Default False Ground / Bootleg Ground

In the last 5 inspections, I found bootleg grounds. I am using an Ideal Suretest. But up till the last 4 my analyzer never reported this. In some of these houses, there are a few outlets that are OK. But most are getting reported as a false ground. Some of these houses are new construction some are several years old. Anyone want to toss in their .02?
Reply With Quote
  #2  
Old 5/11/07, 12:26 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: False Ground / Bootleg Ground

Have you actually checked the ground to verify that it has been "bootlegged?"

The SureTest measures the resistance between the grounding conductor and the grounded conductor. If there is not enough resistance (as determined by the meter) the SureTest will indicate a "false" ground. This can (and often does) occur when the receptacle is close to the panel (where the neutrals and grounds are bonded).

In newer systems, even in long runs, there is very little resistance and you may get this reading even on the other side of the house (I find it most often in GFCI receptacles). This is, in part, due to quality materials and quality installations.

The indications given by our SureTest meters has to be interpreted. It requires an understanding of the meter and the electrical system in order to make accurate interpretations.

Read through your manual and you may get a better understanding of what your meter is really telling you.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 5/11/07, 12:47 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: False Ground / Bootleg Ground

Quote:
Originally Posted by mmorris
Anyone want to toss in their .02?
Yeah, might have some angry homeowners in your future.
Reply With Quote
  #4  
Old 5/11/07, 12:50 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,749
Default Re: False Ground / Bootleg Ground

Quote:
Originally Posted by mmorris
But up till the last 4 my analyzer never reported this.
So, why do you not simply think your SureTest is out of calibration, i.e. "broke" and just needs to be serviced or repaired?
Reply With Quote
  #5  
Old 5/11/07, 7:31 PM
mmorris mmorris is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Duluth, GA
Posts: 29
Default Re: False Ground / Bootleg Ground

Thank you Jeff.

Michael. Thats was my fear, but after reading the manual I found there was more to it than just a broken tool.
Reply With Quote
  #6  
Old 5/16/07, 9:08 PM
jcundiff's Avatar
jcundiff jcundiff is offline
Active Poster
 
Join Date: May 2005
Location: Fairview Park, OH
Posts: 251
Please Note: jcundiff is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: False Ground / Bootleg Ground

Mat- as usual, Jeff is right on the money. The sure test is much less effective in new buildings because of the generally greater ground integrity. I've found the bootleg function most useful in older buildings with box to yolk grounding or systems grounded through conduit. No matter what- you cant use the sure test as the gospel... consider it more as a gauge. Either way- who doesn't LOVE to find those buggers!
Reply With Quote
  #7  
Old 5/16/07, 9:28 PM
Peter C. Russell's Avatar
Peter C. Russell Peter C. Russell is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Alton Bay NH
Posts: 3,998
Default Re: False Ground / Bootleg Ground

I have a question and I think this has been brought up before. I used my tester on a GFI and it didn't trip, when I pushed the button it did, this was in a house that was 20 years old and had other GFIs that where stuck in the open position.
Reply With Quote
  #8  
Old 5/16/07, 9:37 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: False Ground / Bootleg Ground

Quote:
Originally Posted by prussell
I have a question and I think this has been brought up before. I used my tester on a GFI and it didn't trip, when I pushed the button it did...
What's the calibration date on your GFCI tester? It's probably reasonable to say that the GFCI device itself was defective, and not your tester. I just have a problem with folks that condemn equipment without calibrated test equipment. From the standpoint of an electrician, I'd encourage you to report this as a device that "may" have a problem, so that you don't look foolish in case it's fine. There is equipment on the market that will test the exact trip point, in milliamps, at which a GFCI trips.
Reply With Quote
  #9  
Old 5/16/07, 10:25 PM
Peter C. Russell's Avatar
Peter C. Russell Peter C. Russell is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Alton Bay NH
Posts: 3,998
Default Re: False Ground / Bootleg Ground

That's how I wrote it in my report, there where no GFIs at the kitchen sink and that was included as well.

I've test it out in other receptacles at my house and it checks out so I'm thinking it was the outlet.
Reply With Quote
  #10  
Old 5/16/07, 10:28 PM
Christian F. Mettel Christian F. Mettel is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Aurora, On
Posts: 486
Default Re: False Ground / Bootleg Ground

Quote:
Originally Posted by prussell
I have a question and I think this has been brought up before. I used my tester on a GFI and it didn't trip, when I pushed the button it did, this was in a house that was 20 years old and had other GFIs that where stuck in the open position.
I have both the more expensive Ideal Suretest tester and the much less expensive Commercial Electric one that I had bought when I first started out. Usually I use the Suretest, but there are times when the other one comes in handy because of its smaller size. When I have come across GFCI's that don't trip properly using the Suretest, I try it with the Commercial Electric to make sure its not my equipment that is faulty but the receptacle itself.

Chris
Reply With Quote
  #11  
Old 5/16/07, 10:33 PM
Peter C. Russell's Avatar
Peter C. Russell Peter C. Russell is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Alton Bay NH
Posts: 3,998
Default Re: False Ground / Bootleg Ground

Chris, That's a good point, I'll get a back up tester to keep on hand.

Thanks, Pete
Reply With Quote
  #12  
Old 5/16/07, 10:38 PM
Christian F. Mettel Christian F. Mettel is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Aurora, On
Posts: 486
Default Re: False Ground / Bootleg Ground

Quote:
Originally Posted by prussell
Chris, That's a good point, I'll get a back up tester to keep on hand.

Thanks, Pete
Cheers,

Chris
Reply With Quote
  #13  
Old 5/17/07, 12:11 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: False Ground / Bootleg Ground

Quote:
Originally Posted by Marc D. Shunk
There is equipment on the market that will test the exact trip point, in milliamps, at which a GFCI trips.
The SureTest does this. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Bootleg Ground jallingham Electrical Inspections 28 7/13/06 8:43 AM
False Ground Steven Brewster Electrical Inspections 40 4/11/06 1:41 PM


All times are GMT -4. The time now is 3:34 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts