Default Fire waiting to happen

Inspected a manufactured home yesterday where one of the water heater wires was not tight in the termination block of the water heater breaker. (was able to pull wire out of breaker) The wire had gotten so hot that several inches of insulation had melted away. Apparently the wire had been loose for a long time. Also observed a missing knockout on the bottom of the panel and was able to see the interior of the wall.
Attached Thumbnails
fire-waiting-happen-img_0030.jpg   fire-waiting-happen-img_0032.jpg  
Reply With Quote
  #2  
Old 2/3/07, 11:31 AM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Fire waiting to happen

Fire waiting to happen? That's a leap that I might not be willing to take, but it certainly deserves repair. The breaker should also be evaluated for replacement, because the interior components of the breaker will have heated in a similar manner as that visible section of conductor.
Reply With Quote
  #3  
Old 2/3/07, 11:58 AM
Tab M. Wilcox Tab M. Wilcox is offline
Active Poster
 
Join Date: Feb 2006
Location: Yuma, AZ
Posts: 165
Please Note: Tab M. Wilcox is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Fire waiting to happen

Marc, You do not believe that the wire connection could arc or spark? The wire was literally loose. The missing knockout was directly below this area.
Reply With Quote
  #4  
Old 2/3/07, 12:01 PM
Tab M. Wilcox Tab M. Wilcox is offline
Active Poster
 
Join Date: Feb 2006
Location: Yuma, AZ
Posts: 165
Please Note: Tab M. Wilcox is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Fire waiting to happen

By the way I recommended replacement of the breaker and cutting away the damaged end of the wire and re-terminating into new breaker. (there appeared to be enough wire to cut off the bad section) and installing a knockout cover.
Reply With Quote
  #5  
Old 2/3/07, 12:03 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Fire waiting to happen

Quote:
Originally Posted by Tab M. Wilcox
Marc, You do not believe that the wire connection could arc or spark? .
I just believe that the phrase "fire waiting to happen" is over used.
Reply With Quote
  #6  
Old 2/3/07, 12:05 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Fire waiting to happen

Agree on that repair TAB, however we need to evaluate what exactly caused this in the first place.

1.) Was it just a bad connection to the breaker?
2.) Was it a bad breaker?
3.) Examine the load in question for this conductor?
4.) Connect it to a new breaker and AMP Probe it to see the draw?

But regardless KO needs plugged and wire fixed and breaker and circuit evaluated.....FYI.....this is not a normal condition to that alone should elevate it to evaluation.

FYI- However I only have a " In General" knowledge of electrical issues so don't take my word for it.



Paul W. Abernathy
Reply With Quote
  #7  
Old 2/3/07, 12:24 PM
Harold E. Miller's Avatar
Harold E. Miller Harold E. Miller is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Camano Island, WA
Posts: 713
Default Re: Fire waiting to happen

Quote:
Originally Posted by Marc D. Shunk
Fire waiting to happen? That's a leap that I might not be willing to take, but it certainly deserves repair.
Loose connection = high resistance, leading to overheating of conductor, melting insulation, potential arcing.....

....I think fire waiting to happen is not such a leap.

Certainly would not write it up as "fire waiting to happen"
But would use language that would compel people to act quickly on having it reviewed and repair by a licensed electrician.

Just my 2 cents...
Reply With Quote
  #8  
Old 2/3/07, 12:56 PM
ROBERT W. NEWLAND, JR.'s Avatar
ROBERT W. NEWLAND, JR. ROBERT W. NEWLAND, JR. is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: TYRONE, GA
Posts: 2,515
Default Re: Fire waiting to happen

Quote:
Originally Posted by Tab M. Wilcox
By the way I recommended replacement of the breaker and cutting away the damaged end of the wire and re-terminating into new breaker. (there appeared to be enough wire to cut off the bad section) and installing a knockout cover.
I would recommend evaluation by a Lic Electrician but would not recommend any method of repair (cutting away damaged wire). That's for the electrician to decide.
Reply With Quote
  #9  
Old 2/3/07, 1:18 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Fire waiting to happen

Robert that info was for everyone HERE's knowledge I think.....but I agree never put in a report on HOW to fix something because well us Electricians have to eat also...



Paul W. Abernathy
Reply With Quote
  #10  
Old 2/3/07, 4:21 PM
Tab M. Wilcox Tab M. Wilcox is offline
Active Poster
 
Join Date: Feb 2006
Location: Yuma, AZ
Posts: 165
Please Note: Tab M. Wilcox is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Fire waiting to happen

I appreciate the comments from everyone. FYI I did refer this to a licensed electrical contractor. I did not put "fire waiting to happen" in my report. By recommended I mean the buyer asked what the repair might consist of and I told him what I wrote above. I did tell him that the exact repair would be determined by the licensed electrical contractor when he evaluated the condition.

Last edited by Tab M. Wilcox; 2/3/07 at 9:18 PM..
Reply With Quote
  #11  
Old 2/3/07, 4:55 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Fire waiting to happen

Excellent Tab........ Sounds like a good call and a proper way to defer liability.. Very Tactful Defer...



Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Escape, Fire & Smoke Alarms badair Interior Inspections 14 1/28/08 7:21 AM
The Fire Guy ccrooker Canadian Inspectors 0 3/7/06 11:11 PM
Is this a catastrophe waiting to happen? dcossar Plumbing Inspections 10 2/8/06 7:13 PM


All times are GMT -4. The time now is 9:34 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts