  #16  
Old 4/23/07, 5:20 AM
Linda J. Foster's Avatar
Linda J. Foster Linda J. Foster is offline
InterNACHI Member
 
Join Date: Apr 2006
Location: Utopia, TX
Posts: 471
Default Re: floor outlet receptacle

There are two separate floor outlets in family room, ceramic tile floor. Walls are further than 6' from outlets.

The covers are slightly 'domed', overall height is appx. 1/4". The covers sit on top of floor, not 'into' floor surface.

Can't see the height in pic,,,,
Attached Thumbnails
floor-outlet-receptacle-floor_o-small-.jpg.jpg
Views:	49
Size:	49.7 KB
ID:	11038  



Linda Foster
www.HomeInspectionsByFoster.com
HomeInspectionsByFoster@yahoo.com

(210) 347-1023
TREC #7654
InterNACHI #06032691

Reply With Quote
  #17  
Old 4/23/07, 5:33 AM
Frank M. Carrio, CMI's Avatar
Frank M. Carrio, CMI Frank M. Carrio, CMI is offline
ESOP Committee Member
 
Join Date: Jan 2004
Posts: 4,250
Default Re: floor outlet receptacle

[quote=lfoster]
There are two separate floor outlets in family room, ceramic tile floor. Walls are further than 6' from outlets.
Hi Linda,
I don't know the size of this room but that is probably why you have receptacles in the floor
I have seen this type of floor “mounted” receptacle many, many times. It is not unusual and they only "problem" here is that the covering is ugly and does not match the ceramic tile.
The covers are slightly 'domed', overall height is appx. 1/4". The covers sit on top of floor, not 'into' floor surface.
Since the edges are rounded and not "sharp "this covers the "tripping issue". Once again the coverings are ugly but do not pose a tripping hazard.
Can't see the height in pic,,,,


Here is the information from the IRC covering this issue. I have also looked into the IBC, and The ICC electrical codes. None of them address the "height issue".

2006 international residential code for one and two family dwellings
E3801.2.1 Spacing.
Receptacles shall be installed so that no point measured horizontally along the floor line in any wall space is more than 6 feet (1829 mm), from a receptacle outlet.
E3801.2.2 Wall space.
As used in this section, a wall space shall include the following:
1. Any space that is 2 feet (610 mm) or more in width, (including space measured around corners), and that is unbroken along the floor line by doorways, fireplaces, and similar openings.
2. The space occupied by fixed panels in exterior walls, excluding sliding panels.
3. The space created by fixed room dividers such as railings and freestanding bar-type counters
E3801.2.3 Floor receptacles.
Receptacle outlets in floors shall not be counted as part of the required number of receptacle outlets except where located within 18 inches (457 mm) of the wall.



Signed, Frank Carrio, CMI
Certified Master Inspector & Consultant
Certified Commercial Building Inspector
Certified, WDI Inspector
Founder & Current President, New Hampshire State Chapter NACHI
NACHI, State Representative for Legislative Affairs
Retired: ICC Certified Member
Retired: Code Compliance Inspector.
Retired: ASTM Committee Member
New Hampshire License #0096
www.Americascertifiedinspectioncompanyllc.com
Reply With Quote
  #18  
Old 4/23/07, 6:44 AM
David P. Valley's Avatar
David P. Valley David P. Valley is online now
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,475
Default Re: floor outlet receptacle

Quote:
Originally Posted by Speedy Petey
1)2) I did not know juice could make "sparks".
Sorry, this will NOT happen.
Do yourself a favor. Pour a liquid of your choice into one of these receptacles and simply observe.

Quote:
3) What is a "horizontal" floor box?????
Where did I state "horizontal floor box"? I've never heard of one.

It says "Horizontal floor receptacle"

If the receptacle is not protected in any way, I write it up. This is one of many protective covers that I'd like to see.

Reply With Quote
  #19  
Old 4/23/07, 8:15 AM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: floor outlet receptacle

Sorry David, wrong word. Floor receptacle. SEMANTICS in this case.

I still ask, what is a horizontal floor receptacle? And if it has a legal floor cover why would your write it up?

Of course you should write it up if not a proper floor receptacle box/cover. No one ever disputed this.


I HAVE seen liquid in a receptacle, and it never "sparked". Water IS NOT a good conductor. Especially not enough to create a bolted fault.
Reply With Quote
  #20  
Old 4/23/07, 8:20 AM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: floor outlet receptacle

Quote:
Originally Posted by fcarrio
Just curious, where is it located, Hallway, Bedroom, etc. are there other electrical outlets within 6 feet?
If a floor receptacle is located more than 18" from a wall it cannot be counted towards the "required" receptacles in a room. Once it goes beyond this 18" it hold NO bearing on the other receptacles in the room and is simply a convenience receptacle.

The fact that it is within 6' from another receptacle is meaningless. For one thing, to be counted as a required receptacle it can be 12' away, not 6'.
Reply With Quote
  #21  
Old 4/23/07, 9:54 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,689
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: floor outlet receptacle

The only comment I will make about water being a conductor is this...it is a weak one but it is one in a sense that if we are talking about saturation of the outlet with water and it is "STANDING"....and you reach and come in contact with the water it could very well be your last contact...if the conditions are right...

So it is not as much in just having a liquid associated with it..it is what happens as we come in contact with the liquid in this example.

I believe that IF you saw sparks...there is another issue going on in that outlet that preceeded this event....and the moisture simply assperated the condition.



Paul W. Abernathy,CMI,CEI,CEPE
National Electrical Code Expert-ONLY
Weekly Live Chat :http://www.theelectricalguru.com/chat.html
Weekly Chat on Mondays & Wednesdays -8PM E.S.T
* Notice- I will not be conducting any future seminars for the HI Industry. I am a CODE GUY so I will be focusing efforts on the NEC Code. If you have CODE question visit my website...if you have Electrical HI questions ask Nick or Ben Gromicko.
Reply With Quote
  #22  
Old 4/23/07, 12:48 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: floor outlet receptacle

Pure water is a poor conductor but that is hard to find. It only takes a small bit of minerals to make it a surprisingly good conductor. I did some experiments many years ago with a white bucket and 2 10ga probes exactly 1 foot apart, 6" in the water.
<from memory I think the following was true>
Using distilled water the conductivity was very low but a pinch of salt made a 60w bulb start to glow. With a shotglass of salt the 60w bulb burned a warm yellow.
My well water was similar to the test "ionized" water. When I used (Gulf) sea water (~37PPT) the bulb was almost full brightness.

If you want to try this be sure your test setup is such that you are nowhere near the bucket when you energize it since the seawater was boiling pretty good with power applied.

I may try this again with better testing standards if anyone is interested.
Reply With Quote
  #23  
Old 4/23/07, 1:10 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,689
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: floor outlet receptacle

Couple that with most solvents having so many chemicals and so on within it...could happen I guess....



Paul W. Abernathy,CMI,CEI,CEPE
National Electrical Code Expert-ONLY
Weekly Live Chat :http://www.theelectricalguru.com/chat.html
Weekly Chat on Mondays & Wednesdays -8PM E.S.T
* Notice- I will not be conducting any future seminars for the HI Industry. I am a CODE GUY so I will be focusing efforts on the NEC Code. If you have CODE question visit my website...if you have Electrical HI questions ask Nick or Ben Gromicko.
Reply With Quote
  #24  
Old 4/23/07, 1:23 PM
David P. Valley's Avatar
David P. Valley David P. Valley is online now
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,475
Default Re: floor outlet receptacle

Quote:
Originally Posted by Speedy Petey
And if it has a legal floor cover why would your write it up?
Hey Speed,

Are you illiterate or just simply not reading my posts correctly?

Would you be so kind to highlight where I had stated that I'd write up a floor receptacle that had a legal floor cover.

You need to wake up a smell the Daises my friend.
Reply With Quote
  #25  
Old 4/23/07, 6:04 PM
Frank M. Carrio, CMI's Avatar
Frank M. Carrio, CMI Frank M. Carrio, CMI is offline
ESOP Committee Member
 
Join Date: Jan 2004
Posts: 4,250
Default Re: floor outlet receptacle

Quote:
Originally Posted by Speedy Petey
If a floor receptacle is located more than 18" from a wall it cannot be counted towards the "required" receptacles in a room. Once it goes beyond this 18" it hold NO bearing on the other receptacles in the room and is simply a convenience receptacle.

The fact that it is within 6' from another receptacle is meaningless. For one thing, to be counted as a required receptacle it can be 12' away, not 6'.

See the information that I listed in my post above {#17};

2006 international residential code for one and two family dwellings
E3801.2.1 Spacing.

Receptacles shall be installed so that no point measured horizontally along the floor line in any wall space is more than 6 feet (1829 mm), from a receptacle outlet.
E3801.2.2 Wall space.
As used in this section, a wall space shall include the following:
1. Any space that is 2 feet (610 mm) or more in width, (including space measured around corners), and that is unbroken along the floor line by doorways, fireplaces, and similar openings.
2. The space occupied by fixed panels in exterior walls, excluding sliding panels.
3. The space created by fixed room dividers such as railings and freestanding bar-type counters
E3801.2.3 Floor receptacles.
Receptacle outlets in floors shall not be counted as part of the required number of receptacle outlets except where located within 18 inches (457 mm) of the wall.



Signed, Frank Carrio, CMI
Certified Master Inspector & Consultant
Certified Commercial Building Inspector
Certified, WDI Inspector
Founder & Current President, New Hampshire State Chapter NACHI
NACHI, State Representative for Legislative Affairs
Retired: ICC Certified Member
Retired: Code Compliance Inspector.
Retired: ASTM Committee Member
New Hampshire License #0096
www.Americascertifiedinspectioncompanyllc.com

Last edited by fcarrio; 4/23/07 at 6:54 PM..
Reply With Quote
  #26  
Old 4/23/07, 6:06 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Unmoderated Guest
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: floor outlet receptacle

I'm not sure why everyone's jumping Speedy's case. You all are saying the same things in different ways. Speedy's just making sure everyone's on the same page.
Reply With Quote
  #27  
Old 4/23/07, 6:47 PM
Frank M. Carrio, CMI's Avatar
Frank M. Carrio, CMI Frank M. Carrio, CMI is offline
ESOP Committee Member
 
Join Date: Jan 2004
Posts: 4,250
Default Re: floor outlet receptacle

Quote:
Originally Posted by Marc D. Shunk
I'm not sure why everyone's jumping Speedy's case. You all are saying the same things in different ways. Speedy's just making sure everyone's on the same page.


No one is jumping on his case. However if you're going to attempt quote code or speak in an authoritative manner and contradict someone you should be correct in what you say.

2006 international residential code for one and two family dwellings
E3801.2.1 Spacing.

Receptacles shall be installed so that no point measured horizontally along the floor line in any wall space is more than 6 feet (1829 mm), from a receptacle outlet.
E3801.2.2 Wall space.
As used in this section, a wall space shall include the following:
1. Any space that is 2 feet (610 mm) or more in width, (including space measured around corners), and that is unbroken along the floor line by doorways, fireplaces, and similar openings.
2. The space occupied by fixed panels in exterior walls, excluding sliding panels.
3. The space created by fixed room dividers such as railings and freestanding bar-type counters
E3801.2.3 Floor receptacles.
Receptacle outlets in floors shall not be counted as part of the required number of receptacle outlets except where located within 18 inches (457 mm) of the wall.


From the information that we have gathered here this floor receptacle is nothing more than a "convenience receptacle". The picture clearly shows that it is covered and thus supposedly protected.
I am sure that there will be many that come up with their "what if" scenarios but then again all of this debate is meaningless and serves no useful purpose.



Signed, Frank Carrio, CMI
Certified Master Inspector & Consultant
Certified Commercial Building Inspector
Certified, WDI Inspector
Founder & Current President, New Hampshire State Chapter NACHI
NACHI, State Representative for Legislative Affairs
Retired: ICC Certified Member
Retired: Code Compliance Inspector.
Retired: ASTM Committee Member
New Hampshire License #0096
www.Americascertifiedinspectioncompanyllc.com

Last edited by fcarrio; 4/23/07 at 6:51 PM..
Reply With Quote
  #28  
Old 4/23/07, 6:58 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Unmoderated Guest
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: floor outlet receptacle

Quote:
Originally Posted by fcarrio
I am sure that there will be many that come up with their "what if" scenarios but then again all of this debate is meaningless and serves no useful purpose.
No, 'what if's', brother. It's clear to me that you're both saying the same thing in different ways. No matter...
Reply With Quote
  #29  
Old 4/23/07, 9:56 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: floor outlet receptacle

Quote:
Originally Posted by dvalley
I recommend (to my clients) that all horizontal floor receptacles be terminated and capped. When I do find these, there's only one or two in the house.
David, first off, chill the hell out!

Explain the above quote then. I must be confused by your ambiguosity.
It sounds like you would write up any floor receptacle.
Reply With Quote
  #30  
Old 4/23/07, 9:59 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: floor outlet receptacle

Quote:
Originally Posted by fcarrio
E3801.2.1 Spacing.
Receptacles shall be installed so that no point measured horizontally along the floor line in any wall space is more than 6 feet (1829 mm), from a receptacle outlet.
Frank, I am surprised with all your years of experience you still do not understand this.

"No point along a wall is more than 6' from a receptacle."
This DOES NOT mean the receptacles must be 6' apart. It means they can be 12' apart.
Point to a spot on the wall. There must be a receptacle within 6' of your finger, in either direction.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Microwave receptacle jwardenski Electrical 17 9/9/07 7:18 PM
What's This Receptacle For? cmettel Electrical 7 5/25/07 7:35 AM
Bedroom receptacle dnasser Electrical 9 4/16/07 10:33 AM
Online Code Check- Reference pabernathy Electrical 31 11/9/06 3:39 PM
Wiring a Receptacle jallingham Electrical 9 8/6/06 4:34 PM


All times are GMT -4. The time now is 9:18 AM.


Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts