Hey Guys-
I just wanted to double-check with you on this set-up. This has four panels with the last one ending at a detached garage which was about 75 feet from the house. The set-up went as follows: Service panel (1) on far side of house > to distribution panel (2) in basement > to disconnect panel (3) on the other side of the house > to the detached garage panel (4). Does the disconnect box (3) need grounding or bonding? They just used a connector to join the service from the distribution panel to the service going to the garage. And should the detached garage then have it's own grounding/bonding? Thanks. Kenny Rigler Home Inspections Hays, KS 67601 785-656-0272 |
| Need a home inspection in Minnesota? Check out InterNACHI's listing of Minnesota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Photo #1 has a problem with the locknut/bushing at the bottom.
Photo #2 looks OK with separate neutrals and EGC's. Photo #3 appears that the disconnect is not properly grounded. Photo #4 answer depends on when this was installed and the type of raceway. Is there a GES at the garage, there doesn't appear to be a GEC? |
|
#3
|
|||
|
|||
|
Quote:
The raceway between the house and detached garage was plastic. The house was built in 1995 and the detached garage appeared to be constructed around the same time. Pictures 1 and 2 below are the disconnect box at the house. Picture 3 and 4 is the raceway to the garage panel. Rigler Home Inspections Hays, KS 67601 785-656-0272 |
|
#4
|
|||
|
|||
|
IMO, way over-loaded for 150 amp main. 8-220's need at least a 400 amp main service, again, IMO. Document, refer.
CMI, CPI, KS #0110-0094 Termite #16601 KS Radon #KS-MS-0027 BBB A+ Accredited Business Serving the Greater Kansas City Metro Area Eastern Kansas/Western Missouri http://www.metrospeckc.com "If opportunity doesn't knock, build a door"--Milton Berle |
|
#5
|
||||
|
||||
|
The disconnect (#3) should have the egc's bonded directly to the enclosure.
In #4, the panel needs its own grounding electrode (as Robert mentioned), in addition, the egc's must be bonded to the enclosure. Depending on the year it was installed, #4 may have the neutrals also bonded to the enclosure, however, as an HI, you should defer that type of installation for verification of no additional connective (metallic) paths. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#6
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Glad I didn't pay for that opinion, and I would have liked it even less if I paid for a load calculation or if the possible buyers backed out because of statements like this. |
|
#7
|
||||
|
||||
|
Unfortunately, it is a common mistake for some home inspectors to "over-think" this issue, and assume the panel is over loaded based on simple (unqualified) observations.
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#8
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
The true indicator of a panel being overloaded is a load calculation, unless of course you're tripping the main breaker. |
|
#9
|
|||
|
|||
|
I had a home one time that had a 100 amp main breaker, and three down-stream panels that all totaled 920 amps. Is that OK?
I turned on all three central A/C units, the electric dryer, all of the burners of the range top and the double-wall oven units, and the main popped. If you think I am unqualified, then how many amps are allowed on a 150 amp main? CMI, CPI, KS #0110-0094 Termite #16601 KS Radon #KS-MS-0027 BBB A+ Accredited Business Serving the Greater Kansas City Metro Area Eastern Kansas/Western Missouri http://www.metrospeckc.com "If opportunity doesn't knock, build a door"--Milton Berle |
|
#10
|
||||
|
||||
|
Reporting that the panel is overloaded, based on adding up the total breaker-ratings is an "unqualified" opinion.
Reporting that the panel is overloaded, based on a load calculation of the circuits within the residence is a "qualified" opinion. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#11
|
|||
|
|||
|
Yes. There are wattage of appliances to be figured into the calculations via the labels on them. Even the breakers should be figured at 80% load. Example 15 amp circuit times the 120 volts equals total wattage available times .8 which equals a total of 1,440 watts of usage capacity on a 15 amp breaker. Calculations get technical, but when I see anything over 500 amps of breakers on a 100 amp main, I get concerned.
CMI, CPI, KS #0110-0094 Termite #16601 KS Radon #KS-MS-0027 BBB A+ Accredited Business Serving the Greater Kansas City Metro Area Eastern Kansas/Western Missouri http://www.metrospeckc.com "If opportunity doesn't knock, build a door"--Milton Berle Last edited by gfarnsworth; 2/8/12 at 4:35 PM.. |
|
#12
|
||||
|
||||
|
A Square D Service enclosure rated at 200 amps can support 40 separate circuits. Based on having only 15 amp circuit breakers (which would be highly unlikely), the potential load would be 600 amps. Would you call this overloaded without any supporting data?
How about if had all 20 amp circuit breakers? How about two 2-pole 40's, two 2-pole 30's, and the balance with single pole 15's and 20's? Anyone calling these overloaded, without actually running a load calc, would be giving an unqualified opinion. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#13
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Although at times your concerns may be legitimate you really have no way of knowing without doing a load calculation.
|
| Need a home inspection in Minnesota? Check out InterNACHI's listing of Minnesota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#14
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Also there is no 80% limit on the breakers. That would only apply if the load was considered continuous which means on for 3 hours or more. This would rarely be an issue in a dwelling.
A water heater is considered a continuous load, but I will show the math. 4500w/240 = 18.75 amps. 18.75 * 1.25 = 23.475 amps, so a 25 amp breaker would work. The 30 amp two pole with #10 is more common and allowed. Adding up the breaker handles does not take into consideration the load diversity for things that do not run at the same time. |
|
#15
|
||||
|
||||
|
Yep, my 200 amp Square D has a combination of 15, 20, 30 and 50 amp breakers that equal 545 amps. Could easily be much higher.
Christopher Currins Certified, Licensed Proudly serving the St.Louis Metro St. Charles, St. Peters, Maryland Heights, O'Fallon, Florrisant, MO Home Inspector BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Help proof the safety section on inspecting electrical panels: read here | kshepard | Electrical Inspections | 56 | 1/1/12 6:58 PM |
| SEC and panels also CEU course material | dhostetter | Electrical Inspections | 3 | 10/3/08 5:49 PM |
| Distribution panels | bking | Electrical Inspections | 2 | 3/11/07 10:29 AM |
| FPE Panel - Do you open them up? | menser | Electrical Inspections | 11 | 2/7/06 6:31 PM |