Default Federal Pacific fuse panel

Is there any concern with the Federal Pacific FUSED panels or is it just the breaker panels that are of concern?

Thanks in advance!
Reply With Quote
  #2  
Old 6/27/07, 9:30 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Federal Pacific fuse panel

Nope. The problem is with the Stab-lok brand, breakers and panels.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 6/28/07, 1:15 AM
bwooddell bwooddell is offline
New User
 
Join Date: Feb 2006
Location: Kuna, ID
Posts: 51
Please Note: bwooddell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Federal Pacific fuse panel

Thanks Jeff!
Reply With Quote
  #4  
Old 6/28/07, 1:02 PM
dchew dchew is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: San Ramon, CA
Posts: 317
Default Re: Federal Pacific fuse panel

On the other hand, if it has fuses in it and its made by FPE, it must be pretty old. A recommendation for upgrading is appropriate due to "obsolete equipment".
Reply With Quote
  #5  
Old 6/28/07, 1:39 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Federal Pacific fuse panel

Why is "old" necessarily "obsolete". Fuses are a reliable method of providing overcurrent protection, perhaps better than breakers. The only down side is if you are blowing them a lot. That is an indication of bigger problems that should be addressed. A panel full of old dusty fuses is a good indicator that the service is adequate for the connected load.
Just remember a breaker usually fails closed, where a fuse can only fail open, a much safer condition. That is particularly true if the fuses are type S. If I was going to recomend anything about a fuse panel that was large enough for the load, it would be that S adapters should be installed if they are not there already.
BTW that is the current code requirement. I can put in a brand new fuse panel today on new construction if it has type S fuse adapters.

Quote:
240.52 Edison-Base Fuseholders.
Fuseholders of the Edison-base type shall be installed only where they are made to accept Type S fuses by the use of adapters.
Reply With Quote
  #6  
Old 6/29/07, 4:58 PM
dchew dchew is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: San Ramon, CA
Posts: 317
Default Re: Federal Pacific fuse panel

Usually, I take the approach that if it's working, leave it alone. However from the original description, the wiring in the house is probably pretty old and may not have enough capacity to service the needs of a family today.

The last time I saw a fusebox instead of a subpanel, everything was running off of 4 fuses and had obviously been blowing them (a tall stack of spare fuses were sitting inside the box). The wiring was old, no grounds, etc.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Federal Pacific Fuse Panel kmccullough Electrical Inspections 6 10/25/07 6:33 PM
Federal Pacific 200 Amp Fuse Panel jhagarty Electrical Inspections 2 1/24/07 1:12 AM
Federal Pacific Service Panel jweeams Electrical Inspections 18 9/14/06 8:57 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 10:26 PM


All times are GMT -4. The time now is 8:51 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts