Exclamation Floor Outlets

They are acceptable but not when installed in this manner!

Last edited by jtedesco1; 3/4/06 at 9:28 PM..
Reply With Quote
  #2  
Old 1/29/06, 8:06 PM
Joe Farsetta's Avatar
Joe Farsetta Joe Farsetta is offline
ESOP Committee Member
 
Join Date: Oct 2002
Location: Pearl River, NY
Posts: 3,207
Default Re: Floor Outlets

Joe,

What of floor receptacles that may have been okayed by the AHJ? As you know, the applicability of facets of the NEC can vary from town to town. Where such receptacle is seen, I do point out the inherent dangers associated with it, and question whether it was approved. I do not flag it as a code violation, or something that is absolutely not permitted. We dont have that knowledge, I'm afraid
Reply With Quote
  #3  
Old 1/29/06, 8:06 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,826
Send a message via Yahoo to jfunderburk
Default Re: Floor Outlets

Please 'splain the correct method. Thanks.



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #4  
Old 1/29/06, 8:20 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,908
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Floor Outlets

Quote:
Originally Posted by jfarsetta
Joe,

What of floor receptacles that may have been okayed by the AHJ? As you know, the applicability of facets of the NEC can vary from town to town. Where such receptacle is seen, I do point out the inherent dangers associated with it, and question whether it was approved. I do not flag it as a code violation, or something that is absolutely not permitted. We dont have that knowledge, I'm afraid
Joe: I agree, since in older homes and buildings we find them in the floor and they are full of wax and dirt and are sometimes damaged.

The pictures here are from my Best Western Hotel Room, first time I found them in the floor. I know of AHJ's who allowed a "Bell Box" or "FS" (Waterproof) box and a waterproof cover.

Rugs that are washed could lead to problems. See below for more to esplain
Reply With Quote
  #5  
Old 1/29/06, 8:23 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,908
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Floor Outlets

Quote:
Originally Posted by jfunderburk
Please 'splain the correct method. Thanks.

Floor Boxes.
Boxes listed specifically for this application shall be used for receptacles located in the floor.



Exception: Where the authority having jurisdiction judges them free from likely exposure to physical damage, moisture, and dirt, boxes located in elevated floors of show windows and similar locations shall be permitted to be other than those listed for floor applications. Receptacles and covers shall be listed as an assembly for this type of location.

Reply With Quote
  #6  
Old 1/29/06, 8:37 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,908
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Floor Outlets

Here's what I meant when I was thinking about floor wax and dirt, I found this in a furniture store.



Looks like the dirt and floor wax in this "Gem Box" have added more insulation?

These old types of splices used here were usually twisted, soldered, and taped with friction tape, but the box being on the floor may not meet the present requirements.
A floor box of the brass type, often used in the floors around malls and airports, are probably the best, but I see now that some people are stealing the brass for scrap!
Reply With Quote
  #7  
Old 1/29/06, 9:42 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,826
Send a message via Yahoo to jfunderburk
Default Re: Floor Outlets

Quote:
Originally Posted by jtedesco1
Floor Boxes.
Boxes listed specifically for this application shall be used for receptacles located in the floor.


OK, I accept that. But how do I know whether or not it's listed without removing it?



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #8  
Old 1/29/06, 10:00 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,908
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Floor Outlets

Quote:
Originally Posted by jfunderburk


OK, I accept that. But how do I know whether or not it's listed without removing it?




Searched Google Images for Floor Boxes and found this:
emAlbum
Reply With Quote
  #9  
Old 1/29/06, 10:15 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,826
Send a message via Yahoo to jfunderburk
Default Re: Floor Outlets

That one certainly seems sturdy. But how do I know if it's "listed" per the code you cited?



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #10  
Old 1/29/06, 10:41 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,908
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Floor Outlets

Quote:
Originally Posted by jfunderburk
That one certainly seems sturdy. But how do I know if it's "listed" per the code you cited?
UL Listed floor boxes include the complete assembly consisting of the cover,
gasket and box. Receptacles may be included in the packaging or added
to the assembly in the field. Products Listed for installation are covered
under the product categories metallic outlet boxes (QCIT), and nonmetallic outlet boxes (QCMZ)

Listed kits, consisting of the cover and gasket for use with specific
Listed floor boxes, are identified in the installation instructions. The interchangeability of components is authorized only as specified on the
product, or in the installation instructions included with the product.

UL Listed floor boxes bear the complete Listing Mark, including the UL in a circle, the word “Listed,” the product name, and the control number. The Listing Mark consisting of the UL in a circle can be found on the product itself; the complete Listing Mark is usually located on the smallest unit container in which the product is packaged, indicating
that the entire assembly has been evaluated for compliance with applicable
UL Standards and NEC Section 370-27(b). Also, the product identity “floor box” is placed adjacent to the Listing Mark.

Receptacle and cover assemblies complying with NEC Section 370-27(b), are covered under the product category Receptacles for Attachment Plugs and Plugs (RTRT)


These products are Listed as display receptacles, including the receptacle, flush device cover place or outlet box cover, and closure plugs. They are intended for use in show window floors and similar locations where the device is not subjected to scrub water. UL Listed receptacles and cover assemblies are not intended to be used as substitutes or in place of floor boxes.



The special UL meetings for government inspectors provide us an excellent opportunity to ask questions of UL engineers and to clarify UL requirements.

Searching for the letters in parenthesis over on www.ul.com will give more information.

Reply With Quote
  #11  
Old 1/29/06, 10:49 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,826
Send a message via Yahoo to jfunderburk
Default Re: Floor Outlets

Thanks Joe.



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #12  
Old 1/30/06, 12:29 AM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 6,524
Default Re: Floor Outlets

I would just list it as 'significantly deficient'. It is also really stupid.

I am not speaking from code or local AHJ, just plain common sense.

Course, I have not had any buyer's of hotels yet.

Joe, maybe you ought to skip the Best Westerns from now on.



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!

Last edited by wdecker; 1/30/06 at 9:41 AM..
Reply With Quote
  #13  
Old 1/30/06, 9:36 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,020
Default Re: Floor Outlets

I "Red Flag" all residential floor receptacles.

I've never seen a floor receptacle (in a home) with a cover as shown.
I've seen many (with covers) in commercial buildings, which are fine.
Reply With Quote
  #14  
Old 1/30/06, 9:59 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,908
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Talking Re: Floor Outlets

Quote:
Originally Posted by dvalley
I "Red Flag" all residential floor receptacles.

I've never seen a floor receptacle (in a home) with a cover as shown.
I've seen many (with covers) in commercial buildings, which are fine.
I will just have to call another inspector, geeez you are too tough!

Here's some information and lots of images for training purposes

http://www.carlon.com/scripts/emAlbu...=0&page=1&tn=1

Reply With Quote
  #15  
Old 1/30/06, 10:35 AM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 6,524
Default Re: Floor Outlets

What is 'allowed' by some governmental and non-governmental construction authorities is not always what is 'best' or safest.

Codes are a minimum standard, not consistant throughout the country and highly influenced by political and economic considerations.

In Chicago, the electrical union is, de facto, the steering authority for the codes. Here is what happens:

1) Unions see a way to increase their membership (and their political power) by coming up with a new standard, like insisting that all electricl wiring be enclosed in EMT or pipe. (this includes 5 vold, very low amp computer wiring)

2) The publish and make known, to their members, this new 'standard'. They also have 'experts' write white papers and publich them in various electrical engineering journals and trade publications. I read one, one time, about the sever lung damage that occurs when the outer plastic coating or ROMEX gets burned. True, it ain't good to breath this stuff, but in a fire, especially one that has already consumed the drywall and gotten to the wiring between the walls, a small amount of ROMEX vapor is chicken feed when compared to the wood smoke, wouldn't you think. A drop of cyanide in a glass of arsenic means little.

3) The new 'standard' gets known and becomes pervasive.

4) The unions start to demand that builders meet the new 'standard'. It this is not agreed to, they start work slowdowns and the like

5) The unions start to put political pressure on the politicians, especially around election time. Campaign contributions and election day 'canvassars' help.

6) The City council hold hearings on the new 'standard'. What finally comes out is that so many builders are already following it (due to previous union pressure) that making the de facto, de jure faces little opposition.

7) The new 'standard' gets adopted into the 'code' and enforced.

The union now has doubled the work load of its members, ensureing them that wiring a house will not take at least twice as long. They work by the hour.

Don't get me wrong, I happen to believe that wire enclosed in EMT is safer than ROMEX. It also helps to ensure a completely ground bonded system (grounding being continuious through the EMT).

But let's nit delude ourselves that the new 'standard' was adopted by reason of altruism or concern for the public safety. The actual technical reasons are probably the smalled factor in the process.

People should realize that 'codes' are, at least as much, political and economic in nature as they are safety measures.



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 7:12 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts