Default Federal Pacific(stab-lock) comment?

Hello Everyone.. Does any one have a comment for the Fed Pacific panels. I haven't seen one in a while and was curious how you all write them up! I always recommend further evaluation by a sparky, but I am curious to see if anyone goes into depth with their comment!

Thanks in advance,
Chris



Christopher Rich
A Closer Look Home Inspections, LLC
609-802-2001
www.ACloserLookHomeInspectionsNJ.com
ACloserLookHomeInspections@comcast.net
Reply With Quote
  #2  
Old 3/26/08, 11:18 PM
Jeffrey S. Campbell's Avatar
Jeffrey S. Campbell Jeffrey S. Campbell is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Pittston, ME
Posts: 817
Send a message via AIM to jcampbell Send a message via MSN to jcampbell Send a message via Yahoo to jcampbell
Default Re: Federal Pacific(stab-lock) comment?

The panel was manufactured by Federal Pacific Electric Company and employs Stablok breakers and other components that have been alleged to be defective. However, the panel is old and the company is now out of business, and although field reports of defects and dangers were never apparently substantiated by laboratory tests they have been numerous and serious enough for us to recommend either upgrading the panel or seeking a second opinion. Also, you can learn more about this issue from Dan Friedman at www.inspect-ny.com/fpe/fpepanel.htm.



Jeff Campbell
Campbell Property Inspections
http://www.maineshomeinspector.com
Pittston, Maine
NACHI04013010
Reply With Quote
  #3  
Old 3/26/08, 11:25 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,098
Default Re: Federal Pacific(stab-lock) comment?

....
Quote:
The home is equipped with a Federal Pacific brand electrical panel which have been shown to be problematic. Independent laboratory testing indicates some models of these panels are prone to problems that can lead to failures of the panel, fire hazards, lack of proper protection of circuits and other serious issues. I recommend a careful, detailed analysis of these panels by a licensed electrician to determine if any corrective action is needed.
Reply With Quote
  #4  
Old 3/26/08, 11:29 PM
Jeffrey S. Campbell's Avatar
Jeffrey S. Campbell Jeffrey S. Campbell is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Pittston, ME
Posts: 817
Send a message via AIM to jcampbell Send a message via MSN to jcampbell Send a message via Yahoo to jcampbell
Default Re: Federal Pacific(stab-lock) comment?

I don't want to stir anything up but i was once corrected in that no all Fed Pacific panels are problematic... but rather the Stab-Lok variety... Is that correct anyone? Sparkies?



Jeff Campbell
Campbell Property Inspections
http://www.maineshomeinspector.com
Pittston, Maine
NACHI04013010
Reply With Quote
  #5  
Old 3/26/08, 11:30 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,098
Default Re: Federal Pacific(stab-lock) comment?

That's why I word mine the way I do.
Reply With Quote
  #6  
Old 3/26/08, 11:43 PM
cmeyer cmeyer is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: westfield, NJ
Posts: 5
Please Note: cmeyer is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Federal Pacific(stab-lock) comment?

Verbiage was borrowed some time ago from another member (possibly the Pope?)

The home is currently equipped with a Federal Pacific stab-Lok load center which are considered problematic by industry professionals due to their high failure rate. Failure of any component within the electrical system can result in fire and/or electrocution. Recommend evaluation by a licensed electrician.
Reply With Quote
  #7  
Old 3/27/08, 12:14 AM
Joe Hugenroth Joe Hugenroth is offline
InterNACHI Member
 
Join Date: May 2004
Location: Fresno, CA
Posts: 755
Default Re: Federal Pacific(stab-lock) comment?

I think they have a bad enough history to justify recommending they be replaced.
Reply With Quote
  #8  
Old 3/27/08, 12:36 AM
Mark Nahrgang's Avatar
Mark Nahrgang Mark Nahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Saint Peters, MO
Posts: 3,947
Default Re: Federal Pacific(stab-lock) comment?

There is a Federal Pacific Electric “Stab-Lock” service panel in the house. There are some studies that show that its 220-volt circuit breakers fail to trip in response to an over-current or a short circuit. Since the Consumer Products Safety Commission has not issued a formal product recall, we cannot definitively call these panels defective. We recommend, for your peace of mind, to consult a qualified electrical contractor to get their opinion on this matter. There does not appear to be any current concerns in relation to currently installed panel.
Reply With Quote
  #9  
Old 3/27/08, 12:44 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: Federal Pacific(stab-lock) comment?

Quote:
Originally Posted by jcampbell
I don't want to stir anything up but i was once corrected in that no all Fed Pacific panels are problematic... but rather the Stab-Lok variety... Is that correct anyone? Sparkies?
That is correct.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #10  
Old 3/27/08, 2:50 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
Active Poster
 
Join Date: Jul 2003
Location: East Northport, NY
Posts: 741
Default Re: Federal Pacific(stab-lock) comment?

Quote:
Originally Posted by jcampbell
I don't want to stir anything up but i was once corrected in that not all Fed Pacific panels are problematic... but rather the Stab-Lok variety...
See this article ... IMO one of the best on the issue written so far.

http://www.codecheck.com/pdf/electri...%20Nov2003.pdf



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #11  
Old 3/27/08, 4:13 PM
Steven C. Waskewicz's Avatar
Steven C. Waskewicz Steven C. Waskewicz is offline
InterNACHI Member
 
Join Date: Apr 2006
Location: Colorado Springs, CO
Posts: 1,208
Default Re: Federal Pacific(stab-lock) comment?

Nice Article Robert, thanks a bunch. I'll provide that document with my reports
if/when I come across more of these, as I've seen before.



Steven Waskewicz
Rest Assured Inspection Services, LLC.
12615 Halleluiah Trail
Elbert, Colorado 80106
Office 719-510-7703 mobile all the time
Fax 719-495-7166
Serving Colorado Springs, and surrounding areas.

www.restassuredinspection.com
s_waskewicz@msn.com
NACHIiid=NACHI06032370



Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Federal Reserve advisory group warns foreclosures to get worse jburkeson1 Misc. Discussion 2 3/9/07 8:10 PM
Ottawa to stiffen radon guidelines. gromicko Canadian Inspectors 1 8/16/06 6:28 AM


All times are GMT -4. The time now is 2:15 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts