Default How far would you go!!

I posted information pertaining to an exterior disconnect & wanted to follow up with my inspection that I performed today.

This is the thread I started. http://www.nachi.org/forum/f19/main-disconnect-11630/

So the question I posted on my thread tittle today is as a Home Inspector (Not an electrician) how far would you go to inspect this exterior.

1) Open exterior cover & then remove the 2 screws.
2) There is a GFCI in the cover & you need to remove 2 screws that are stripped. GFCI didnt work & I figured it was there for the utility company as the home had a front & back GFCI & this would not be needed by the home owner. I reported as inoperable
3) The interior cover you need to pry to remove. Will not lift out with installed handle assemply.

I stopped at this point as the cover would not come out with moderate pressure.

Now to the interior panel. This appeared to be a remote distribution panel.

As you can see from the photos the white romex was added on by the homeowner to the basement. He used 14 gauge to 20 amp breakers. He also ran 2 wires in one hole so I knew it was done by a handyman.

Question. Can a siemens breaker be installed in a cutler hammer panel?

Thanks
Attached Thumbnails
far-would-you-go-89106-br.hts.-001-small-.jpg.jpg
Views:	72
Size:	30.3 KB
ID:	8120   far-would-you-go-89106-br.hts.-010-small-.jpg.jpg
Views:	72
Size:	26.6 KB
ID:	8121   far-would-you-go-89106-br.hts.-015-small-.jpg.jpg
Views:	77
Size:	70.9 KB
ID:	8122  
Reply With Quote
  #2  
Old 1/1/07, 7:09 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: How far would you go!!

On the inside, the two cables into a singel NM connector is prefectly fine, safe and legal.
The #14 on a 20a is a blatant violation and not exactly safe.
The Siemens breaker may very well be legal in that panel. A slong as it is rated to use in a BR panel.
Reply With Quote
  #3  
Old 1/1/07, 7:24 PM
Thomas H. Dietrich's Avatar
Thomas H. Dietrich Thomas H. Dietrich is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: How far would you go!!

Quote:
On the inside, the two cables into a singel NM connector is prefectly fine, safe and legal.
IMHO, might be beyond a HI task. The rule is 1 cable per connector unless the manufacturer says its ok. So, from what I do, it's a c-500 or Ai's Black buttons, I wouldn't know off the top of my head it it was ok. Might want to defer er the whole electrical system, since the collection of 'flaws' is growing.

Quote:
The #14 on a 20a is a blatant violation and not exactly safe.
Very true if it's 14# gauge. Don't' fall into the color trap, manufacturers changed to colors to try and non-reading inspectors and workers to stop over loading the wires. Take the time to read the information on the jacket, you might find people using NM instead of NM-B, and it might be 12/2 romex, just a couple years old, prior to coloring.

Quote:
The Siemens breaker may very well be legal in that panel. A slong as it is rated to use in a BR panel.
"Slong"?

Check the inside, usually there is a disclaimer as to what breakers are allowed in the panel. Also, I've seen some people use 'off' brands of breakers to bypass the panel manufacturers designs to limit the use of tandem breakers. Count the number of breakers, this panel could also be overloaded, per code.

Just thinking out loud...

tom

Last edited by tdietrich1; 1/1/07 at 7:27 PM..
Reply With Quote
  #4  
Old 1/1/07, 8:22 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: How far would you go!!

About the connectors. I don't think I've ever seen a two-screw (typical) metallic NM cable connector that was not rated for at least two cables.
This is SOP for me so I can leave as many unused K-O's as I can. I HATE it when I come across a panel with no available K-O's and every damn NM connector has only one cable. AGRH!
Reply With Quote
  #5  
Old 1/1/07, 8:36 PM
Thomas H. Dietrich's Avatar
Thomas H. Dietrich Thomas H. Dietrich is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: How far would you go!!

Warning readers, This has gone a tangent....

Quote:
About the connectors. I don't think I've ever seen a two-screw (typical) metallic NM cable connector that was not rated for at least two cables.
I was warned about some clamps coming from "India" that had almost no ratings and the "finger", on the movable part, that would pierce the jacket, too easily.

Quote:
This is SOP for me so I can leave as many unused K-O's as I can. I HATE it when I come across a panel with no available K-O's and every damn NM connector has only one cable. AGRH!
Ah personally I hate you. I love when I come to a panel and to run a new circuit, I can just fish my cable through an existing clamp. Saves me time, and material.

tom
Reply With Quote
  #6  
Old 1/1/07, 9:10 PM
rromoser's Avatar
rromoser rromoser is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Fishers, IN
Posts: 187
Default Re: How far would you go!!

I might be wrong, but it seems to me that only some of the plastic "RX" connectors are UL listed for 2 cables.
Reply With Quote
  #7  
Old 1/2/07, 12:57 AM
salexander salexander is offline
New User
 
Join Date: Jan 2005
Location: Newton, Ks
Posts: 29
Please Note: salexander is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: How far would you go!!

Funny thing is while debating the proper use of a romex connector on the white romex, none of the yellows even have connectors.
Reply With Quote
  #8  
Old 1/2/07, 1:39 AM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: How far would you go!!

Quote:
Originally Posted by salexander
Funny thing is while debating the proper use of a romex connector on the white romex, none of the yellows even have connectors.
It might appear that way, but I just barely detect that they're installed with "black buttons". Arlington Industries is one of the main manufacturers of this type of NM connector.



According to the manufacturers chart, they take:
1-14/2 to 1-10/2
2-14/2 to 2-10/2
1-14/2 and 1-12/2
1-14/3 to 1-10/3
2-14/3 to 2-12/3
1-14/2 and 1-10/2
1-12/2 and 1-10/2
1-14/3 and 1-12/3

A fella would really be doing something to get two 12-3's in those black button connectors, but it is permitted.
Reply With Quote
  #9  
Old 1/2/07, 3:04 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: How far would you go!!

Love them connectors.......its all I use now. Anyone that works with them knows once the wire is in...its TOUGH to get back out, it is possible but you have to be careful not to rip the jacket.

Got a WHOLE box of em....

Yep..that panel has those type of connectors..perfectly fine.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #10  
Old 1/2/07, 12:55 PM
Thomas H. Dietrich's Avatar
Thomas H. Dietrich Thomas H. Dietrich is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: How far would you go!!

Quote:
Originally Posted by pabernathy
Love them connectors...
Same here, saves time, weighs nothing, and the price is right. I don't like is, newbs who think they can just yank out a cable from them, because their plastic. I've seen home run sheaths damaged because of newbs.

tom

P.S. Been waiting for the local supply shops to get the RACO's version in, they connect from the inside out. Wouldn't mind having a few of those. <crossing fingers>
Reply With Quote
  #11  
Old 1/2/07, 1:12 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: How far would you go!!

I hear ya Tom....lets just say...I wish I had invented those freakin connectors.....simple...yet effective....DANG i missed the boat on that invention.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #12  
Old 1/2/07, 6:37 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: How far would you go!!

Quote:
Originally Posted by pabernathy
I hear ya Tom....lets just say...I wish I had invented those freakin connectors.....simple...yet effective....DANG i missed the boat on that invention.
Arlington invents some of the coolest stuff. I'm glad to see a "flush" romex connector. Often, people would omit any kind of connector for coming in the back of kitchen exhaust hoods and fluorescent strip lights over closet doors. The flush type romex connector is more palletable to installers for those applications.
Reply With Quote
  #13  
Old 1/2/07, 6:51 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: How far would you go!!

I agree Marc.......love some of the side screw boxes they have come up with.....makes it easy for retro's in already finished areas.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #14  
Old 1/2/07, 7:22 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: How far would you go!!

Quote:
Originally Posted by rromoser
I might be wrong, but it seems to me that only some of the plastic "RX" connectors are UL listed for 2 cables.
Look harder.
Arlington 841, an industry standard, is rated for several combinations of three cables, not just two.

1-14/2 & 1-14/3, or 1-14/2 to 10/2 NM

1-14/2 & 1-12/3, or 1-14/3 to 10/3 NM

1-12/2 & 1-14/3, or 2-14/2 to 10/2 NM

1-12/2 & 1-12/3, or 1-14/2 & 1-12/2 NM

2-14/2 & 1-14/3, or 1-14/2 & 1-10/2 NM

2-14/2 & 1-12/3, or 1-12/2 & 1-10/2 NM


or 3-14/2 NM



BTW, Arlington is one of my favorite companies as well. They have saved the day more times than I care to remember.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 3:28 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147