Default Federal pacific

Have a federal pacific 200 amp main service disconect. Should it be reported on as needing replacement? Panels have been replaced.

Last edited by jritter; 11/26/13 at 3:50 PM..
Reply With Quote
Need a home inspection in Arizona? Check out InterNACHI's listing of Arizona certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 8/22/13, 11:26 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 20,336
Default Re: Federal pacific

Why did you see any thing wrong with other then the name .
Looks OK to me .
.So I see no reason to report it.
If it said SQ D on the out side would you be asking this question



If you do not search for more ,
......You will never find it.

............. Roycooke@hotmail.com
...................613-827-2011
Reply With Quote
  #3  
Old 8/22/13, 11:31 AM
John Ritter John Ritter is offline
InterNACHI Member
 
Join Date: May 2012
Location: Cape Coral, Fl.
Posts: 1,246
Default Re: Federal pacific

Quote:
Originally Posted by rcooke View Post
Why did you see any thing wrong with other then the name .
Looks OK to me .
.So I see no reason to report it.
If it said SQ D on the out side would you be asking this question
Probally not ,just wanted to hear from some others to see if the name scared you.
Reply With Quote
  #4  
Old 8/22/13, 11:43 AM
Jeffrey R. Pope, CMI's Avatar
Jeffrey R. Pope, CMI Jeffrey R. Pope, CMI is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 11,774
Default Re: Federal pacific

Many here are "scared" of the name, so don't be surprised when someone jumps in and calls it a latent fire hazard.

Disregard any such response and look at the panel/disconnect for yourself.

In this particular instance, I see no reason to give this disconnect a second look.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 8/22/13, 12:15 PM
Joshua L. Frederick Joshua L. Frederick is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Defiance, OH
Posts: 2,226
Send a message via AIM to jfrederick
Default Re: Federal pacific

There's nothing "Stab-lok" about this panel/breaker. The ones that had "issues" were the Stab-Lok type. FP made other panels that didn't use stab-lok breakers.
Reply With Quote
  #6  
Old 8/22/13, 12:35 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 20,336
Default Re: Federal pacific

Quote:
Originally Posted by jfrederick View Post
There's nothing "Stab-lok" about this panel/breaker. The ones that had "issues" were the Stab-Lok type. FP made other panels that didn't use stab-lok breakers.
What are your concerns with stab-lok and what do you say about them .
Thanks... Roy



If you do not search for more ,
......You will never find it.

............. Roycooke@hotmail.com
...................613-827-2011
Reply With Quote
  #7  
Old 8/22/13, 12:49 PM
John Ritter John Ritter is offline
InterNACHI Member
 
Join Date: May 2012
Location: Cape Coral, Fl.
Posts: 1,246
Default Re: Federal pacific

Thanks I appreaciate the response. Only issue was the name, everything else was good. CMA
Reply With Quote
  #8  
Old 8/22/13, 1:05 PM
Greg Bell, Sr's Avatar
Greg Bell, Sr Greg Bell, Sr is offline
InterNACHI Member
 
Join Date: Oct 2002
Location: Titusville, FL
Posts: 4,593
Default Re: Federal pacific

The insurance company may have a problem with it if you did a four point.



Greg Bell
Titusville, Fl
02111507

Serving Central Florida
Reply With Quote
  #9  
Old 8/22/13, 3:03 PM
John Ritter John Ritter is offline
InterNACHI Member
 
Join Date: May 2012
Location: Cape Coral, Fl.
Posts: 1,246
Default Re: Federal pacific

Quote:
Originally Posted by gbell View Post
The insurance company may have a problem with it if you did a four point.
Some times there is just no way to win. This was on my mind, but I was only doing the home inspect today. With no defect to the discount there is nothing to report, with insurance it needs reporting. Thanks
Reply With Quote
  #10  
Old 8/22/13, 6:27 PM
Jeffrey Belfus Jeffrey Belfus is offline
InterNACHI Member
 
Join Date: Oct 2012
Location: Turnersville New jersey
Posts: 51
Default Federal pacific

Stab-lok FP breakers were known to overheat and not trip under a fault. When I see them in a home I just report that it is working or Not and give a link where the customer can read some info on it for themselves.








Jeffrey Belfus
Precision Property Inspections LLC
JBelfusPPI@gmail.com
215-432-1649
www.turnersvillehomeinspections.com

Reply With Quote
  #11  
Old 8/22/13, 6:29 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 20,336
Default Re: Federal pacific

Quote:
Originally Posted by jbelfus View Post
Stab-lok FP breakers were known to overheat and not trip under a fault. When I see them in a home I just report that it is working or Not and give a link where the customer can read some info on it for themselves.
Gee would you post that link so we can all see this information . Thanks . Roy



If you do not search for more ,
......You will never find it.

............. Roycooke@hotmail.com
...................613-827-2011
Reply With Quote
  #12  
Old 8/22/13, 6:49 PM
Jeffrey Belfus Jeffrey Belfus is offline
InterNACHI Member
 
Join Date: Oct 2012
Location: Turnersville New jersey
Posts: 51
Default Federal pacific

Roy, here is an article I reference to clients.
http://inspectapedia.com/fpe/fpepanel.htm








Jeffrey Belfus
Precision Property Inspections LLC
JBelfusPPI@gmail.com
215-432-1649
www.turnersvillehomeinspections.com

Reply With Quote
  #13  
Old 8/22/13, 7:30 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 2,088
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Federal pacific

Judging from the size of that it appear to only be a disconnect switch and not an OCPD.
Reply With Quote
Need a home inspection in Arizona? Check out InterNACHI's listing of Arizona certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 8/22/13, 11:13 PM
Russell J. Hensel's Avatar
Russell J. Hensel Russell J. Hensel is offline
InterNACHI Member
 
Join Date: Jul 2008
Location: My house
Posts: 9,736
Default Re: Federal pacific

looks like a service disconnect to me...200 amps...and it was off next to the meter. Looks like the service breaker to me.



Comprehensive Building Consultants
Naples Home Inspection, Naples Mold Inspection, Naples Radon Inspection, Bonita Springs Home Inspection, Bonita Springs Mold Inspection, Bonita Springs Radon Inspection.



Last edited by rhensel; 8/22/13 at 11:19 PM..
Reply With Quote
  #15  
Old 8/22/13, 11:25 PM
Jeffrey R. Pope, CMI's Avatar
Jeffrey R. Pope, CMI Jeffrey R. Pope, CMI is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 11,774
Default Re: Federal pacific

Quote:
Originally Posted by jbelfus View Post
Stab-lok FP breakers were known to overheat and not trip under a fault. When I see them in a home I just report that it is working or Not and give a link where the customer can read some info on it for themselves.
Please research the info you're passing off to your clients. The site you provided in your subsequent post is full of misinformation and unsubstantiated allegations.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Federal Pacific Panel opinion khouse1 Florida Inspectors 27 5/6/13 9:07 PM
Federal Pacific Controls jleahy Electrical Inspections 1 6/19/12 7:53 AM
Federal Pacific System and Homeowner Wiring pmagrone Electrical Inspections 2 8/2/07 5:30 PM
Federal Pacific Panels cbottger Electrical Inspections 26 8/22/06 12:43 PM

All times are GMT -4. The time now is 6:49 PM.
no new posts