Default Federal Pacific electrical panels

I inspected a home that had a recalled federal pacific panel installed
in a 1989 home.There were no visual defects,but if a breaker was to go bad they would have to change the entire panel.Can anyone lead me to the re-call information on these panels?


I NEED A PROFESSINAL OPINION !
Reply With Quote
  #2  
Old 6/3/06, 6:52 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Federal Pacific electrical panels

FPE has never been recalled!!



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 6/3/06, 6:56 PM
Curtis Petty Curtis Petty is offline
InterNACHI Member
 
Join Date: Jul 2005
Location: fayetteville, ga
Posts: 68
Default Re: Federal Pacific electrical panels

Jeff-The electrician said the panel does not exsist any more.What happens in they burn/or damage a breaker.The electrician said they no longer have the type they would need?
Reply With Quote
  #4  
Old 6/3/06, 6:59 PM
Curtis Petty Curtis Petty is offline
InterNACHI Member
 
Join Date: Jul 2005
Location: fayetteville, ga
Posts: 68
Default Re: Federal Pacific electrical panels

Quote:
Originally Posted by jpope
FPE has never been recalled!!
jeff did you see what I wrote back and can you help out?
Reply With Quote
  #5  
Old 6/3/06, 7:01 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Federal Pacific electrical panels

There are replacement breakers available and still in production. The electrician misinformed you.

There has never been a recall on FPE or its breakers, although the Stab-lok load centers were "branded" as hazardous http://www.inspect-ny.com/fpe/fpepanel.htm



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #6  
Old 6/3/06, 7:07 PM
Curtis Petty Curtis Petty is offline
InterNACHI Member
 
Join Date: Jul 2005
Location: fayetteville, ga
Posts: 68
Default Re: Federal Pacific electrical panels

Quote:
Originally Posted by jpope
There are replacement breakers available and still in production. The electrician misinformed you.

There has never been a recall on FPE or its breakers, although the Stab-lok load centers were "branded" as hazardous http://www.inspect-ny.com/fpe/fpepanel.htm
Thats the type of panel Stab-lock.My customer has concerns about this panel.I have noted no visual defects and proper awg conductor,no arcing present but they still insist the seller replace the panel.
Reply With Quote
  #7  
Old 6/3/06, 7:10 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Federal Pacific electrical panels

Give them the info, send them the link, but don't say it has been recalled. That simply isn't true.

I would be one pissed off seller if you made a false statement such as that.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #8  
Old 6/3/06, 11:23 PM
tneumann's Avatar
tneumann tneumann is offline
Active Poster
 
Join Date: Jan 2006
Location: Woodland Park, co
Posts: 2,060
Please Note: tneumann is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Federal Pacific electrical panels

Give them the info...let them argue w/ the seller that isn't your job, unless they want to split the commission?
Reply With Quote
  #9  
Old 6/4/06, 10:57 AM
Jason A. Sieg, CMI's Avatar
Jason A. Sieg, CMI Jason A. Sieg, CMI is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Davison, MI
Posts: 839
Default Re: Federal Pacific electrical panels

If they want it replaced that is between them and the seller. In either case it doesn't cost that much to have that done. $100.00 to 200.00 for supplies & labor. A good electrician should be able to change over the panel in under 3-4 hours unless there are some major problems with the original wiring.

Peace of Mind for under $500.00. Am I wrong?



Jason Sieg, CMI
Davison, MI
NACHI05091399


Knowing the current condition,
to make a wise decision.

President, Great Lakes-East Chapter
Join NACHI Great Lakes - East Chapter

http://mi.nachi.org/greatlakes-east/about.html
ssieg@gfn.org
Reply With Quote
  #10  
Old 6/4/06, 11:21 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Federal Pacific electrical panels

Those must be MI prices Jason. A new 100 amp service sets you back at least $1200 in these parts.

That's still a small price to pay as far as I am concerned.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #11  
Old 6/4/06, 11:26 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,611
Default Re: Federal Pacific electrical panels

http://www.schneider-electric.ca/www...l/19451968.htm
These panels are still being manufactured and used in Canada.
I do not know if they are much different then what you have in the USA .
I think that around 50% of the homes I inspect have them .
They are not a big concern and I have seen no more difficulties then I see in other installations .
Roy Cooke sr. Royshomeinspection.com
Reply With Quote
  #12  
Old 6/4/06, 11:47 AM
Jason A. Sieg, CMI's Avatar
Jason A. Sieg, CMI Jason A. Sieg, CMI is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Davison, MI
Posts: 839
Default Re: Federal Pacific electrical panels

Quote:
Originally Posted by jpope
Those must be MI prices Jason. A new 100 amp service sets you back at least $1200 in these parts.

That's still a small price to pay as far as I am concerned.
You have got to be kidding!

I can go to any Home Depot or Lowes and buy a Square D for under $100.00


http://www.lowes.com/lowes/lkn?actio...VP5&lpage=none

Square D Company
100 Amp Main Breaker Panel Value Pack



Item #: 39032 Model: HOMVP5
$54.91

Contains: (1) 20 space 20 circuit panel main breaker panel and (5) 20AMP single pole circuit breakers
Indoor



Jason Sieg, CMI
Davison, MI
NACHI05091399


Knowing the current condition,
to make a wise decision.

President, Great Lakes-East Chapter
Join NACHI Great Lakes - East Chapter

http://mi.nachi.org/greatlakes-east/about.html
ssieg@gfn.org
Reply With Quote
  #13  
Old 6/4/06, 11:54 AM
Jason A. Sieg, CMI's Avatar
Jason A. Sieg, CMI Jason A. Sieg, CMI is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Davison, MI
Posts: 839
Default Re: Federal Pacific electrical panels

Square D Company
200 Amp 30/40 Main Breaker Panel Value Pack



Item #: 39537 Model: HOMVP9$119.00
30 space, 40 circuit
Contains: (1) HOM3040M200TC panel, (1) equipment ground bar, (6) 15AMP and (6) 20AMP single pole, (1) 30 AMP and (1) 50AMP two pole circuit breakers
For indoor use


http://www.lowes.com/lowes/lkn?actio...VP9&lpage=none


GE
32 Space, 200 Amp, Main Breaker Load Center Contractor Kit



Item #: 103821 Model: TM3220CCU2K$110.00
Interchanging of GE breakers and load centers with other manufacturer's products voids GE's life time warranty
UL listed
200 amp, 32 circuits
Single phase, 3 wire, 120/240/volts AC
Includes the following 1" breakers: ten single pole 20 amp, one double pole 30 amp and one double pole 50 amp
Uses TGK32 ground bar kit if necessary
Factory installed main breaker

http://www.lowes.com/lowes/lkn?actio...U2K&lpage=none



Cutler-Hammer
200 Amp Indoor Load Center Value Pack



Item #: 101588 Model: BR3040B200V$99.00
30 space, 40 circuits
Type BW 10kAIC breaker
Aluminum bus
NEMA 1- indoor use
Includes BR3040B200 loadcenter, With 5-BR120 and 1-BR230 branch breakers

http://www.lowes.com/lowes/lkn?actio...00V&lpage=none



Jason Sieg, CMI
Davison, MI
NACHI05091399


Knowing the current condition,
to make a wise decision.

President, Great Lakes-East Chapter
Join NACHI Great Lakes - East Chapter

http://mi.nachi.org/greatlakes-east/about.html
ssieg@gfn.org
Reply With Quote
  #14  
Old 6/4/06, 12:03 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: Federal Pacific electrical panels

Around here it would be at least $1,200 for a qualified electrician to upgrade to 150 to 200 amp.
Reply With Quote
  #15  
Old 6/4/06, 12:20 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Federal Pacific electrical panels

Quote:
Originally Posted by jsieg
If they want it replaced that is between them and the seller. In either case it doesn't cost that much to have that done. $100.00 to 200.00 for supplies & labor. A good electrician should be able to change over the panel in under 3-4 hours unless there are some major problems with the original wiring.

Peace of Mind for under $500.00. Am I wrong?

Glad I am not working in YOUR state........NOT worth my time for $ 500.00 bucks.......a DIYer maybe..not a REAL contractor...

Try about $ 900 to $ 1,500 bucks.........and depending on the amount of work....5-6 hours.....



Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Federal Pacific electrical panels Harvey W. Kelly Electrical Inspections 3 9/6/07 10:55 AM
Federal Pacific Panels cbottger Electrical Inspections 26 8/22/06 12:43 PM
Electrical Safety Information jtedesco1 Electrical Inspections 0 2/19/06 1:48 AM
Federal Pacific Panels gbeaumont Electrical Inspections 7 1/2/06 12:55 PM


All times are GMT -4. The time now is 3:35 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts