Default Federal Pacific Service Panel

I came across a Federal Pacific panel this evening while doing an inspection. I was taught to never open one of these because the can be a hazard/liability. What is the proper procedure telling the client what to do about this situation, as well as why it's not good to open a F.P panel?
Reply With Quote
  #2  
Old 9/14/06, 12:06 AM
nwagner's Avatar
nwagner nwagner is offline
InterNACHI Member
 
Join Date: May 2006
Location: Baraboo, WI
Posts: 2,948
Default Re: Federal Pacific Service Panel

I would explain that these panels are notorious for freezing breakers and arching; dangerous conditions that could and have resulted in house fires. I'd explain that I wouldn't feel safe opening a known defective panel and that I wouldn't want to provide a false sense of security by personally inspecting such a panel. I'd strongly urge the client to have a licensed Master Electrician evaluate the panel and would very strongly recommend that the panel be replaced and upgraded to a 200 amp service (might as well, won't cost much more).
Reply With Quote
  #3  
Old 9/14/06, 12:07 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 7,708
Send a message via Yahoo to jfunderburk
Default Re: Federal Pacific Service Panel

I open them unless I see something extraordinarily hazardous. How will you know the wiring type (copper or aluminum) if you don't?



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #4  
Old 9/14/06, 12:22 AM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,862
Default Re: Federal Pacific Service Panel

Quote:
Originally Posted by jfunderburk
I open them unless I see something extraordinarily hazardous. How will you know the wiring type (copper or aluminum) if you don't?
I do what Joe does.

http://www.inspect-ny.com/fpe/fpestlouis.htm
Reply With Quote
  #5  
Old 9/14/06, 12:25 AM
tdutt tdutt is offline
Active Poster
 
Join Date: Dec 2005
Location: Lake Oswego, OR
Posts: 155
Please Note: tdutt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Federal Pacific Service Panel

Gerry Beaumont has created an electrical course that may be of help to you. Go to the Education section, click Education, then click Online Electrical Course, then Service Panels, then Problem Panels. You'll get some information on the "Stab-lok" brand of Federal Pacific Panels.

I took an electrical course from Gerry at last year's NACHI convention in Florida and he gave us a great tip in regard to inspecting these panels. When unscrewing the dead front cover if you feel the breakers pushing against the dead front as you are removing it, then stop, tighten the dead front cover and defer to a licensed electrician. This happened to me a couple of months later on the only FPE "Stab-Lok" panel I've had the pleasure of inspecting. I was really glad I didn't open that thing up and have circuit breakers popping out. I explained the situation to the client, who had a licensed electrican remove the dead front and inspect the panel and stated everything was fine.

Another good resource for home inspectors is the book Electrical Inspection of Existing Dwellings by Hansen, Kardon, and Casey.
Reply With Quote
  #6  
Old 9/14/06, 12:36 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Federal Pacific Service Panel

Quote:
Originally Posted by bkelly2
I do what Joe does.
As do I.

This one was from today.

FPE Stab-lok, scorched/burnt bus bars, one breaker falling out, rust/moisture damage to another breaker and feeders so close to the dead-front, it's difficult to remove or replace without contacting them.

All in all, not bad for FPE
Attached Thumbnails
federal-pacific-service-panel-hpim8286.jpg   federal-pacific-service-panel-hpim8287.jpg   federal-pacific-service-panel-hpim8288.jpg   federal-pacific-service-panel-hpim8289.jpg   federal-pacific-service-panel-hpim8290.jpg  




IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #7  
Old 9/14/06, 12:43 AM
Patrick Bolliger's Avatar
Patrick Bolliger Patrick Bolliger is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Chicago, IL
Posts: 890
Send a message via Skype™ to pbolliger
Default Re: Federal Pacific Service Panel

Wow Jeff,

I am surprised you are not the first to answer on this post being the "FPE Man" you are...
Must be busy unlike the rest of us...
Reply With Quote
  #8  
Old 9/14/06, 12:47 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Federal Pacific Service Panel

Quote:
Originally Posted by pbolliger
Wow Jeff,

I am surprised you are not the first to answer on this post being the "FPE Man" you are...
Must be busy unlike the rest of us...
Missed it by about 40 minutes Looks like others covered it well.

It has been a busy week so far.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #9  
Old 9/14/06, 1:05 PM
jhugenroth jhugenroth is offline
InterNACHI Member
 
Join Date: May 2004
Location: Fresno, CA
Posts: 1,152
Please Note: jhugenroth is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Federal Pacific Service Panel

Quote:
Originally Posted by tdutt
...This happened to me a couple of months later on the only FPE "Stab-Lok" panel I've had the pleasure of inspecting.....I explained the situation to the client, who had a licensed electrican remove the dead front and inspect the panel and stated everything was fine.
Everything was fine? EVERY sparky I've ever talked to about these
says replace them, and that's what I recommend to my clients.

Luckily they are pretty scarce around here, but I had a fun one about a year ago, when I looked in the common laundry room of a 16 unit apt. building, and there was an FPE panel. Naturally all of the units had an FPE sub. Other than that apt. inspection, I've only seen about six others.
Reply With Quote
  #10  
Old 9/14/06, 1:57 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 7,708
Send a message via Yahoo to jfunderburk
Default Re: Federal Pacific Service Panel

I had an older electrician tell me recently FPE was his favorite manufacturer of panels. But then, I woudn't trust him to screw in a light bulb.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #11  
Old 9/14/06, 3:11 PM
tdutt tdutt is offline
Active Poster
 
Join Date: Dec 2005
Location: Lake Oswego, OR
Posts: 155
Please Note: tdutt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Federal Pacific Service Panel

Quote:
Originally Posted by jhugenroth
Everything was fine? EVERY sparky I've ever talked to about these
says replace them, and that's what I recommend to my clients.

Luckily they are pretty scarce around here, but I had a fun one about a year ago, when I looked in the common laundry room of a 16 unit apt. building, and there was an FPE panel. Naturally all of the units had an FPE sub. Other than that apt. inspection, I've only seen about six others.
I was a little surprised. I explained in my report the potential problems with these panels, explained the condition of the breakers pushing against the dead front, and told her it would be best to have a licensed electrician open up that panel and look it over. The electrician she chose was a friend of hers, and he told her everything looked fine. It's my job to educate the client about the potential problems and then recommend further evaluation by a licensed electrician (I stress that it would be good to choose an older electrician with years of experience with older equipment). If I've educated the client about the potential for problems, and a specialist says there is no problem with a particular piece of equipment, then I've done my job. I'm not going to tell her to replace the panel when a specialist says that it's fine, the liability is now his.

Last edited by tdutt; 9/14/06 at 4:25 PM..
Reply With Quote
  #12  
Old 9/14/06, 4:02 PM
John Bowman's Avatar
John Bowman John Bowman is offline
Active Poster
 
Join Date: Dec 2003
Location: ROME, PA
Posts: 2,204
Please Note: jbowman is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Federal Pacific Service Panel

Anyone know if there is more current information from the CPSC other than this 1983 statement?

http://www.cpsc.gov/cpscpub/prerel/prhtml83/83008.html
Reply With Quote
  #13  
Old 9/14/06, 4:10 PM
jhugenroth jhugenroth is offline
InterNACHI Member
 
Join Date: May 2004
Location: Fresno, CA
Posts: 1,152
Please Note: jhugenroth is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Federal Pacific Service Panel

Quote:
Originally Posted by jbowman
Anyone know if there is more current information from the CPSC other than this 1983 statement?

http://www.cpsc.gov/cpscpub/prerel/prhtml83/83008.html
John,
As far as I know, that's the latest word.
Reply With Quote
  #14  
Old 9/14/06, 4:21 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 7,708
Send a message via Yahoo to jfunderburk
Default Re: Federal Pacific Service Panel

Quote:
Originally Posted by tdutt
I explained in my report the potential problems with these panels, explained the condition of the breakers pushing against the dead front, and told her it would be best to have a licensed electrician open up that panel and look it over.
Did you also recommend replacement? Did you say anything like, "The FPE Stab-Lok service equipment panel is considered a safety hazard. The hazards associated with this manufacturer have been documented by the Consumer Product Safety Commission and by industry experts. A high percentage of FPE Stab-Lok breakers have failed to open under over-current conditions. Replacement is advised for safety reasons."

Simply telling the client to have an electrician open the panel and examine it is not the best recommendation in my opinion.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #15  
Old 9/14/06, 4:32 PM
John Bowman's Avatar
John Bowman John Bowman is offline
Active Poster
 
Join Date: Dec 2003
Location: ROME, PA
Posts: 2,204
Please Note: jbowman is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Federal Pacific Service Panel

Quote:
Originally Posted by jfunderburk
The hazards associated with this manufacturer have been documented by the Consumer Product Safety Commission...
Joe,

Where do we find this documentation? My post above is the only thing I could find from the CPSC on this panel.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Federal Pacific Fuse Panel kmccullough Electrical Inspections 6 10/25/07 6:33 PM
Federal Pacific fuse panel bwooddell Electrical Inspections 5 6/29/07 4:58 PM
Federal Pacific 200 Amp Fuse Panel jhagarty Electrical Inspections 2 1/24/07 1:12 AM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 10:26 PM


All times are GMT -4. The time now is 9:08 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts