:15 AM
Richard L. Bennett Richard L. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Frostproof, Fl
Posts: 2,304
Default Re: False Ground

Bruce

Point well taken

What seems to be basic knowledge to many is advanced to many others.

It is hard to inspect something that one does not understand. Too bad homes are not required to have on file up to date one line electrical diagrams

rlb
Reply With Quote
  #38  
Old 4/11/06, 10:56 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: False Ground

Quote:
Originally Posted by rbennett
PULL THE COVER OFF AND LOOK AT IT
As Bruce stated, that may not give you the answer you're looking for. As in the case where the homeowner creates the "bootleg" at an attic junction box rather than the receptacle itself - which is quite often the case in older, two-wire systems, where NM is tied in for additional circuits.

We need to learn to interpret our instruments based on their indicators as well as other conditions present in the home.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net



Last edited by jpope; 4/11/06 at 11:04 AM..
Reply With Quote
  #39  
Old 4/11/06, 11:26 AM
Richard L. Bennett Richard L. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Frostproof, Fl
Posts: 2,304
Default Re: False Ground

Jeff

Understand about the J box in the attic "converting" two wire to three wire. Wonder how far away the box could be so that the suretest would not see it?

rlb

Last edited by rbennett; 4/11/06 at 11:29 AM..
Reply With Quote
  #40  
Old 4/11/06, 12:46 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: False Ground

As a general rule, the SureTest will indicate a "false ground" if there is a connection between the neutral and ground within about 15 feet (conductor length) of the receptacle being tested.

Obviously, there are many variables that can come into play, so it's important to "get a feel" for your tester before writing up every false-ground indication.

It becomes more apparent in cases such as condos, where they have interior distribution (sub) panels, as these require isolated neutrals. A false ground indication in this case would almost certainly indicate a wiring error, whether it's a bootleg ground, or neutrals bonded/grounded to the distribution panel.

In any event, we shouldn't arbitrarily "flag" every false-ground indication.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #41  
Old 4/11/06, 1:41 PM
rdawes's Avatar
rdawes rdawes is offline
Active Poster
 
Join Date: Nov 2004
Location: Plano, TX
Posts: 427
Please Note: rdawes is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: False Ground

Side note on Sure Test instruments. I bought a 61-155 off of Ebay about a year ago and used it on every inspection since then. About 3 weeks ago the % Voltage Drop measurement stopped working. I sent it in to Sure Test to ask what it would cost for repair. Today I got a brand new 61-165 back from them for free! That is good customer service!

Last edited by rdawes; 4/11/06 at 1:55 PM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
False Ground / Bootleg Ground mmorris Electrical Inspections 12 5/17/07 12:11 PM
Grounding Myths Quiz pabernathy Electrical Inspections 33 1/26/07 6:59 PM
Harmonized Ground Fault Circuit Interrupters jtedesco1 Electrical Inspections 5 3/21/06 8:48 AM