Default Federal Pacific Stabloc Panel Found

So I found this Federal Pacific Panel with Stab Loc circuits while doing a 4 point on a 1955 home in Tampa Bay. The Insurance Agent said I needed to give the remaining "life expectancy" of all four points. What would you have answered for the Electrical?
I'll try to attach photo's for your viewing pleasure:

Panel
Panel Open
Above Panel

Can you notice any other interesting items in this panel?




Lee Curtis - Home Inspector
Revealing the Secrets of Your Home!
CGC1519195 - HI3222 - InterNACHI #11011001
Lee@CurtisHomeInspections.com
www.CurtisHomeInspections.com

www.CurtisHomeDesign.com
Reply With Quote
Need a home inspection in Utah? Check out InterNACHI's listing of Utah certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 5/10/11, 4:18 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,252
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Federal Pacific Stabloc Panel Found

I see no connector/raceway for the service entrance conductors. And it's a split-bus panel.

Reply With Quote
  #3  
Old 5/10/11, 7:06 PM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,636
Default Re: Federal Pacific Stabloc Panel Found

"Remaining Life Expectancy ?"

.....30 seconds or 30 feet
whichever comes first..




Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #4  
Old 5/10/11, 7:11 PM
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 5,482
Default Re: Federal Pacific Stabloc Panel Found

FWIW--it's not the panel per se that is the problem here--it is the way it's installed (it usually is).

Refer to a licensed electrician for repair.



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
  #5  
Old 5/10/11, 7:29 PM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,636
Default Re: Federal Pacific Stabloc Panel Found

Quote:
Originally Posted by jwilliams4 View Post
FWIW--it's not the panel per se that is the problem here--it is the way it's installed (it usually is).

Refer to a licensed electrician for repair.
It is a Stab-Lok...
What about this particular panel do you find
NOT Warranting a Recommendation
for Replacement?



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #6  
Old 5/10/11, 7:31 PM
Harry D. Vandermeulen Harry D. Vandermeulen is offline
InterNACHI Member
 
Join Date: Sep 2010
Location: Sarasota, FL
Posts: 57
Default Re: Federal Pacific Stabloc Panel Found

Looks like white ungrounded conductors as well
Reply With Quote
  #7  
Old 5/10/11, 7:46 PM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,636
Default Re: Federal Pacific Stabloc Panel Found

Quote:
Originally Posted by jhagarty View Post
It is a Stab-Lok...
What about this particular panel do you find
NOT Warranting a Recommendation
for Replacement?
I guess the IR Camera found all breakers within acceptable temp range...
so...
it must be good




Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #8  
Old 5/10/11, 7:49 PM
Ken Brittain Ken Brittain is offline
New User
 
Join Date: Apr 2011
Location: Harrisburg North Carolina
Posts: 9
Please Note: Ken Brittain is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Federal Pacific Stabloc Panel Found

Is that melted insulation around the SE cables at the lugs?

I would not speculate on life expectancy as mentioned evaluate by a qualified specialist and/or recommend replacement. I'm sure there is some standard write up for these.

Glad you were able to open it with out any issues. The safety aspect can be a reason for not inspecting
Reply With Quote
  #9  
Old 5/12/11, 11:49 PM
agallatin agallatin is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Trail BC
Posts: 194
Default Re: Federal Pacific Stabloc Panel Found

That's a pretty amazing wiring job ! And it's worked for how many years ?



galaxyhomeinspections.com



An amateur built the Ark !
Professionals built the Titanic !
Reply With Quote
  #10  
Old 5/16/11, 8:40 PM
George P. Wells, CMI's Avatar
George P. Wells, CMI George P. Wells, CMI is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Michigan
Posts: 554
Send a message via Skype™ to gwells
Default Re: Federal Pacific Stabloc Panel Found

Quote:
Originally Posted by lcurtis1 View Post
So I found this Federal Pacific Panel with Stab Loc circuits while doing a 4 point on a 1955 home in Tampa Bay. The Insurance Agent said I needed to give the remaining "life expectancy" of all four points. What would you have answered for the Electrical?
When my wife had breast cancer, she and I asked her oncologist what her expected life expectancy was. He refused to give us a direct answer. Instead, he said he would give us the published statistics that are available to anyone. However, he said, he would not speculate on her life expectancy. He went on to say that regardless of the odds, she should follow his advice and get the treatment he recommended. She did. Statistically, she had two years. That was 13 years ago. She is still alive and is doing well.

At exactly the same time, when my mother had renal failure, we asked her endocrinologist what her expected life expectancy was. He too refused to give us a direct answer. Instead, he said he would give us the published statistics that are available to anyone. He would not speculate on her life expectancy. He went on to say that regardless of the odds, she should follow his advice and get the treatment he recommended. She did. Statistically, she had two years. She died two months later.

Have the real estate agent call me.



BestInspectors.Net
& Real Estate Training Academy

Inspection Report Software for
Windows - iOS - Mac - Android

Continuing Education
Home and Commercial Building Inspection - Skilled Trades – Real Estate – Appraisal – NFPA 921

http://www.bestinspectors.net

est. 1992

Last edited by gwells; 5/16/11 at 8:49 PM..
Reply With Quote
  #11  
Old 5/17/11, 11:11 AM
George P. Wells, CMI's Avatar
George P. Wells, CMI George P. Wells, CMI is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Michigan
Posts: 554
Send a message via Skype™ to gwells
Default Re: Federal Pacific Stabloc Panel Found

Quote:
Originally Posted by Ken Brittain View Post
Is that melted insulation around the SE cables at the lugs?
It is probably an oxide inhibitor.



BestInspectors.Net
& Real Estate Training Academy

Inspection Report Software for
Windows - iOS - Mac - Android

Continuing Education
Home and Commercial Building Inspection - Skilled Trades – Real Estate – Appraisal – NFPA 921

http://www.bestinspectors.net

est. 1992
Reply With Quote
  #12  
Old 5/18/11, 9:58 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Federal Pacific Stabloc Panel Found

Quote:
Originally Posted by jhagarty View Post
It is a Stab-Lok...
What about this particular panel do you find
NOT Warranting a Recommendation
for Replacement?
Are you calling it out because it is a "Stab-Lok" as a design flaw.....Federal Pioneer ( Schnieder- Makers of Square D) would disagree as would I if installed properly. I would call it out due to age and life expectancy on the OCPD's and the fact the branch circuit overcurrent devices are not reliable based on the CPSC's findings ( while not totally reliable since they kinda took the low road, they still originally issued the report anyway)....give them the option to replace the breakers with modern replacements that are properly UL Listed....or the option to replacement as a solution.

Then defer it to a licensed electrical contractor and let the client make the choice based on your educated advice...


P.S. I even have one more solution for you inspectors......Eaton Cutler Hammer makes an insert that replaced the entire panelboard in the older FPE panels...the "GUTS" are replaced with UL Listed and Approved inserts designed to go into those panels and it holds modern breakers....might be the BEST solution you can give them as the enclosure is typically fine.....just replace the panelboard "GUTS"......it is an option, it is cost effective and it is UL approved and eaton will create a cover that matches the screws perfectly on the older FPE enclosure for a nice finish...



Paul W. Abernathy

Last edited by pabernathy; 5/18/11 at 10:02 PM..
Reply With Quote
  #13  
Old 5/18/11, 10:05 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Federal Pacific Stabloc Panel Found

lol..I feel like I am selling Eaton Products.......well I don't consult for them anymore so I still believe in their stuff and those inserts are awesome...I have used them on two specific occasions and it worked great..... What is the cost....well it is less than a totally new service change since you are only removing the paneboard but overall cost is dependant on the electrical contractor doing the job...again only a recommendation as cost is not part your job...just recommendations and let them choose.



Paul W. Abernathy
Reply With Quote
Need a home inspection in Utah? Check out InterNACHI's listing of Utah certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 5/24/11, 12:56 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Federal Pacific Stabloc Panel Found

Remaining life - zero to none ...

For an FPE panel call for an evaluation by an electrical specialist, and repair or replacement as needed, based on a known history of problems.

It's more than just unreliable breakers in the FPE panels. There are also issues with the breaker attachment to the bus bar and some panels did not have enough room for wires/bends, but thats not as significant as breakers that may not trip or a poor bus connection.

http://www.cahillinspection.com/imag...nsen%20FPE.pdf
http://www.inspectapedia.com/fpe/fpepanel.htm

Keep it simple and let an electrician decide the best course of action.

JMO & 2-Nickels



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...

Last edited by roconnor; 5/30/11 at 11:09 AM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Federal Pacific Panel - Manf in Raleigh NC crichiii Electrical Inspections 6 7/15/08 12:58 AM
Federal Pacific Panels cbottger Electrical Inspections 26 8/22/06 12:43 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM