Default Fixture in Attic, am I missing something?

The picture shows a label that reads DO NOT HAVE INSULATION WITHIN 3 INCHES UNLESS FOR i.c application. Insulation all over it. What is I.C?
Thanks
Rusty
Attached Thumbnails
fixture-attic-am-missing-something-fixturenote.jpg  
Reply With Quote
  #2  
Old 5/8/07, 5:40 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Fixture in Attic, am I missing something?

There's more information inside that can. Note that the label says "Remove this label if installed in an I.C. (insulated ceiling) application".

To use that can in an insulated ceiling application and still have the insulation around it, certain lamp sizes and certain trim models must be observed. That information will be on the label inside the can. If the lamp type and size, along with the trim model, jive with the "IC" chart inside the can, it's okay to insulate around that can.
Reply With Quote
  #3  
Old 5/8/07, 5:46 PM
rkeith rkeith is offline
InterNACHI Member
 
Join Date: Nov 2006
Location: St Augustine, FL
Posts: 44
Default Re: Fixture in Attic, am I missing something?

Thanks, but if all that info is INSIDE the can what am I to do? I can't take the can apart in a non-intrusive inspection. This is a new condo and I imagine all is well but HOW DO I KNOW FOR SURE?
Rusty
Reply With Quote
  #4  
Old 5/8/07, 6:09 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Fixture in Attic, am I missing something?

Quote:
Originally Posted by rkeith
This is a new condo and I imagine all is well...
Don't be so sure.

Quote:
Originally Posted by rkeith
...but HOW DO I KNOW FOR SURE?
If you can't take the trim down, I have no idea. If you're permitted to take the panel cover off, surely you can lower a recessed light trim to read a label, I would think, because it doesn't even require any tools. Hard to say. Probably have to wait for a home inspector to advise you on that.
Reply With Quote
  #5  
Old 5/8/07, 8:04 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Fixture in Attic, am I missing something?

Lightolier Lytening is the same way. The same can is used for both IC and non-IC applications. The trim and lamp determine the rating.

There is NO WAY to tell without removing the trim.



Quote:
Originally Posted by rkeith
What is I.C?
The term IC means "Insulated ceiling" as Marc stated, or "In contact" as in "in contact with insulation".
Isn't the term "I.C." covered in H-I seminars or classes?
Reply With Quote
  #6  
Old 5/8/07, 8:25 PM
Doug Edwards's Avatar
Doug Edwards Doug Edwards is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Florida panhandle
Posts: 4,850
Default Re: Fixture in Attic, am I missing something?

Speedy,
Unfortunately much is not covered in the average HI course today. Typically lasts a couple of weeks at best and a couple of days at worst. Plus a lot of bogus information and myths are perpetuated in HI schools/courses. Rule of thumb myths that continue to be passed down class after class. They take the students money and lead them to believe they are going out to make a killing and not the reality of setting up a business and running it. That is one reason why so many fail. Many of the old time courses taught everything including how to set up your business, run it and market it, keep the records, write the reports, etc. Most of them got out of the business because of the two weeks school houses that popped up all over the place. Less time and less money to be up and "running", so to speak. The one I took in 1993 was part of McGraw-Hill Education and it took over a year to complete. But it was well done and covered everything and then some. I don't blame the inspectors though. I still decided to go to the various trade schools too to get the hands on needed while I was building my business. I still run up on things I've never seen before and have to go digging to find the answers.
Another thing we had was after market help from the school as well. If you had a problem or question a year later you could call your old instructor and talk directly to him.

Last edited by dedwards; 5/8/07 at 8:30 PM..
Reply With Quote
  #7  
Old 5/8/07, 9:15 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Fixture in Attic, am I missing something?

Doug, that is truly a shame. I guess those sorts of things go on in every aspect of life.
Reply With Quote
  #8  
Old 5/8/07, 11:16 PM
Scott Schultz Scott Schultz is offline
Active Poster
 
Join Date: Sep 2006
Location: Surprise, AZ
Posts: 216
Please Note: Scott Schultz is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Fixture in Attic, am I missing something?

There's nothing worse than ambiguity. It says plain as day on the label "Do not install within 3 inches of insulation" But, if you take apart the unit and read the INSIDE label, it might be ok to do so. I wish things were just clear cut....either you can or you can't. PERIOD.
Reply With Quote
  #9  
Old 5/9/07, 10:15 AM
rkeith rkeith is offline
InterNACHI Member
 
Join Date: Nov 2006
Location: St Augustine, FL
Posts: 44
Default Re: Fixture in Attic, am I missing something?

Thanks Gentelmen,
But here is the problem, I am viewing this fixture from the attic space. The light is high above a staircase and hard to get to from that side. I thought the I.C designation was supposed to be clearly shown on top of the can (I have seen this).
Rusty
Reply With Quote
  #10  
Old 5/9/07, 11:04 AM
Blaine Wiley Blaine Wiley is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Rotonda West, FL
Posts: 3,186
Send a message via MSN to bwiley
Default Re: Fixture in Attic, am I missing something?

When I'm in that position I write up the light. It says on them to remove the label, and the label is still on it. Make the installer prove the condition is safe.



Don't interfere with anything in the Constitution. That must be maintained, for it is the only safeguard of our liberties.
Abraham Lincoln



www.qualityhomeinspectionsfl.com
Reply With Quote
  #11  
Old 5/9/07, 11:25 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Fixture in Attic, am I missing something?

This is my standard disclaimer because I'm not taking light fixtures apart and examining bulb wattages:

"We were unable to confirm that the recessed lights are designed to be installed in ceilings surrounded by insulation (IC rated). Recessed light fixtures that are installed in insulated ceilings can represent a fire hazard if they are not suitably rated for this application. Unfortunately, it is difficult to verify that the installation has been made correctly during a home inspection as the manufacturer's label is often inside the light fixture assembly. It is recommended that a licensed electrician be engaged to verify the safety of the system."



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #12  
Old 5/9/07, 2:24 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Fixture in Attic, am I missing something?

Quote:
Originally Posted by rkeith
The picture shows a label that reads DO NOT HAVE INSULATION WITHIN 3 INCHES UNLESS FOR i.c application. Insulation all over it. What is I.C?
Thanks
Rusty
Write it up Rusty.
In an IC installation the labels are supposed to be removed.
Who ever comes behind you to correct any defects called out in your report will verify that the installation is IC compliant and remove ALL the labels, or they will find it is not IC compliant and remove ALL of the insulation within 3" of the can, or they won't do anything at all.

You do not have time, nor are you getting paid enough to check every light in the ceiling.
</IMG></IMG>
Reply With Quote
  #13  
Old 5/9/07, 2:52 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Fixture in Attic, am I missing something?

Quote:
Originally Posted by Speedy Petey
Lightolier Lytening is the same way. The same can is used for both IC and non-IC applications. The trim and lamp determine the rating.

There is NO WAY to tell without removing the trim.



The term IC means "Insulated ceiling" as Marc stated, or "In contact" as in "in contact with insulation".
Isn't the term "I.C." covered in H-I seminars or classes?
Might have slept throught that part of the class myself, like the installer.
Reply With Quote
  #14  
Old 5/9/07, 3:53 PM
Blaine Wiley Blaine Wiley is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Rotonda West, FL
Posts: 3,186
Send a message via MSN to bwiley
Default Re: Fixture in Attic, am I missing something?

Quote:
Originally Posted by bkelly2
Might have slept throught that part of the class myself, like the installer.
Now that is funny, I don't care who you are, that there is funny!



Don't interfere with anything in the Constitution. That must be maintained, for it is the only safeguard of our liberties.
Abraham Lincoln



www.qualityhomeinspectionsfl.com
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Light Bulbs- All Ya Wanna Know pabernathy Electrical Inspections 9 4/18/07 7:22 PM
Spray Foam to the Rescue ? mcyr Structural Inspections 3 3/27/07 7:29 PM
Attic Inspection rbritton Electrical Inspections 19 8/2/06 2:58 PM
Attic Temperatures Can Pose Serious Risks jtedesco1 Interior Inspections 4 4/2/06 10:17 AM