Default Flexible conduit used as ground?

1924 house with two individual conductors run through flexible conduit and the conduit is used as grounding. I know that rigid conduit is generally acceptable as a ground, but is flexible?
Attached Thumbnails
flexible-conduit-used-ground-p1250522.jpg  
Reply With Quote
Need a home inspection in Rhode Island? Check out InterNACHI's listing of Rhode Island certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 1/24/11, 11:36 PM
Robert Ernst Robert Ernst is offline
InterNACHI Member
 
Join Date: Sep 2010
Location: Sparks,NV
Posts: 654
Default Re: Flexible conduit used as ground?

I think it was common practice at one time. But older BX shouldn't be used as a ground. Newer Armored Cable has a ground strip in it and can be used as a ground.
Reply With Quote
  #3  
Old 1/25/11, 4:53 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,252
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Flexible conduit used as ground?

In general FMC or flexible metal conduit is limited to 6' in length when used as an EGC (equipment grounding conductor). Since this is an old installation it's likely grandfathered in, however by modern standards it's could be considered ungrounded even though all of the components of the system are metallic. Is the stuff in the photo actually FMC or is it old AC (BX) cable?

Quote:
250.118 Types of Equipment Grounding Conductors.
The equipment grounding conductor run with or enclosing the circuit conductors shall be one or more or a combination of the following:
FPN: For effective ground-fault current path, see 250.2 Definition.
(5) Listed flexible metal conduit meeting all the following conditions:
a. The conduit is terminated in listed fittings.
b. The circuit conductors contained in the conduit are protected by overcurrent devices rated at 20 amperes or less.
c. The combined length of flexible metal conduit and flexible metallic tubing and liquidtight flexible metal conduit in the same ground return path does not exceed 1.8 m (6 ft).
d. Where used to connect equipment where flexibility is necessary after installation, an equipment grounding conductor shall be installed.
Reply With Quote
  #4  
Old 1/25/11, 8:17 AM
rhornung rhornung is offline
InterNACHI Member
 
Join Date: Apr 2010
Posts: 52
Default Re: Flexible conduit used as ground?

Thanks for the followup! The cable is probably an early (original to the house, 1924) BX cable. The conductors have the same type of insulation found on knob and tube wiring. While it's certainly grandfathered in, the City of Dearborn is requesting the following on their occupancy cert: "Install GFI protected outlets in all wall outlets--exterior and interior." I would assume they mean wherever normally needed like kitchen, bath, basement, garage, etc. But they are all already present. I'm concerned that if they are upgrading existing three prong outlets to GFI this conduit as ground may become a factor.
Reply With Quote
  #5  
Old 1/25/11, 11:12 AM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is online now
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: Flexible conduit used as ground?

Are the outlets actually grounded. Did you remove a cover and look? Three prong outlets are not a guarantee of what you have. Never assume. Just because you see armored cable, does not mean the boxes are metallic. Two wire ungrounded was very common in 1924. Did you find any K&T in the home? It could just be a partial upgrade at the panel from years ago.
Reply With Quote
  #6  
Old 1/25/11, 11:42 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Flexible conduit used as ground?

Quote:
Originally Posted by rhornung View Post
While it's certainly grandfathered in, the City of Dearborn is requesting the following on their occupancy cert: "Install GFI protected outlets in all wall outlets--exterior and interior." I would assume they mean wherever normally needed like kitchen, bath, basement, garage, etc.
Based on the age of the home and the wiring methods, this is generally a system where the branch circuits are not grounded. It sounds to me as if the City is requiring an upgrade for compliance with current standards, which would mean that ALL branch circuit receptacles be protected by ground-fault circuit interrupters.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #7  
Old 1/25/11, 4:14 PM
rhornung rhornung is offline
InterNACHI Member
 
Join Date: Apr 2010
Posts: 52
Default Re: Flexible conduit used as ground?

Quote:
Are the outlets actually grounded. Did you remove a cover and look? Three prong outlets are not a guarantee of what you have. Never assume. Just because you see armored cable, does not mean the boxes are metallic. Two wire ungrounded was very common in 1924. Did you find any K&T in the home? It could just be a partial upgrade at the panel from years ago.
I didn't assume anything with these. The outlets are actually grounded, I verified every outlet. I also opened a number of them and they were consistently lacking ground wires even though they had continuity to ground. There was no evidence of the house ever having had Knob and Tube, no remnants, no holes, etc. Parts of the system have been upgraded to newer NM, but several parts of the house still used the BX or FMC as ground.
Quote:
It sounds to me as if the City is requiring an upgrade for compliance with current standards, which would mean that ALL branch circuit receptacles be protected by ground-fault circuit interrupters.
Are you saying that proper grounds will need to be run to install the GFIs or will they simply need to install them and mark them as non-grounded? Thanks for the help guys.
Reply With Quote
  #8  
Old 1/25/11, 4:40 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,252
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Flexible conduit used as ground?

Quote:
Originally Posted by rhornung View Post
I didn't assume anything with these. The outlets are actually grounded, I verified every outlet. I also opened a number of them and they were consistently lacking ground wires even though they had continuity to ground. There was no evidence of the house ever having had Knob and Tube, no remnants, no holes, etc. Parts of the system have been upgraded to newer NM, but several parts of the house still used the BX or FMC as ground.
Are you saying that proper grounds will need to be run to install the GFIs or will they simply need to install them and mark them as non-grounded? Thanks for the help guys.
Yes old AC cable will test good for ground continuity because it's made of metal and is attached to a metal box. The question is will it have a low enough impedance under fault conditions to open the OCPD? Maybe, maybe not.

GFCI protection is not a substitute for grounding but is permitted for increasing safety in an ungrounded system. Only problem is that when used with old AC cable the metallic jacket of the cable will still be carrying the fault current during a ground fault condition so the GFCI protection will actually do nothing.
Reply With Quote
  #9  
Old 1/25/11, 6:30 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Flexible conduit used as ground?

Quote:
Originally Posted by rhornung View Post
Are you saying that proper grounds will need to be run to install the GFIs or will they simply need to install them and mark them as non-grounded? Thanks for the help guys.
The NEC allows for replacement of non-grounding type receptacles with GFCI protected receptacles, without requiring that the GFCI be grounded.

Out of curiosity, what type of instrument did you use to determine that the existing receptacles were grounded? Did you happen to check the impedance of the grounding connection?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #10  
Old 1/25/11, 7:15 PM
rhornung rhornung is offline
InterNACHI Member
 
Join Date: Apr 2010
Posts: 52
Default Re: Flexible conduit used as ground?

Quote:
Out of curiosity, what type of instrument did you use to determine that the existing receptacles were grounded? Did you happen to check the impedance of the grounding connection?
I used a simple tester at first and when I visually observed that the breaker panel had a number of incoming wires without grounds, I traced a couple of circuits to outlets that showed up as grounded. I then removed an outlet from its box and noted that no ground wire was present and that there was no continuity to ground when not connected to the box. I did not check impedance.
Reply With Quote
  #11  
Old 1/26/11, 4:38 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,252
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Flexible conduit used as ground?

Quote:
Originally Posted by rhornung View Post
I used a simple tester at first and when I visually observed that the breaker panel had a number of incoming wires without grounds, I traced a couple of circuits to outlets that showed up as grounded. I then removed an outlet from its box and noted that no ground wire was present and that there was no continuity to ground when not connected to the box. I did not check impedance.

Any kind of basic tester would show this receptacle as grounded before you unscrewed it.
Reply With Quote
  #12  
Old 1/26/11, 5:08 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Flexible conduit used as ground?

Quote:
Originally Posted by Robert Meier View Post
Any kind of basic tester would show this receptacle as grounded before you unscrewed it.
That's why I asked. I would have been inclined to check impedance in an older system like this. The SureTest has that functionality.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #13  
Old 1/26/11, 7:25 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,252
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Flexible conduit used as ground?

Quote:
Originally Posted by jpope View Post
That's why I asked. I would have been inclined to check impedance in an older system like this. The SureTest has that functionality.

Yes, unless you could test it with something more sophisticated than a standard tester you would only know that the ground was continuous. If it is suitable to carry the entire fault current in a ground fault condition would require other methods.

So how does the Suretest test for impedance?
Reply With Quote
Need a home inspection in Rhode Island? Check out InterNACHI's listing of Rhode Island certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 1/26/11, 9:22 PM
Tim Spargo's Avatar
Tim Spargo Tim Spargo is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Lancaster, CA
Posts: 2,407
Default Re: Flexible conduit used as ground?

I don't know if all do it.. I have the 165, You scroll via the arrows to that function. You can test the impedance of the Hot Neutral or Ground

I don't test every outlet with it... I will sample upon finishing with the 3 bulb. *Interesting* results can be found in McMansions.....AND old houses.
Attached Thumbnails
flexible-conduit-used-ground-dscf6053.jpg   flexible-conduit-used-ground-dscf6054.jpg  



Home Inspections in Palmdale Lancaster California

Tim Spargo
Spec Rite Inspections
Commercial and Residential Inspections
Palmdale Lancaster Santa Clarita CA
661-317-5770








Reply With Quote
  #15  
Old 1/26/11, 9:28 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,252
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Flexible conduit used as ground?

Quote:
Originally Posted by tspargo View Post
I don't know if all do it.. I have the 165, You scroll via the arrows to that function. You can test the impedance of the Hot Neutral or Ground

I don't test every outlet with it... I will sample upon finishing with the 3 bulb. *Interesting* results can be found in McMansions.....AND old houses.
Interesting tester, but I'm skeptical that the impedance test is real world predictor of how the armored cable will react when an actual ground fault occurs. The reason being that when a ground fault is connected across a piece of old AC cable the fault current is potentially in the thousands of amps. Can this tester actually simulate that?
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Help. What is the correct way to report a breaker that is too big. gromicko Electrical Inspections 77 5/10/12 6:13 PM
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 9:24 AM


All times are GMT -4. The time now is 9:35 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts