Hey Guys-

I just wanted to double-check with you on this set-up. This has four panels with the last one ending at a detached garage which was about 75 feet from the house. The set-up went as follows:

Service panel (1) on far side of house > to distribution panel (2) in basement > to disconnect panel (3) on the other side of the house > to the detached garage panel (4).

Does the disconnect box (3) need grounding or bonding? They just used a connector to join the service from the distribution panel to the service going to the garage. And should the detached garage then have it's own grounding/bonding? Thanks.

Kenny
Attached Thumbnails
four-panels-gedc9942.jpg   four-panels-img_0646.jpg   four-panels-gedc9927.jpg   four-panels-gedc9973.jpg  



Rigler Home Inspections
Hays, KS 67601
785-656-0272
Reply With Quote
Need a home inspection in Minnesota? Check out InterNACHI's listing of Minnesota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 2/7/12, 1:55 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,252
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Four Panels

Photo #1 has a problem with the locknut/bushing at the bottom.
Photo #2 looks OK with separate neutrals and EGC's.
Photo #3 appears that the disconnect is not properly grounded.
Photo #4 answer depends on when this was installed and the type of raceway. Is there a GES at the garage, there doesn't appear to be a GEC?
Reply With Quote
  #3  
Old 2/7/12, 2:18 PM
Kenny Rigler Kenny Rigler is offline
InterNACHI Member
 
Join Date: Apr 2009
Location: Hays, KS
Posts: 255
Default Re: Four Panels

Quote:
Originally Posted by Robert Meier View Post
Photo #3 appears that the disconnect is not properly grounded.
Photo #4 answer depends on when this was installed and the type of raceway. Is there a GES at the garage, there doesn't appear to be a GEC?
The disconnect box (#3) between the distribution panel and the garage didn't have any grounding or bonding. The neutral and ground from the distribution panel were joined with the neutral going to the garage within that connector. Nothing was attached to the box.

The raceway between the house and detached garage was plastic. The house was built in 1995 and the detached garage appeared to be constructed around the same time.

Pictures 1 and 2 below are the disconnect box at the house. Picture 3 and 4 is the raceway to the garage panel.
Attached Thumbnails
four-panels-gedc9927.jpg   four-panels-gedc9929.jpg   four-panels-gedc9997.jpg   four-panels-gedc9971.jpg  



Rigler Home Inspections
Hays, KS 67601
785-656-0272
Reply With Quote
  #4  
Old 2/7/12, 4:04 PM
Gary Farnsworth Gary Farnsworth is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Olathe, KS
Posts: 3,715
Default Re: Four Panels

IMO, way over-loaded for 150 amp main. 8-220's need at least a 400 amp main service, again, IMO. Document, refer.



CMI, CPI, KS #0110-0094 Termite #16601
KS Radon #KS-MS-0027
BBB A+ Accredited Business
Serving the Greater Kansas City Metro Area
Eastern Kansas/Western Missouri
http://www.metrospeckc.com
"If opportunity doesn't knock, build a door"--Milton Berle
Reply With Quote
  #5  
Old 2/7/12, 4:21 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Four Panels

The disconnect (#3) should have the egc's bonded directly to the enclosure.

In #4, the panel needs its own grounding electrode (as Robert mentioned), in addition, the egc's must be bonded to the enclosure.

Depending on the year it was installed, #4 may have the neutrals also bonded to the enclosure, however, as an HI, you should defer that type of installation for verification of no additional connective (metallic) paths.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #6  
Old 2/8/12, 12:24 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Four Panels

Quote:
Originally Posted by gfarnsworth View Post
IMO, way over-loaded for 150 amp main. 8-220's need at least a 400 amp main service, again, IMO. Document, refer.
So instead of doing a load calculation we assume a panel is overloaded based on a visual count of 240 volt breakers? This could be 8 small units that just happen to be 240 volts. Your statement does not take into account for the possible loading of those circuits, not does it consider load diversity for things like heat and A/C that are not used at the same time.

Glad I didn't pay for that opinion, and I would have liked it even less if I paid for a load calculation or if the possible buyers backed out because of statements like this.
Reply With Quote
  #7  
Old 2/8/12, 12:34 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Four Panels

Quote:
Originally Posted by Jim Port View Post
Glad I didn't pay for that opinion, and I would have liked it even less if I paid for a load calculation or if the possible buyers backed out because of statements like this.
Unfortunately, it is a common mistake for some home inspectors to "over-think" this issue, and assume the panel is over loaded based on simple (unqualified) observations.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #8  
Old 2/8/12, 2:36 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,252
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Four Panels

Quote:
Originally Posted by Jim Port View Post
Glad I didn't pay for that opinion, and I would have liked it even less if I paid for a load calculation or if the possible buyers backed out because of statements like this.
Jim thanks for bringing that up. Out in the field you hear all sorts of crazy thing about adding up the circuit breaker values and they can't exceed X% of the main's ampacity. Of course the party making the statement says "it's right there in the codebook you just have to look for it".

The true indicator of a panel being overloaded is a load calculation, unless of course you're tripping the main breaker.
Reply With Quote
  #9  
Old 2/8/12, 3:57 PM
Gary Farnsworth Gary Farnsworth is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Olathe, KS
Posts: 3,715
Default Re: Four Panels

I had a home one time that had a 100 amp main breaker, and three down-stream panels that all totaled 920 amps. Is that OK?

I turned on all three central A/C units, the electric dryer, all of the burners of the range top and the double-wall oven units, and the main popped.

If you think I am unqualified, then how many amps are allowed on a 150 amp main?



CMI, CPI, KS #0110-0094 Termite #16601
KS Radon #KS-MS-0027
BBB A+ Accredited Business
Serving the Greater Kansas City Metro Area
Eastern Kansas/Western Missouri
http://www.metrospeckc.com
"If opportunity doesn't knock, build a door"--Milton Berle
Reply With Quote
  #10  
Old 2/8/12, 4:27 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Four Panels

Reporting that the panel is overloaded, based on adding up the total breaker-ratings is an "unqualified" opinion.

Reporting that the panel is overloaded, based on a load calculation of the circuits within the residence is a "qualified" opinion.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #11  
Old 2/8/12, 4:32 PM
Gary Farnsworth Gary Farnsworth is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Olathe, KS
Posts: 3,715
Default Re: Four Panels

Yes. There are wattage of appliances to be figured into the calculations via the labels on them. Even the breakers should be figured at 80% load. Example 15 amp circuit times the 120 volts equals total wattage available times .8 which equals a total of 1,440 watts of usage capacity on a 15 amp breaker. Calculations get technical, but when I see anything over 500 amps of breakers on a 100 amp main, I get concerned.



CMI, CPI, KS #0110-0094 Termite #16601
KS Radon #KS-MS-0027
BBB A+ Accredited Business
Serving the Greater Kansas City Metro Area
Eastern Kansas/Western Missouri
http://www.metrospeckc.com
"If opportunity doesn't knock, build a door"--Milton Berle

Last edited by gfarnsworth; 2/8/12 at 4:35 PM..
Reply With Quote
  #12  
Old 2/8/12, 5:00 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Four Panels

A Square D Service enclosure rated at 200 amps can support 40 separate circuits. Based on having only 15 amp circuit breakers (which would be highly unlikely), the potential load would be 600 amps. Would you call this overloaded without any supporting data?

How about if had all 20 amp circuit breakers?

How about two 2-pole 40's, two 2-pole 30's, and the balance with single pole 15's and 20's?

Anyone calling these overloaded, without actually running a load calc, would be giving an unqualified opinion.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #13  
Old 2/8/12, 5:07 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,252
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Four Panels

Quote:
Originally Posted by gfarnsworth View Post
Calculations get technical, but when I see anything over 500 amps of breakers on a 100 amp main, I get concerned.
Although at times your concerns may be legitimate you really have no way of knowing without doing a load calculation.
Reply With Quote
Need a home inspection in Minnesota? Check out InterNACHI's listing of Minnesota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 2/8/12, 8:24 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Four Panels

Also there is no 80% limit on the breakers. That would only apply if the load was considered continuous which means on for 3 hours or more. This would rarely be an issue in a dwelling.

A water heater is considered a continuous load, but I will show the math. 4500w/240 = 18.75 amps. 18.75 * 1.25 = 23.475 amps, so a 25 amp breaker would work. The 30 amp two pole with #10 is more common and allowed.

Adding up the breaker handles does not take into consideration the load diversity for things that do not run at the same time.
Reply With Quote
  #15  
Old 2/8/12, 8:42 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Four Panels

Quote:
Originally Posted by jpope View Post
A Square D Service enclosure rated at 200 amps can support 40 separate circuits.
Yep, my 200 amp Square D has a combination of 15, 20, 30 and 50 amp breakers that equal 545 amps. Could easily be much higher.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Help proof the safety section on inspecting electrical panels: read here kshepard Electrical Inspections 56 1/1/12 6:58 PM
SEC and panels also CEU course material dhostetter Electrical Inspections 3 10/3/08 5:49 PM
Distribution panels bking Electrical Inspections 2 3/11/07 10:29 AM
FPE Panel - Do you open them up? menser Electrical Inspections 11 2/7/06 6:31 PM


All times are GMT -4. The time now is 9:37 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts