Default Re: floor outlet receptacle

Quote:
Originally Posted by Speedy Petey
David, first off, chill the hell out!

Explain the above quote then. I must be confused by your ambiguosity.
It sounds like you would write up any floor receptacle.
You're the one with the attitude there, Buddy. I'm a happy individual.

There's no ambiguosity whatsoever, you simply have to open your eyes and use your brain and look a little further on down into the thread, I clearly stated this....

Quote:
If the receptacle is not protected in any way, I write it up. This is one of many protective covers that I'd like to see.


I did state
Quote:
I recommend (to my clients) that all horizontal floor receptacles be terminated and capped. When I do find these, there's only one or two in the house.
because I've never ran into a protected receptacle...Period.
Reply With Quote
  #32  
Old 4/24/07, 9:17 AM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: floor outlet receptacle

Quote:
Originally Posted by dvalley
You're the one with the attitude there, Buddy. I'm a happy individual.
Whatever Dave. Obviously you need to open your eyes and use your brain as well I guess.
You are confusing disagreement with attitude. There IS a difference.





Quote:
Originally Posted by dvalley
because I've never ran into a protected receptacle...Period.
Which is odd. I don't think I've ever seen a floor receptacle without a floor cover.
Must be a location thing.
Reply With Quote
  #33  
Old 4/24/07, 9:42 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,482
Default Re: floor outlet receptacle

Quote:
Originally Posted by Speedy Petey

"No point along a wall is more than 6' from a receptacle."
This DOES NOT mean the receptacles must be 6' apart. It means they can be 12' apart.
Point to a spot on the wall. There must be a receptacle within 6' of your finger, in either direction.
It seems a lot of people misinterpret that.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #34  
Old 4/24/07, 10:00 AM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: floor outlet receptacle

Quote:
Originally Posted by lkage
It seems a lot of people misinterpret that.
I find that as well. I really do wish they would re-word that paragraph of the code, or at least clarify a bit.
Reply With Quote
  #35  
Old 4/24/07, 10:57 AM
Dan Bowers, CMI Dan Bowers, CMI is online now
InterNACHI Member
 
Join Date: Oct 2003
Location: Shawnee Mission, KS
Posts: 3,586
Default Re: floor outlet receptacle

Some of us must really like to write things up. 98% of the time when I see these they're in the middle of a good sized room AND the furniture placement is such that there will be a light or couch, end table, etc over them.

They're a convenience so the occupants can place their furniture, lights in a reasonable arrangement AND not be stringing extension cords all across the floor where they REALLY become a trip hazard.
Reply With Quote
  #36  
Old 4/24/07, 11:16 AM
William Warner's Avatar
William Warner William Warner is offline
InterNACHI Member
 
Join Date: May 2003
Location: Dayton, OH
Posts: 3,236
Default Re: floor outlet receptacle

Quote:
Originally Posted by Speedy Petey
Which is odd. I don't think I've ever seen a floor receptacle without a floor cover.
Must be a location thing.
Here you go from an inspection last week.floor-outlet-receptacle-pict9954.jpg




Submit your AWARDS NOMINATIONS here

Visit the InterNACHI Awards web portal here

Blessed are the blissfully ignorant... for they shall be easily led...
Reply With Quote
  #37  
Old 4/24/07, 11:31 AM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: floor outlet receptacle

Write it up!

Of course it happens. Like I said, I just can't remember the last time I saw that.
Reply With Quote
  #38  
Old 4/24/07, 11:37 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: floor outlet receptacle

Quote:
Originally Posted by wwarner
Here you go from an inspection last week.Attachment 11087
Thank you William. This is the only type I find on a regular basis. That's why I write them up.
Reply With Quote
  #39  
Old 4/24/07, 12:56 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,557
Default Re: floor outlet receptacle

Well Duh!

Speedy is an electrician who knows how to install them correctly. That's what he sees.

Most of the rest of us here are HIs who see the the results of Home Owner Harry NOT hiring a qualified electrician or bothering to find out the what correct way to install them is. That's what we see.

So let's all just realize we come at this issue from different perspectives.

No need for all the acrimony generated here.
Reply With Quote
  #40  
Old 4/25/07, 10:29 PM
smcarthur smcarthur is offline
New User
 
Join Date: Jul 2006
Location: Rock Hill, SC
Posts: 96
Please Note: smcarthur is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: floor outlet receptacle

Quote:
Originally Posted by dvalley

I recommend (to my clients) that all horizontal floor receptacles be terminated and capped. When I do find these, there's only one or two in the house.
The only problem that I see with that statement is that sometimes a floor receptacle is the only means to satisfy the 6' rule for receptacle spacing, say for instance on a balcony with 15' of railing. The railing counts as wall space and must be provided with properly spaced receptacles to meet code requirements.
Reply With Quote
  #41  
Old 4/26/07, 4:33 PM
Frank M. Carrio, CMI's Avatar
Frank M. Carrio, CMI Frank M. Carrio, CMI is offline
ESOP Committee Member
 
Join Date: Jan 2004
Posts: 4,363
Default Re: floor outlet receptacle

Quote:
Originally Posted by Speedy Petey
Frank, I am surprised with all your years of experience you still do not understand this.

"No point along a wall is more than 6' from a receptacle."
This DOES NOT mean the receptacles must be 6' apart. It means they can be 12' apart.
Point to a spot on the wall. There must be a receptacle within 6' of your finger, in either direction.
Jesus, Mary & Joseph!
YES I AM CLEAR ON THE REQUIRED SPACING OF THE RECEPTACLES.
It is you who does not either understand or who cannot read! The Codes are very clear on this issue and I thought that by posting them it would it any and all speculation.

THERE IS NO CONFUSION ON MY PART! SEE POSTS #17, 25. & 27!

WORTH REPEATING!

2006 international residential code for one and two family dwellings
E3801.2.1 Spacing.

Receptacles shall be installed so that no point measured horizontally along the floor line in any wall space is more than 6 feet (1829 mm), from a receptacle outlet.
E3801.2.2 Wall space.
As used in this section, a wall space shall include the following:
1. Any space that is 2 feet (610 mm) or more in width, (including space measured around corners), and that is unbroken along the floor line by doorways, fireplaces, and similar openings.
2. The space occupied by fixed panels in exterior walls, excluding sliding panels.
3. The space created by fixed room dividers such as railings and freestanding bar-type counters
E3801.2.3 Floor receptacles.
Receptacle outlets in floors shall not be counted as part of the required number of receptacle outlets except where located within 18 inches (457 mm) of the wall.


From the information that we have gathered here this floor receptacle is nothing more than a "convenience receptacle". The picture clearly shows that it is covered and thus supposedly protected.
I am sure that there will be many that come up with their "what if" scenarios but then again all of this debate is meaningless and serves no useful purpose.



Signed, Frank Carrio, CMI
Certified Master Inspector & Consultant
Certified Commercial Building Inspector
Certified, WDI Inspector
Founder & Current President, New Hampshire State Chapter NACHI
NACHI, State Representative for Legislative Affairs
Retired: ICC Certified Member
Retired: Code Compliance Inspector.
Retired: ASTM Committee Member
New Hampshire License #0096
Reply With Quote
  #42  
Old 4/26/07, 5:18 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: floor outlet receptacle

Wow Frank. There is medicine to help you stay calm in these situations.


So botom line. Regardless of the exact wording of the code, how far apart can receptacles be in a residential bedroom installation?
Reply With Quote
  #43  
Old 4/26/07, 6:04 PM
Frank M. Carrio, CMI's Avatar
Frank M. Carrio, CMI Frank M. Carrio, CMI is offline
ESOP Committee Member
 
Join Date: Jan 2004
Posts: 4,363
Default Re: floor outlet receptacle

Quote:
Originally Posted by Speedy Petey
Wow Frank. There is medicine to help you stay calm in these situations.
ROTFLMAO!


So botom line. Regardless of the exact wording of the code, how far apart can receptacles be in a residential bedroom installation?
WOW!
After all of these years in the business and you still don't know this!

READ THIS!
E3801.2.1 Spacing.
Receptacles shall be installed so that no point measured horizontally along the floor line in any wall space is more than 6 feet (1829 mm), from a receptacle outlet.



Signed, Frank Carrio, CMI
Certified Master Inspector & Consultant
Certified Commercial Building Inspector
Certified, WDI Inspector
Founder & Current President, New Hampshire State Chapter NACHI
NACHI, State Representative for Legislative Affairs
Retired: ICC Certified Member
Retired: Code Compliance Inspector.
Retired: ASTM Committee Member
New Hampshire License #0096
Reply With Quote
  #44  
Old 4/26/07, 6:06 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,557
Default Re: floor outlet receptacle

What we have here is a failure to communicate.
I went back and read the thread so I hope I have this right.

Speedy and Frank C. are both correct in what they say.

Let me restate the situation.

The floor outlets in question are more than 2 ft away from the wall so they can not be counted for the within 6 ft. rule along a wall space.

They are not in the picture so to speak and are as Frank stated convenience outlets.

Can we all just get along now??
Reply With Quote
  #45  
Old 4/26/07, 6:07 PM
Frank M. Carrio, CMI's Avatar
Frank M. Carrio, CMI Frank M. Carrio, CMI is offline
ESOP Committee Member
 
Join Date: Jan 2004
Posts: 4,363
Default Re: floor outlet receptacle

Hey Speedy!
I have better things to do, and this "Good natured bantering" is not serving any useful purpose so I am signing off on this thread.



Signed, Frank Carrio, CMI
Certified Master Inspector & Consultant
Certified Commercial Building Inspector
Certified, WDI Inspector
Founder & Current President, New Hampshire State Chapter NACHI
NACHI, State Representative for Legislative Affairs
Retired: ICC Certified Member
Retired: Code Compliance Inspector.
Retired: ASTM Committee Member
New Hampshire License #0096
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Microwave receptacle jwardenski Electrical Inspections 17 9/9/07 8:18 PM
What's This Receptacle For? cmettel Electrical Inspections 7 5/25/07 8:35 AM
Bedroom receptacle dnasser Electrical Inspections 9 4/16/07 11:33 AM
Online Code Check- Reference pabernathy Electrical Inspections 31 11/9/06 4:39 PM
Wiring a Receptacle jallingham Electrical Inspections 9 8/6/06 5:34 PM


All times are GMT -4. The time now is 11:15 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts