This is an FP Panel I looked at Saturday. Aside from the FP panel and aluminum wiring advisory, I think the Perf board surrounding the panel is a problem. I also didn't see neutral and ground busses bonded. There is a main cutoff on the outside of the house with a 150 Amp breaker but no bond apparent there. There were no fault indications for polarity on any of the wiring in the house. could the bus bars be mounted directly to the panel and be bonded by the metal panel?

Thanks in advance
Mike
Attached Thumbnails
fp-panel-fppanel1.jpg   fp-panel-fppanel2.jpg   fp-panel-fppanel3a.jpg  
Reply With Quote
  #2  
Old 3/6/06, 11:20 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: FP Panel

This is not the service equipment, therefore, it is wired improperly. The grounds and neutrals should be separated, grounds bonded to the enclosure and neutrals isolated from the enclosure.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 3/6/06, 12:51 PM
mbledsoe mbledsoe is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Morrow, GA
Posts: 60
Default Re: FP Panel

Quote:
Originally Posted by jpope
This is not the service equipment, therefore, it is wired improperly. The grounds and neutrals should be separated, grounds bonded to the enclosure and neutrals isolated from the enclosure.
So would the single 150 amp breaker near the service entrance in a separate box be considered the be considered the service equipment? and that one should be bonded? Thanks for the feedback.
Reply With Quote
  #4  
Old 3/6/06, 1:00 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: FP Panel

Yes, Michael the 150A Main Service Disconnect as you stated in the separate box is the main OCPD. The panel you have shown should be of (4) wire nature and a floating neutral terminal bar....as Jeff stated it should not be bonded with the grounding bar....and all neutrals should go to the floating neutral bar...not the same terminal bar as the grounds...to be correct anyway.

Also those multiple neutral's under the single terminal....well you know the answer to that one...



Paul W. Abernathy
Reply With Quote
  #5  
Old 3/6/06, 1:04 PM
mbledsoe mbledsoe is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Morrow, GA
Posts: 60
Default Re: FP Panel

Great feedback, very much appreciated!
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 7:28 PM
Panel Inspection Safety roconnor Electrical Inspections 10 9/24/06 9:02 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 10:25 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts