Default Foundation grounding

I was wondering if anyone has come across a panel that has been grounded to the re-bar in the foundation and how do you write it up.
Reply With Quote
  #2  
Old 12/17/07, 4:05 PM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Foundation grounding

This is the best grounding electrode known to mankind.

Edited to add:

(3) Concrete-Encased Electrode. An electrode encased by at least 50 mm (2 in.) of concrete, located within and near the bottom of a concrete foundation or footing that is in direct contact with the earth, consisting of at least 6.0 m (20 ft) of one or more bare or zinc galvanized or other electrically conductive coated steel reinforcing bars or rods of not less than 13 mm (½ in.) in diameter, or consisting of at least 6.0 m (20 ft) of bare copper conductor not smaller than 4 AWG. Reinforcing bars shall be permitted to be bonded together by the usual steel tie wires or other effective means.
Reply With Quote
  #3  
Old 12/17/07, 4:11 PM
Peter C. Russell's Avatar
Peter C. Russell Peter C. Russell is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Alton Bay NH
Posts: 3,998
Default Re: Foundation grounding

Thanks Mike, good info.

The reason I ask is I have a garage to build that will have a studio apartment on the second floor and the building inspector wants the foundation grounded.

If I can I'll take pictures of it and post it.

Last edited by prussell; 12/17/07 at 4:21 PM..
Reply With Quote
  #4  
Old 12/17/07, 4:29 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Foundation grounding

It's not that he wants the foundation grounded. He wants the "foundation" used as a ground(ing electrode).

As Mike said, a Ufer, concrete encased electrode, etc. is the best "ground" yet. NO supplemental electrode is required and they are easy to do if planned for.
Reply With Quote
  #5  
Old 12/17/07, 6:25 PM
Peter C. Russell's Avatar
Peter C. Russell Peter C. Russell is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Alton Bay NH
Posts: 3,998
Default Re: Foundation grounding

Quote:
Originally Posted by Speedy Petey
It's not that he wants the foundation grounded. He wants the "foundation" used as a ground(ing electrode).

As Mike said, a Ufer, concrete encased electrode, etc. is the best "ground" yet. NO supplemental electrode is required and they are easy to do if planned for.
Sorry, my bad, I'll still post pictures as it's being completed.
Reply With Quote
  #6  
Old 12/17/07, 7:07 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,798
Default Re: Foundation grounding

I built an Air-Craft Maintenance Complex at Loring Airforce Base back in 1983 and when I did the foundation, grounding electrodes were cadwelded to re-bar in the footing and also a complete grid around the builiding with groundrods every 25' or so and also interconnected the steel columns around the perimeter.

I had no idea what kind of wasted money that was about. Still haven't figured it out. ha. ha.
Maybe it had something to do with the aircraft maintenance. Who knows.

Marcel
Reply With Quote
  #7  
Old 12/17/07, 7:33 PM
gporter's Avatar
gporter gporter is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Orlando, fl
Posts: 3,281
Default Re: Foundation grounding

Thanks Speedy Pete



Gary Porter

GLP's Home and Mold Inspections
321-239-0621

Certified Commercial Mold Inspector

Serving Orlando, Kissimmee, Winter Park, Winter Springs, Oviedo, Titusville, Celebration, Harmony, Avalon, Windermere, Deltona, Debary, Sanford
Orange County, Seminole County, Volusia County, Osceola County

www.homeandmoldinspections.com
Reply With Quote
  #8  
Old 12/17/07, 8:13 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Foundation grounding

Quote:
Originally Posted by prussell
Sorry, my bad, I'll still post pictures as it's being completed.
Hey, no bad at all.
Pics would be cool though.
Reply With Quote
  #9  
Old 12/17/07, 8:32 PM
Peter C. Russell's Avatar
Peter C. Russell Peter C. Russell is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Alton Bay NH
Posts: 3,998
Default Re: Foundation grounding

Quote:
Originally Posted by Speedy Petey
Hey, no bad at all.
Pics would be cool though.
Hopefully I'll still be able to dig a hole and pour concrete next week, with all this cold weather I think the frost may settle in to quick.
Reply With Quote
  #10  
Old 12/17/07, 8:36 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Foundation grounding

Oh wow. You're not even poured yet.
Yeah man, it's gettin' COLD!
Reply With Quote
  #11  
Old 12/17/07, 8:43 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Foundation grounding

Quote:
Originally Posted by mcyr
I built an Air-Craft Maintenance Complex at Loring Airforce Base back in 1983 and when I did the foundation, grounding electrodes were cadwelded to re-bar in the footing and also a complete grid around the builiding with groundrods every 25' or so and also interconnected the steel columns around the perimeter.

I had no idea what kind of wasted money that was about. Still haven't figured it out. ha. ha.
Maybe it had something to do with the aircraft maintenance. Who knows.

Marcel
cadwelding

You think this guy would wear gloves
Reply With Quote
  #12  
Old 12/17/07, 8:56 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,798
Default Re: Foundation grounding

Quote:
Originally Posted by bkelly2
cadwelding

You think this guy would wear gloves
No doubt Brian.

My electrician was though and so would I.

Attachment 16784

There will always be one that thinks nothing of it.

Marcel

Last edited by mcyr; 7/2/08 at 11:26 AM..
Reply With Quote
  #13  
Old 12/17/07, 9:30 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is online now
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: Foundation grounding

Quote:
Originally Posted by mcyr
There will always be one that thinks nothing of it.
And it's usually the guys that have been welding for a long time...they get cocky and feel invincable...stupid is more like it !!!
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Demystify Grounding & Bonding Class pabernathy Inspection Education & Training 5 12/24/06 1:10 AM
Common Defects List by Age of House trausch Inspection Education & Training 10 6/12/06 4:52 AM


All times are GMT -4. The time now is 9:35 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts