I looked at a house yesterday that had a Federal Pacific Panel. I noted that 3 breakers had been replaced with Challenger breakers. Are Challenger breakers approved replacement breakers in a Federal Pacific Panel?

Any insights will be greatly appreciated.

Thanks

Jonathan




Jonathan N. Leahy
President
A Rock Solid Home Inspection, LLC.
www.arocksolidhome.com
303-718-7779
Residential Home Inspections, Radon Testing, Mold Inspections
Reply With Quote
Need a home inspection in Ohio? Check out InterNACHI's listing of Ohio certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 12/5/11, 8:20 PM
wsiegel wsiegel is online now
Active Poster
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 2,649
Please Note: wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Federal Pacific Panel

No, they are not.
Reply With Quote
  #3  
Old 12/5/11, 9:34 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,109
Default Re: Federal Pacific Panel

Although I would take Challenger breakers over Federal Pacific any day.

A Federal Pacific Electric "Stab-Lok" service panel is in use. These panels and breakers are a latent hazard and can fail to trip in response to over current, leading to electrical fires. The breakers may also fail to shut off internally even if the toggle is switched to "off." Some double-pole (240-Volt) FPE circuit breakers and single-pole FPE Stab-Lok circuit breakers simply do not work safely. There are other panel-defects independent of the breaker problems, panel and panel-bus fires and arcing failures in some equipment. The failure rates for these circuit breakers were and still are significant. In some cases failure to trip occurs 60% of the time - a serious fire and electrical shock hazard. Failures are documented in the CPSC study and by independent research. Have a licensed electrician make further evaluation and corrections as needed.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #4  
Old 12/5/11, 9:51 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,620
Default Re: Federal Pacific Panel

Quote:
Originally Posted by kwood View Post
Although I would take Challenger breakers over Federal Pacific any day.

A Federal Pacific Electric "Stab-Lok" service panel is in use. These panels and breakers are a latent hazard and can fail to trip in response to over current, leading to electrical fires. The breakers may also fail to shut off internally even if the toggle is switched to "off." Some double-pole (240-Volt) FPE circuit breakers and single-pole FPE Stab-Lok circuit breakers simply do not work safely. There are other panel-defects independent of the breaker problems, panel and panel-bus fires and arcing failures in some equipment. The failure rates for these circuit breakers were and still are significant. In some cases failure to trip occurs 60% of the time - a serious fire and electrical shock hazard. Failures are documented in the CPSC study and by independent research. Have a licensed electrician make further evaluation and corrections as needed.
Sorry I disagree with your post .
ESA does not say this and they are still manufactured in Canada.

Roy



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #5  
Old 12/6/11, 7:30 AM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,109
Default Re: Federal Pacific Panel

I know Roy! You still can be my friend. LOL



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #6  
Old 12/6/11, 3:00 PM
Gary Farnsworth Gary Farnsworth is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Olathe, KS
Posts: 3,715
Default Re: Federal Pacific Panel

Inform, document, refer, collect the check, done. IMO, I recommend replacement on all FPE panels. I just let the buyer know, refer him/her to web sites, let them decide.



CMI, CPI, KS #0110-0094 Termite #16601
KS Radon #KS-MS-0027
BBB A+ Accredited Business
Serving the Greater Kansas City Metro Area
Eastern Kansas/Western Missouri
http://www.metrospeckc.com
"If opportunity doesn't knock, build a door"--Milton Berle
Reply With Quote
  #7  
Old 12/6/11, 8:47 PM
Chad Norlen, CPI's Avatar
Chad Norlen, CPI Chad Norlen, CPI is offline
InterNACHI Member
 
Join Date: Nov 2011
Location: American Falls, ID
Posts: 232
Default Re: Federal Pacific Panel

Possibly a dumb question, but... The names "Federal Pacific" and "Stab-Lok" seem to be used interchangeably. Are there FPE panels that are NOT Stab-Loks that are not problematic?



Chad Norlen
SEI Inspections
InterNACHI Member

Certified Professional Inspector
HVAC Journeyman - State of Idaho
EPA Certified Universal Technician
Reply With Quote
  #8  
Old 12/6/11, 9:04 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: Federal Pacific Panel

Quote:
Originally Posted by wsiegel View Post
No, they are not.

Is that even possible??




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
  #9  
Old 12/6/11, 9:08 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,109
Default Re: Federal Pacific Panel

It is the way the breakers are installed on the bus bar.
They are stabbed into position and they are supposed to lock.
If you have opened a panel with FP with SL and had the breakers fall out. You have just experienced the locking mechanism failure.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #10  
Old 12/6/11, 9:58 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Federal Pacific Panel

Quote:
Originally Posted by kwood View Post
It is the way the breakers are installed on the bus bar.
They are stabbed into position and they are supposed to lock.
If you have opened a panel with FP with SL and had the breakers fall out. You have just experienced the locking mechanism failure.
That's what Sean is stating, how is it possible to install Challenger breakers?



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #11  
Old 12/7/11, 1:19 AM
Jonathan N. Leahy Jonathan N. Leahy is offline
InterNACHI Member
 
Join Date: Sep 2007
Location: Westminster, CO
Posts: 98
Default Re: Federal Pacific Panel

I did advise the client of the issues with Federal Pacific panels and advised to have an electrical contractor fully evaluate the panel.

Thanks

Jonathan




Jonathan N. Leahy
President
A Rock Solid Home Inspection, LLC.
www.arocksolidhome.com
303-718-7779
Residential Home Inspections, Radon Testing, Mold Inspections
Reply With Quote
  #12  
Old 12/9/11, 10:44 AM
Mark L. Brown's Avatar
Mark L. Brown Mark L. Brown is offline
InterNACHI Member
 
Join Date: Jul 2007
Location: Dension, TX
Posts: 41
Default Re: Federal Pacific Panel

You did not mentioned, but were branch circuits connected to the challenger breakers, or were they simply plugging missing twist outs? The challenger breakers I've seen did not mechanically appear possible to connect to the buss.

You are correct to point this out at any rate, as the breakers are improper for this panel.
Reply With Quote
  #13  
Old 12/9/11, 10:52 AM
Mark L. Brown's Avatar
Mark L. Brown Mark L. Brown is offline
InterNACHI Member
 
Join Date: Jul 2007
Location: Dension, TX
Posts: 41
Default Re: Federal Pacific Panel

Jonathan, was the tag on the inside of the panel showing a 'list of compatible breakers' there? A lot of older panels are missing these labels, but it is a good place to start.
Reply With Quote
Need a home inspection in Ohio? Check out InterNACHI's listing of Ohio certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 12/9/11, 11:13 AM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is online now
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: Federal Pacific Panel

Quote:
Originally Posted by mbrown5 View Post
Jonathan, was the tag on the inside of the panel showing a 'list of compatible breakers' there? A lot of older panels are missing these labels, but it is a good place to start.
One problem with an older panel is that at the time the panel was manufactured, many now compatible breakers did not exist.
Reply With Quote
  #15  
Old 12/9/11, 11:32 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Federal Pacific Panel

I seem to recall Challenger breakers that were specifically made for use in FPE Stab-Lok panels. I will check into it a bit further, but I'm almost certain they exist.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
federal pacific panel box pcavalcante Electrical Inspections 5 4/7/11 3:53 PM
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 7:28 PM
Main panel...recommendation ? dnasser Electrical Inspections 6 11/22/09 9:55 PM
Federal Pacific nbhi Electrical Inspections 5 11/23/08 9:34 AM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 9:32 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts