The fixture is okay, but there is supposed to be a protective cover over the bulb.
Mark Nahrgang www.DaytonSpringfieldHomeInspector.com www.HeyMark.info Home Inspections for Springfield, Dayton, and surrounding OH areas. |
|
#3
|
||||
|
||||
|
Not sure what you mean Mark?
Do you mean flat fixture glass sitting on the ceiling ring? or did you mean a gasket around the bulb socket. |
|
#4
|
||||
|
||||
|
I would say it needs a flat fixture that covers and protects the bulb from any splashing.
Mark Nahrgang www.DaytonSpringfieldHomeInspector.com www.HeyMark.info Home Inspections for Springfield, Dayton, and surrounding OH areas. |
|
#5
|
||||
|
||||
|
Quote:
![]() Picture of the ring which has a foam gasket. |
|
#6
|
||||
|
||||
|
Quote:
In your first picture, there is nothing protecting the bulb. It looks like the fixture itself is okay, but it is missing the vital cover piece to make it whole. Mark Nahrgang www.DaytonSpringfieldHomeInspector.com www.HeyMark.info Home Inspections for Springfield, Dayton, and surrounding OH areas. |
|
#7
|
||||
|
||||
|
Quote:
Sounds crazy but do they make those kind of bulbs? Spot lights are outside all over. This is a subject I never think about because I do expect to see a glass light screen. |
|
#8
|
||||
|
||||
|
Quote:
My guess is they are tougher and don't break as easily. I still wouldn't want one over a shower though. If a bulb bursts outside, there likely isn't a naked wet person underneath it when it happens. Mark Nahrgang www.DaytonSpringfieldHomeInspector.com www.HeyMark.info Home Inspections for Springfield, Dayton, and surrounding OH areas. |
|
#9
|
||||
|
||||
|
Quote:
I do not wish to say I recommend a Licensed Electrician examine and evaluate , "just because of that reason". I need good wordage here. |
|
#10
|
||||
|
||||
|
Quote:
SAFETY CONCERN: While the recessed light fixture over the tub in the master bathroom is rated for a damp location; it is currently missing the vital cover over the bulb which would protect anyone in the case of breakage.The current occupants have installed an exterior bulb as a replacement. This is not a recommended practice nor suitable or safe repair. Recommend appropriate repair or replacement by a qualified electrical expert. Mark Nahrgang www.DaytonSpringfieldHomeInspector.com www.HeyMark.info Home Inspections for Springfield, Dayton, and surrounding OH areas. |
|
#11
|
||||
|
||||
|
Quote:
Thank you for the help . |
|
#12
|
||||
|
||||
|
The PDF file you provided has your answer. All of these trims are suitable for damp locations, but those suitable for "showers" or "wet locations" are specially marked.
Article 100 of NEC defines "damp location" and "wet location". A shower is a wet location and a device suitable for a damp location is unsuitable for a shower and needs to be replaced. James H. Bushart Professional Building Analyst, BPI Missouri, Kansas and Arkansas 314-803-2167 Inspecting in Aurora, Branson, Carthage, Granby, Joplin, Kimberling City, Monett, Mount Vernon, Neosho, Nixa, Purdy, Reed Spring, Republic, Springfield and surrounding areas. |
|
#13
|
||||
|
||||
|
Quote:
Here's an corrected comment... SAFETY CONCERN: While the recessed light fixture over the tub in the master bathroom is rated for a "damp location" it is not rated for use in a "wet location" such as over a tub. This fixture does not have a vital cover over the bulb which would protect anyone in the case of breakage.The current occupants have installed an exterior bulb as a substitute. This is not a recommended practice nor suitable nor safe for this location. Recommend appropriate repair or replacement by a qualified electrical expert. Mark Nahrgang www.DaytonSpringfieldHomeInspector.com www.HeyMark.info Home Inspections for Springfield, Dayton, and surrounding OH areas. |
| Find an InterNACHI certified New Hampshire Home Inspector (and anywhere else in North America) |
|
#14
|
||||
|
||||
|
Quote:
I will recommend replacement of that fixture. Putting the report in this morning. |
|
#15
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Why would the ceiling of a shower be be considered to be a wet location? Using the NEC definition of wet location it is not underground or subject to saturation, nor is it outside in an unprotected location. Using 410.4(D) only says listed for wet locations "if subject to shower spray". I guess someone could spray the ceiling with a handheld showerhead, but that seems to be a stretch.
Seagull Lighting has several open baffle trims for recessed that are shower rated. The bulbs listed for use with the trims are either PAR 30 or 38 bulbs. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Recessed Light fixture and insulation | Rick Vollmer | Interior Inspections | 3 | 11/19/09 10:42 AM |
| Light Fixture Recall | mbazzo | Electrical Inspections | 8 | 6/11/08 1:06 PM |
| Recall of Exterior Lighting Fixture | jbushart | Electrical Inspections | 0 | 3/19/08 6:28 PM |
| Recall of Outdoor Lighting Fixture | jbushart | Exterior Inspections | 0 | 3/19/08 6:26 PM |
| Light Bulbs- All Ya Wanna Know | pabernathy | Electrical Inspections | 9 | 4/18/07 8:22 PM |