Question Federal Electric 100A standalone main breaker -- OK or problematic?

I did an inspection, which had an old c. 1960 Bulldog pushmatic type circuit breaker panel, with a 100A Federal Electric main breaker in a separate main panel.

This did not appear to be a "Stab-LOk" breaker. Does anyone in the house (ahem!) know whether or not this type of Federal breaker is associated with the usual FPE circuit breaker issues?

Internet searches turned up lots of irrelevant stuff, as usual.
Attached Thumbnails
federal-electric-100a-standalone-main-breaker-ok-problematic-img_0055t.jpg   federal-electric-100a-standalone-main-breaker-ok-problematic-img_0056t.jpg   federal-electric-100a-standalone-main-breaker-ok-problematic-img_0060t.jpg  

Last edited by fbartlo; 8/4/10 at 11:35 PM..
Reply With Quote
Need a home inspection in Rhode Island? Check out InterNACHI's listing of Rhode Island certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 8/4/10, 11:29 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,956
Default Re: Federal Electric 100A standalone main breaker -- OK or problematic?

Do you have a pic of the breakers from the subpanel?



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
  #3  
Old 8/4/10, 11:32 PM
Frank L. Bartlo Frank L. Bartlo is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: SE Michigan
Posts: 236
Default Re: Federal Electric 100A standalone main breaker -- OK or problematic?

This was from a standalone main. No other breakers in the Federal panel. here are a couple pics.

The other panel was a perfectly fine Bulldog panel with "Pushmatic" type breakers. Not Federal Electric/FPE.
Attached Thumbnails
federal-electric-100a-standalone-main-breaker-ok-problematic-img_0054_48_1.jpg   federal-electric-100a-standalone-main-breaker-ok-problematic-img_0055_49_1.jpg   federal-electric-100a-standalone-main-breaker-ok-problematic-img_0053b.jpg  

Last edited by fbartlo; 8/4/10 at 11:40 PM..
Reply With Quote
  #4  
Old 8/4/10, 11:36 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,956
Default Re: Federal Electric 100A standalone main breaker -- OK or problematic?

Main, only, looks okay. Just remember that the next panel down the line is a subpanel and must be wired, accordingly.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
  #5  
Old 8/4/10, 11:42 PM
Frank L. Bartlo Frank L. Bartlo is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: SE Michigan
Posts: 236
Default Re: Federal Electric 100A standalone main breaker -- OK or problematic?

Good point. The grounding electrode appeared to have been run directly to the sub-panel.
Reply With Quote
  #6  
Old 8/5/10, 8:39 AM
Bill Smith's Avatar
Bill Smith Bill Smith is online now
InterNACHI Member
 
Join Date: Jun 2003
Location: East Northport, NY
Posts: 1,043
Default Re: Federal Electric 100A standalone main breaker -- OK or problematic?

based on the age of the main breaker I would recommend replacement. Breakers are not like wine, they don't get better with age.



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
  #7  
Old 8/5/10, 9:00 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,252
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Federal Electric 100A standalone main breaker -- OK or problematic?

Quote:
Originally Posted by bsmith View Post
based on the age of the main breaker I would recommend replacement. Breakers are not like wine, they don't get better with age.
Bill, what would you use to back up your recommendation on replacement of the main CB, besides it looks old.
Reply With Quote
  #8  
Old 8/6/10, 9:44 AM
Bill Smith's Avatar
Bill Smith Bill Smith is online now
InterNACHI Member
 
Join Date: Jun 2003
Location: East Northport, NY
Posts: 1,043
Default Re: Federal Electric 100A standalone main breaker -- OK or problematic?

Based on it's age. Breakers are mechanical devices that can be affected by a wide range of things (dust, wear, moisture, etc). Manufacturers usually guarantee breakers for only one or two years. I routinely recommend replacement of any breaker that is 25 years or older.



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
  #9  
Old 8/6/10, 3:58 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Federal Electric 100A standalone main breaker -- OK or problematic?

Quote:
Originally Posted by bsmith View Post
Manufacturers usually guarantee breakers for only one or two years. I routinely recommend replacement of any breaker that is 25 years or older.
might want to change your ideas.

From a Cutler-Hammer brochure

Cutler-Hammer Type CH breakers
also carry a lifetime warranty
the best in the industry.

For Square D

Square D/Schneider Electric Residential Products Limited Warranty
I. Square D/Schneider Electric QO® brand Load Centers and Load Center Branch Circuit Breakers
Square D/Schneider Electric warrants its branch circuit breakers to be free from defects in material and workmanship under normal care and proper usage in a residential installation, for the lifetime of the load center in which it is installed. QO® brand load centers are also covered under the same lifetime warranty. If the circuit breaker or QO brand load center fails within the warranty period because of a defect in material or workmanship, Square D/Schneider Electric will replace the defective breaker free of charge upon following the notice procedures below and return of the product to place
of purchase.

Reply With Quote
  #10  
Old 8/6/10, 9:25 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,252
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Federal Electric 100A standalone main breaker -- OK or problematic?

Quote:

Originally Posted by bsmith
Manufacturers usually guarantee breakers for only one or two years. I routinely recommend replacement of any breaker that is 25 years or older.



Quote:
Originally Posted by Jim Port View Post
might want to change your ideas.

From a Cutler-Hammer brochure

Cutler-Hammer Type CH breakers
also carry a lifetime warranty
the best in the industry.

For Square D

Square D/Schneider Electric Residential Products Limited Warranty
I. Square D/Schneider Electric QO® brand Load Centers and Load Center Branch Circuit Breakers
Square D/Schneider Electric warrants its branch circuit breakers to be free from defects in material and workmanship under normal care and proper usage in a residential installation, for the lifetime of the load center in which it is installed. QO® brand load centers are also covered under the same lifetime warranty. If the circuit breaker or QO brand load center fails within the warranty period because of a defect in material or workmanship, Square D/Schneider Electric will replace the defective breaker free of charge upon following the notice procedures below and return of the product to place
of purchase.


I agree with Jim here. Unless you have specific documentation, you're kind of going out on a limb saying that an old looking breaker needs to be replaced.
Reply With Quote
  #11  
Old 8/7/10, 10:01 AM
Bill Smith's Avatar
Bill Smith Bill Smith is online now
InterNACHI Member
 
Join Date: Jun 2003
Location: East Northport, NY
Posts: 1,043
Default Re: Federal Electric 100A standalone main breaker -- OK or problematic?

Good info Jim - but that pertains to new breakers. Don't forget we are talking about breakers that are 25 years old, or older. You won't find any documentation to support replacing old breakers in the NEC, but based on comments from Paul Abernathy, and info from the book "Electrical Inspection of Existing Dwellings" I am comfortable suggesting the replacement of older breakers. As Home Inspectors we can suggest safety measures even if they are not code supported. We are not code enforcement officials. For example: I can recommend that a handrail be installed on stairs with less than 3 risers. Codes will not support that, but I can recommend it. I think it's important to keep our clients safety in mind.



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
  #12  
Old 9/2/10, 8:51 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Federal Electric 100A standalone main breaker -- OK or problematic?

Yep....if the breakers are to replace existings breakers then Schneider (Square D) can stick it. The Mag. V. Moss act made his replacement argument pointless. This is the intent of a UL Classified Breaker and has it's own warranty. Have you ever tried to get Square D ( Schnieder ) to replace a 25 year old breaker...good luck. Adding a new UL Listed classified breaker has it's own warranty by Eaton regardless of the panel it is installed in as long as it is tested for that panel...and their is a list on here I posted of all classified breakers and the panels to be used in.

If the breaker is simply OLD...and not defective then the warranty is pointless. The issue of suggesting replacements for breakers that are 25+ years old is a sound one considering the importance of the Overcurrent Protection and since older devices are thermal activated....heat has negative effects over time so I have no problem with the recommendation on old breakers....none what so ever.



Paul W. Abernathy
Reply With Quote
  #13  
Old 9/2/10, 9:19 PM
Mark Thorman Mark Thorman is offline
Unmoderated Guest
 
Join Date: Mar 2008
Posts: 392
Please Note: Mark Thorman is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Federal Electric 100A standalone main breaker -- OK or problematic?

Quote:
Originally Posted by bsmith View Post
I am comfortable suggesting the replacement of older breakers. As Home Inspectors we can suggest safety measures even if they are not code supported.

Do you take it to the next logical step and recommend AFCI's as the CPSC and most fire prevent organizations do?

www.MauiHomeInspections.com
Reply With Quote
Need a home inspection in Rhode Island? Check out InterNACHI's listing of Rhode Island certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 9/2/10, 11:28 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Federal Electric 100A standalone main breaker -- OK or problematic?

Quote:
Originally Posted by Mark Thorman View Post
Do you take it to the next logical step and recommend AFCI's as the CPSC and most fire prevent organizations do?

www.MauiHomeInspections.com
I recommend AFCI's


Quote:
Although not required when originally built the system does not include arc-fault circuit interrupters, which , are used to protect 15 and 20 amp branch circuits serving bedrooms.
You may wish to have an Electrician add Arc Fault protectors as a safety upgrade.
Reply With Quote
  #15  
Old 9/2/10, 11:35 PM
Mark Thorman Mark Thorman is offline
Unmoderated Guest
 
Join Date: Mar 2008
Posts: 392
Please Note: Mark Thorman is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Federal Electric 100A standalone main breaker -- OK or problematic?

Here's mine.

The 15 and 20 amp circuits of the home are not AFCI (Arc Fault Circuit Interrupter) protected circuits.
AFCI’s are a relatively new safety device that can protect the home from a potential fire as a result of damaged wiring, loose connections or defective appliances by shutting off the circuit when a hazardous arc fault condition exists.
The CPSC (Consumer Product Safety Commission) and numerous fire prevention organizations strongly recommend that older homes be upgraded to AFCI protected circuits.
More information regarding AFCI’s can be obtained at


www.MauiHomeInspections.com
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Federal Pacific Main Panel...Question dnasser Electrical Inspections 12 4/30/10 7:52 PM
Federal Electric Panel jleahy Electrical Inspections 3 5/27/09 10:54 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 9:32 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts