Default Feeder Cables

Hey folks,
I don't usually see individual feeder cables supplying a panel board from the SE. This just doesn't look right. Shouldn't these cables be installed in a conduit? Any help would be appreciated.
Attached Thumbnails
feeder-cables-hpim3779-small-.jpg.JPG
Views:	142
Size:	55.6 KB
ID:	3061   feeder-cables-hpim3780-small-.jpg.JPG
Views:	106
Size:	60.5 KB
ID:	3062   feeder-cables-hpim3782-small-.jpg.JPG
Views:	103
Size:	63.6 KB
ID:	3063   feeder-cables-hpim3778-small-.jpg.JPG
Views:	152
Size:	77.7 KB
ID:	3064  
Reply With Quote
  #2  
Old 4/23/06, 7:50 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Feeder Cables

IRC E3702.2.2
Cable installed parallel to framing members

Where cables are installed parallel to the sides of rafters, studs, or floor joists, guard strips and running boards shall not be required, and the installation shall comply with Table E3702.1.

I'd recommend stapling of these cables to the floor joists.

Last edited by dvalley; 4/23/06 at 7:53 AM..
Reply With Quote
  #3  
Old 4/23/06, 8:52 AM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Feeder Cables

Hi to all,

That whole installation is obviously a homeowner special and should be further evaluated by an electician.
  • Unattached wiring
  • Double tapped breaker (left side)
  • Neutral and ground on the same bus in a sub panel
Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #4  
Old 4/23/06, 9:46 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 7,708
Send a message via Yahoo to jfunderburk
Default Re: Feeder Cables

And somebody installed the insulation upside down.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #5  
Old 4/23/06, 9:47 AM
Pierre Belarge Pierre Belarge is offline
Active Poster
 
Join Date: Apr 2006
Posts: 202
Please Note: Pierre Belarge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Feeder Cables

Steven
I am not surprised anymore at how poorly some installations are. This ties in with aother post I made earlier about how the installations are possibly not being installed by electricians, and people who do not know what they are doing are really creating not just violations, but some serious hazards.

The wiring you are referring to is not "cables", they are conductors". You will be able to find them in table 310.13. You will also note the NEC and all other codes require conductors to be installed in one of the methods described in chapter 3. Those are open conductors and you are correct in stating they need to be installed inside one of the raceway types in chapter three.

You can also see in one of your photos, that the 100 amp 2-pole breaker is supplying a 3 conductor cable (copper). If that is supplying a subpanel, there is no neutral conductor installed with it.


I will not comment on any other part of buildings, but it is good to see the effort you are all making in trying to protect the consumer from the abominations we are seeing on the electrical threads.
Reply With Quote
  #6  
Old 4/23/06, 10:04 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,482
Default Re: Feeder Cables

Quote:
Originally Posted by jfunderburk
And somebody installed the insulation upside down.
What I thought too.
Reply With Quote
  #7  
Old 4/23/06, 5:06 PM
rrichards2 rrichards2 is offline
Active Poster
 
Join Date: Mar 2006
Location: SHARON, ON
Posts: 426
Please Note: rrichards2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Feeder Cables

Quote:
Originally Posted by dvalley
IRC E3702.2.2
Cable installed parallel to framing members

Where cables are installed parallel to the sides of rafters, studs, or floor joists, guard strips and running boards shall not be required, and the installation shall comply with Table E3702.1.

I'd recommend stapling of these cables to the floor joists.
I'm not sure that rule applies to to high amperage main feeds inside the house. I have only seen them run inside BX or in conduit and terminated inside the panel.
Reply With Quote
  #8  
Old 4/23/06, 6:17 PM
Bob Badger Bob Badger is offline
New User
 
Join Date: Dec 2003
Posts: 77
Please Note: Bob Badger is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Feeder Cables

Forget stapling these cables.

They are required to be in a raceway.
Reply With Quote
  #9  
Old 4/23/06, 10:23 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,482
Default Re: Feeder Cables

Quote:
Originally Posted by Bob Badger
Forget stapling these cables.

They are required to be in a raceway.
But that'll make it too hard to tap into them when we need a light in the attic.
Reply With Quote
  #10  
Old 4/24/06, 6:54 AM
Bob Badger Bob Badger is offline
New User
 
Join Date: Dec 2003
Posts: 77
Please Note: Bob Badger is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Feeder Cables

Quote:
Originally Posted by lkage
But that'll make it too hard to tap into them when we need a light in the attic.
It could be a very bright light......no pesky breakers to trip.
Reply With Quote
  #11  
Old 4/24/06, 8:14 AM
N5XL N5XL is offline
New User
 
Join Date: Jan 2006
Posts: 11
Please Note: N5XL is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Feeder Cables

The individual conductors that feed this sub really need to be in conduit.
I can't see any white tape on the neutral in the subpanel.
All of those breakers are different types. Are they allowed to be mixed in this panel?
Is this panel allowed to have tandem breakers or have they been modified to fit in this panel?
There is double lugging on the neutral bar on the right hand side.
There is a ground wire on the neutral bar on the right hand side.
Its too hard to see whats going on with that 100 amp breaker and the wires going to it...need a better pic to tell.
There may be double lugging on the middle breaker on the left hand side. If breaker is not rated for this, flag it...need a better pic to tell.
Take a closer look at the wires coming into the top of the panel. There are a lot there and I cant tell how they are secured...need a better pic to tell.

You've got enough there to justify a proper electrician fix this panel.
Reply With Quote
  #12  
Old 4/24/06, 10:47 AM
Steven Brewster Steven Brewster is offline
New User
 
Join Date: Aug 2005
Location: Southside, AL
Posts: 57
Please Note: Steven Brewster is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Feeder Cables

Sorry I haven't responded sooner to your posts. The owner of this home works for the power company and probably got these conductors from the utility. I think these conductors are utilized for service drops and should be in a conduit with a dwelling.

The AHJ in our area grandfathers 3 wire feeds to sub panels, I alway write it up.

I knew it just didn't look right and found several IRC code violations which resulted in my recommendation for evaluation/repair by a licensed electrician.

I really appreciate the opportunity to participate on this forum. It is and has always been a positive learning experience.

Thanks,
Steven
Reply With Quote
  #13  
Old 4/24/06, 12:18 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Feeder Cables

Quote:
Originally Posted by Steven Brewster
The AHJ in our area grandfathers 3 wire feeds to sub panels. . .
To the best of my knowledge, a "three-wire" feed has never been allowed (unless inside a metal raceway) for a load side panel. How can this be grandfathered? Four conductors have always been required.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net



Last edited by jpope; 4/24/06 at 12:46 PM..
Reply With Quote
  #14  
Old 4/24/06, 6:09 PM
Steven Brewster Steven Brewster is offline
New User
 
Join Date: Aug 2005
Location: Southside, AL
Posts: 57
Please Note: Steven Brewster is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Feeder Cables

Jeff,

Go figure, 1960 home with 100 amp service and SE located inside in a hallway (old fuse panel with disconnect- usually a Walker panel in this area), gets a service upgrade to 200 amps and the original panel becomes a sub off the new panel (now the SE) installed beneath the meter. Find it all the time and the AHJ and all electricians will tell you the 3-wire original panel is a grandfathered installation. In other words, they will not require a 4-wire feed be installed in the remote panel.

Now, if it is a new permitted installation of a remote panel, a 4-wire feed is required. But in actuality, I rarely find them done correctly.

Anyway, this panel should have been a 4-wire feed from the SE and I always write it up.
Reply With Quote
  #15  
Old 4/24/06, 7:00 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Feeder Cables

AL? Where is that? Alabama? Friggen Hillbillies


Call it what you will, but allowing that type of set-up is not grandfathering, it's just wrong. There should be an equipment grounding conductor and a neutral conductor.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Abandoned Cables in Commercial Buildings jtedesco1 Electrical Inspections 1 12/31/06 7:50 PM
Electric Panel Cables Color Code wrosario Electrical Inspections 5 7/8/06 11:48 AM
post tension cables jlybolt Structural Inspections 2 4/18/06 12:55 AM
Ceilings falling with wires in it. jsmith3 Interior Inspections 8 3/16/06 8:24 PM