I see in 348.12 that FMC is allowed in wet locations if the conductors are approved.....

I see a lot of exterior hvac units with the FMC but can not be sure if the correct conductor insulation type is present.

Some have THHN and some have stranded copper with no easily visible markings.

Anyone have any advice on this?

thanks



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #2  
Old 2/28/07, 12:04 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Flexible metal conduit

Virtually all THHN is dual rated THWN, stranded or solid
Reply With Quote
  #3  
Old 2/28/07, 9:17 AM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Flexible metal conduit

I was told the actual item that turns 60C insulation into 90C insulation is the clear outer jacket. Also the jacket serves the purpose to make it water tight, thus making it THWN as well.

Now don't quote me on this, just that I was told this.

tom

Had to edit this, not 'water tight' but part of it being 'liquid resistant' Had clear up what I was told, since Greg reminded me.

Last edited by tdietrich1; 2/28/07 at 3:37 PM..
Reply With Quote
  #4  
Old 2/28/07, 12:05 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Flexible metal conduit

That is not the way I have heard it. I understand the outer clear jacket is not even necessary to get to the listed rating. It is just there to lower pulling tension and to provide oil resistance. Maybe Pierre has more on this. Logic says all of the insulation would have to be capable of handling the 90c. As for the "W" part, when you use dual rated conductors in a wet location it assumes the THWN rating of 75c. That can become important when you have a lot of wire in the raceway or when you are running over a rooftop.
Reply With Quote
  #5  
Old 2/28/07, 6:24 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Flexible metal conduit

Here's your rule of thumb... if you see individual conductors pulled in that FMC, and they have plastic insulation, chances are 99% that they are conductors with a "W" in the nomenclature (wet location). If you see braided conductors or NM cable pulled in that FMC, that would be worthy of calling out.
Reply With Quote
  #6  
Old 2/28/07, 6:49 PM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Flexible metal conduit

Quote:
Originally Posted by Marc D. Shunk
braided conductors
Dreadlocks or pig-tails?

Reply With Quote
  #7  
Old 2/28/07, 6:56 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Flexible metal conduit

Quote:
Originally Posted by tdietrich1
Dreadlocks or pig-tails?

I guess I did open that door, didn't I? Braided fabric insulation.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Help. What is the correct way to report a breaker that is too big. gromicko Electrical Inspections 77 5/10/12 6:13 PM
Light Bulbs- All Ya Wanna Know pabernathy Electrical Inspections 9 4/18/07 7:22 PM
NACHI Chapters Free Electrical Training Available jtedesco1 Inspection Education & Training 5 8/11/06 4:46 PM
PVC conduit interior location kelliott Electrical Inspections 6 4/21/06 11:55 AM


All times are GMT -4. The time now is 9:35 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts