#1
|
||||
|
||||
|
1. Is there a safe maximum distance between the main panel and the home it protects?
2. Is there a safe maximum distance between a GFCI breaker and the outlet it protects? Kenton Shepard, InterNACHI member # 04082383 Certified Master Inspector (CMI) InterNACHI Director of International Development Director of Green Building EXPERT WITNESS SERVICE Conventional and Log homes (303) 717-8940
|
|
#2
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
1) I don't understand the question. The panel must be IN/ON the home it protects. Any other situation would be absurdly cumbersome.
2) No, not really. If the GFI protection is remote, a sricker should be used on what it's protecting. |
|
#3
|
||||
|
||||
|
Don Peterson, CMI AmeriDream Home Inspections Inc. NYS License: 16000014560 |
|
#4
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
The service disconnect has to be on the property but not necessarily on a building. Each building does require a disconnect though. I have inspected "may pole" instlations where they have a 3r service disconnect on a pole in the middle of the property and radial feeders going to each building. That is best for mitigating voltage drop.
The "length" on the GFCI circuit is to reduce niusanse tripping, not a safety issue. If the circuit is too long they fear you will get too much coupling to ground. I have not seen that at my house. I have a long circuit in my screen cage hitting all the lights and a long circuit down to my boat lift. I don't have a tripping problem on either of them. Both have several hundred feet of wire in pipe. |
|
#5
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
I answered #1 the way I did because he specifically stated main "panel", not main disconnect. Now I wonder which he means.
Like Greg said though, even if there is a "main disconnect" somewhere on the property, the structure MUST have it's own service disconnect on it or just inside of it. |
|
#6
|
|||
|
|||
|
Please Note:
mthomas2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
The Cliff Notes version of the Square D doc Donald cites above:
NOTE: To minimize nuisance tripping: • Do not connect circuit breaker to swimming pool equipment installed before adoption of the 1965 National Electrical Code. • Do not connect circuit breaker to electric ranges or clothes dryers whose frames are grounded by connection to a neutral conductor. • Do not connect circuit breaker to more than 250 ft. (76 m) of load conductor for the total one-way run. |
|
#7
|
||||
|
||||
|
This was a situation in which a sub-panel (no GFCI breakers) for a detached garage was located on another building with approximately 100 feet between the sub-panel and the garage.
Underground conductors ran to 2 GFCI outlets in the garage which protected garage wiring. I was wondering if the breakers in the sub-panel could be replaced with GFCI breakers to protect the garage. Kenton Shepard, InterNACHI member # 04082383 Certified Master Inspector (CMI) InterNACHI Director of International Development Director of Green Building EXPERT WITNESS SERVICE Conventional and Log homes (303) 717-8940
|
|
#8
|
|||
|
|||
|
Quote:
InterNachi Awards Portal: http://co.nachi.org/inachiawards/ ____________________________________________ "An Education, not just an Inspection" Larry Kage, CMI Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector serving the Traverse City, Michigan area and beyond.
|
|
#9
|
||||
|
||||
|
Please Note:
Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Quote:
Are you saying that there is a set of feeders and two branch circuits feeding this garage? Quote:
Quote:
|
|
#10
|
|||
|
|||
|
Please Note:
mthomas2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
1) So - to be sure I understand - you cannot (for example) separate outlet and lighting circuits to the garage, you would have to run feeders to a load-side panel in the garage instead.
2) Are any of the conditions listed in 225.30(A-E) likely relevant to Home Inspectors? ---------- Are you by any chance the Mike Whitt who grew up Roseland? |
|
#11
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
(A) Special Conditions. Additional feeders or branch circuits shall be permitted to supply the following:
(1) Fire pumps (2) Emergency systems (3) Legally required standby systems (4) Optional standby systems (5) Parallel power production systems (B) Special Occupancies. By special permission, additional feeders or branch circuits shall be permitted for the following: (1) Multiple-occupancy buildings where there is no space available for supply equipment accessible to all occupants, or (2) A single building or other structure sufficiently large to make two or more supplies necessary. (C) Capacity Requirements. Additional feeders or branch circuits shall be permitted where the capacity requirements are in excess of 2000 amperes at a supply voltage of 600 volts or less. (D) Different Characteristics. Additional feeders or branch circuits shall be permitted for different voltages, frequencies, or phases or for different uses, such as control of outside lighting from multiple locations. (E) Documented Switching Procedures. Additional feeders or branch circuits shall be permitted to supply installations under single management where documented safe switching procedures are established and maintained for disconnection. |
|
#12
|
||||
|
||||
|
Please Note:
Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Yes, a multiwire circuit can be installed to a detached garage as long as there is a disconnect that is rated as service equipment installed at the garage. Article 225 was introduced to the NEC in the early 1970s and the requirement for a disconnect was entered in the 1993 code cycle, 225-8 with 225-8(c) requiring the disconnect to be rated as service equipment. In today’s code (2005) 225.36 has an exception which states; Exception: For garages and outbuildings on residential property, a snap switch or a set of 3-way or 4-way snap switches shall be permitted as the disconnecting means. What we need to understand is that the part of this exception that limits the use of these switches is “A snap switch” and “A set of 3-way or 4-way snap switches” which clearly denotes a single switch or a single set of 3-way or 4-way switches. 225.39 states what size these circuits must be. Quote:
---------- Quote:
Rumor has it that some of my ancestors may have ended up at area 51 a few years back but if they did the government is keeping a tight lid on their where-a-bouts. Wait a minute you said Roseland, NC not Roswell Nv., LOL I do have distant relatives scattered all over the state of NC and Va. The family moved to the mountains of Va. in the 1800s and migrated south over the state of NC for the next century. Over the past 50 years my brothers and first cousins have moved as far West and North as Maple Falls, Washington and as far East and South as Key West Florida. No I am not this man although I have been there. |
|
#13
|
||||
|
||||
|
Sorry... one set of feeders exist only. They run from a Non-GFCI sub-panel out back of the main building to the double garage (serving separate units of a duplex). Also on this circuit are exterior walkway lighting for the duplex structure. Feeders run to two GFCI's in the garage (no separate sub-panel), and then to a couple of outlets, switches, lights and overhead door openers, one at each side of the garage.
Kenton Shepard, InterNACHI member # 04082383 Certified Master Inspector (CMI) InterNACHI Director of International Development Director of Green Building EXPERT WITNESS SERVICE Conventional and Log homes (303) 717-8940
|
|
#14
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Mike, the aliens landed in Roswell NM, not Nevada.
|
|
#15
|
||||
|
||||
|
Please Note:
Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Feeders will always have overcurrent on both ends. Branch circuits will have overcurrent on the line end. Service conductors will have overcurrent on the load end |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| AFCI Questions and Answers - Mike Holt | pabernathy | Electrical Inspections | 2 | 1/8/11 8:04 PM |
| GFCI Safety Notice | rcooke | Electrical Inspections | 1 | 10/30/07 1:29 PM |
| Bathroom outlet near floor: GFCI | mthomas2 | Electrical Inspections | 3 | 4/13/07 11:35 PM |